    Smile Unable to decipher high pressure fault - help!!



    Hello

    This system is a walk in freezer room approx 2.5m x 2.5m x2.5m R404a

    HP 18.5 bar (43c) 10k subcooling
    LP 2.4 bar (-15c) superheat not known
    Ambient 17c
    Rooom should be at -18c but only holding at -8c.

    I've tested for non-condensibles and there are none.

    Condenser clear and fan ok, presumed over-charged so removed 0.5 kilo R404

    This resulted in the following:

    HP 17 bar (38c) 6k subcooling
    LP 2.1 bar (-18c) superheat not known
    Ambient 17c

    System now undercharged with bubbles in sightglass, but room temp now dropped and holding at -13c.

    (Removed 300g to start with, waited a few minutes but no significant changes so removed a further 200g until bubbles started showing)

    I've had a good look at the condenser and checked for non condensibles, all fine.

    Any ideas anyone?

    Thanks



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Unable to decipher high pressure fault - help!!

    I had in the past something similar with compressed air refrigerated drier, couldn't find anything wrong.

    Recovered all the gas, new drier, vacuum and recharged with virgin 404.

    the machine worked fine so i didn't bother to make more checks.

    Give it a try and see how it goes.

  3. #3
    Join Date
    Apr 2005
    Location
    Manchester England
    Age
    43
    Posts
    332
    Rep Power
    20

    Re: Unable to decipher high pressure fault - help!!

    hi there can you check across the liquid line to see if you have a temperature drop along the line?

  4. #4
    Join Date
    May 2007
    Location
    Scotland
    Posts
    327
    Rep Power
    17

    Re: Unable to decipher high pressure fault - help!!

    thanks

    I did wonder about the gas as the unit has had some work in the past.

    Are you saying the liquid line / drier are blocked, if so why the high LP?

    Thanks

  5. #5
    Join Date
    Dec 2007
    Location
    lebanon
    Posts
    130
    Rep Power
    17

    Re: Unable to decipher high pressure fault - help!!

    h ti
    if ur compressor matches the fan coil look after the txv look like too big orifice

  6. #6
    Join Date
    Nov 2006
    Location
    UK
    Age
    50
    Posts
    708
    Rep Power
    23

    Re: Unable to decipher high pressure fault - help!!

    Quote Originally Posted by chemi-cool View Post
    I had in the past something similar with compressed air refrigerated drier, couldn't find anything wrong.

    Recovered all the gas, new drier, vacuum and recharged with virgin 404.

    the machine worked fine so i didn't bother to make more checks.

    Give it a try and see how it goes.
    I will second this as I`ve had this before on a small freezer

    New charge (virgin) every time in my opinion

  7. #7
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Unable to decipher high pressure fault - help!!

    What are the condenser air on/air off temps?

  8. #8
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Unable to decipher high pressure fault - help!!

    Are you sure another tech filled other gas in it, partially R404 and some other gas?
    Otherwise, I apply the same technique as Chemi. Recover, new dryer, vacuum and restart with new gas. This unit is too small to spend too much time on it.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  9. #9
    Join Date
    May 2007
    Location
    Scotland
    Posts
    327
    Rep Power
    17

    Re: Unable to decipher high pressure fault - help!!

    I willtry replacing gas and changing the drier, but does anybody think the TEV could be causing this ?

  10. #10
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Unable to decipher high pressure fault - help!!

    No, the TEV isn't the cause for a high HP.
    Then your LP should be also far beyond normal working conditions.

    Possible causes for a too high HP:
    non-condensables in teh system
    too small condenser surface,
    clogged,
    fan defective,
    overcharged
    Bended discharge lines

    That's all...I think
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  11. #11
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Unable to decipher high pressure fault - help!!

    Bubbles in the liquid sight glass is no evidence of an insufficient charge. Flashing can be caused by a number of reasons, least of which undercharge.
    If subcooling is 6k then the amount of refrigerant is still much, despite bubbles in the sight glass.

  12. #12
    Join Date
    May 2007
    Location
    Scotland
    Posts
    327
    Rep Power
    17

    Re: Unable to decipher high pressure fault - help!!

    hello

    changed sight glass and refrigerant and system working well, so thanks to everyone.

  13. #13
    Join Date
    Aug 2010
    Location
    australia
    Posts
    15
    Rep Power
    0

    Re: Unable to decipher high pressure fault - help!!

    remember r 404a is a blend if you lose a certain amount of vapour it will ruin the blend. reclaim the charge of 404a and put in r 507 and see how you go

  14. #14
    Join Date
    Oct 2010
    Location
    NJ, U.S.A.
    Posts
    8
    Rep Power
    0

    Re: Unable to decipher high pressure fault - help!!

    Quote Originally Posted by NoNickName View Post
    Bubbles in the liquid sight glass is no evidence of an insufficient charge. Flashing can be caused by a number of reasons, least of which undercharge.
    If subcooling is 6k then the amount of refrigerant is still much, despite bubbles in the sight glass.
    great point ..... most guys i know automatically ASSume vapor in the sight glass means low charge .. some ppl have even brainwashed the customer into thinking this ... this has led to quite a few calls ive encountered where a unit ended up bein grossly over charged by a diy'r trying to save a buck by clearing the glass.

  15. #15
    Join Date
    May 2007
    Location
    Scotland
    Posts
    327
    Rep Power
    17

    Re: Unable to decipher high pressure fault - help!!

    If a system is known to have worked well in the past, there is no noticeable temperature drop across components in the liquid line (by touch) and there is good sub cooling as in this case, would you say it is safe to rule out pre-expansion as a possible problem.

    Or are there other causes i'm not aware of?

    If a liquid line is suitable for a virgin blend and some of it has leaked, then this presumably could sometimes result in pre expansion?

