Condensing Water Quality parameters
I have a requirement for the new Cooling Towers that requires the water to be monitored of its quality.
The CT will be part of the old AC system installation and is part of the retrofitting project we're currently undertaking.
However, the designer has required the following parameters which i feel is already too much.
These are the parameters,
- PH - 7.5 to 9.0
- Turbidity (FTU scale) - <20 units
- TDS (total dissolved solids) - <250 ppm
- Iron - <1.0ppm
- Copper - <0.1ppm
- Bacteria Count - <10npml
- Hardness as Caco³ - 30 ~ 200 ppm
- Chlorides - <125 ppm
- Sulfates - < 125 ppm
Other than the first three, i believe that the others can be neglected since the "condensing water" only serves the chiller units and for no other purpose.
Do you agree on me with this one?
Typically though i use only the PH and the conductivity rating to monitor the water quality for most of the cooling towers i have installed and even some cooling towers come built-in with them.
I need a credible explanation to the building tenant that is why I'm sourcing out some help.
Similar Threads
-
water softener effects on condensing tower
By nh3junkie10 in forum NH3Replies: 1Last Post: 10-10-2010, 08:31 PM -
pure water from air
By Lc_shi in forum New TechnologiesReplies: 32Last Post: 26-02-2009, 12:25 PM -
desuperheating not condensing
By CCLPaul in forum Technical SpeculationsReplies: 17Last Post: 26-02-2008, 03:05 AM -
open cycle R718 A/C that also provides high purity water?
By star882 in forum Technical SpeculationsReplies: 7Last Post: 27-07-2006, 04:18 AM -
Evaporative Condensers info
By Tomás in forum Technical DiscussionsReplies: 4Last Post: 31-05-2004, 08:28 AM