    Thanks
    Last edited by Contactor; 24-10-2010 at 04:21 PM. Reason: Daikin - faulty

  16. #16
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: Unable to decipher high pressure fault - help!!

    Quote Originally Posted by Contactor View Post
    If a system is known to have worked well in the past, there is no noticeable temperature drop across components in the liquid line (by touch) and there is good sub cooling as in this case, would you say it is safe to rule out pre-expansion as a possible problem.

    Or are there other causes i'm not aware of?

    If a liquid line is suitable for a virgin blend and some of it has leaked, then this presumably could sometimes result in pre expansion?

    Thanks
    Hi Contactor.
    I read the below info and saved it, you may find it interesting.

    Why do bubbles appear in the sight glass when I use a blend? Does this mean I don't have enough refrigerant?
    There are several reasons for bubbles in the sight glass. If one of the traditional refrigerants showed vapor in the sight glass it often meant there wasn't enough liquid refrigerant being fed to the valve, and more refrigerant was added to the system.
    Blends could show flashing for the same reason, however, they can also flash when there is plenty of liquid in the receiver. Ironically, this liquid in the receiver could be causing the problem, particularly when the equipment is in a hot environment. Blends will come out of the condenser slightly subcooled - at a temperature below the saturated temperature of the blend at the existing high side pressure.
    Yet when the blend sits in the receiver, it can "locally fractionate," or change composition slightly by shifting one of the components into the vapor space of the receiver. This will effectively produce a saturated liquid in the receiver, at the same pressure you had before, which flashes when it hits the expanded volume of the sight glass. In most cases these bubbles will collapse when the blend gets back into the tubing which feeds the valve, and the system will operate just fine.
    Check other system parameters such as pressures, superheat and amperage to confirm whether you have the right charge. Don't rely solely on the sight glass.

    Grizzly

  17. #17
    Join Date
    May 2007
    Location
    Scotland
    Posts
    327
    Rep Power
    17

    Re: Unable to decipher high pressure fault - help!!

    I had a feeling there would be more to it... thanks

    Bearing that in mind, whats the best method of gassing up a new job running a blend, I usually charge to a full sight glass, periodically check the SH and SC and leave it at that. Most of my installs are designed by others - i'm never given a charge by weight to use and even if I did then it often wouldn't be much use because there is usually a difference between whats on the final drawing and as installed....

  18. #18
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Unable to decipher high pressure fault - help!!

    Quote Originally Posted by Contactor View Post
    I had a feeling there would be more to it... thanks

    Bearing that in mind, whats the best method of gassing up a new job running a blend, I usually charge to a full sight glass, periodically check the SH and SC and leave it at that. Most of my installs are designed by others - i'm never given a charge by weight to use and even if I did then it often wouldn't be much use because there is usually a difference between whats on the final drawing and as installed....
    Start with a rough estimate of 1 kg gas/kW for a cooling application, and 0,75 kg/kW for a freezer and 0,5 to 0.3 kg/kW for an airco application.
    You never can calculate it before.
    If you have to add double on a small hermetic, then there's something wrong. 80% of the receiver is also a rough guideline for standard pre-assembled groups.

    As soon you've reached design conditions and the SH is 5 or 6 K (measured on the evaporator and corrected for measuring fault) or as designed, then your evaporator is fully charged, even with a not full sightglass and you have theoretically enough gas in the system.

    I demonstrate several times that bubbles in a sight glass disappears many times on small hermetics when you cover the condenser with a paper and they come back when you remove it again. Most can't explain why this happens. Explaining this will lead us to the upper left corner on a cycle on a log p/g chart and the associated thermal inertia of the components which provokes this.
    Same phenomena when fans on a condenser are cycled on and off and bubbles appears when switching off the fans and they disappear some time (speaking in seconds) after switching off the fans again.
    Last edited by Peter_1; 24-10-2010 at 07:02 PM.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  19. #19
    Join Date
    Feb 2010
    Location
    uae
    Age
    48
    Posts
    39
    Rep Power
    0

    Re: Unable to decipher high pressure fault - help!!

    HI try using pressure temp charts while charging.
    got a few tips posted earlier at this forum.

    Normal Suction Pressure Example
    Refrigerant type R-404A

    Return air temperature (box) 20 F

    Suction pressure from gauge manifold 40 psig

    Box temperature - 15 F = estimated evaporator temperature 20 - 15 = 5 F

    Use P/T chart to convert evaporator temperature to pressure 38 psig

    Compare estimated pressure to gauge pressure 40/38 close


    Normal Discharge Pressure Example
    Refrigerant type R-404A

    Ambient air temperature entering condenser coil 90 F

    Discharge pressure from gauge manifold 305 psig

    Ambient temperature + 30 F = estimated condenser temperature 90 + 30 = 120 F

    Use P/T chart to convert condenser temperature to pressure 310 psig

    Compare estimated pressure to gauge pressure 305/310 Same

    Condenser coil temperature runs about 30 F hotter than ambient air or ambient air runs 30 F cooler than the condenser coil to promote rapid heat exchange
    Last edited by muju; 24-10-2010 at 08:22 PM.

  20. #20
    Join Date
    Oct 2010
    Location
    Australia
    Posts
    9
    Rep Power
    0

    Re: Unable to decipher high pressure fault - help!!

    Quote Originally Posted by NoNickName View Post
    Bubbles in the liquid sight glass is no evidence of an insufficient charge. Flashing can be caused by a number of reasons, least of which undercharge.
    If subcooling is 6k then the amount of refrigerant is still much, despite bubbles in the sight glass.
    I was thinking this. Sight glass is for moisture indication ONLY.

    Never charge off sight glass.

  21. #21
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Unable to decipher high pressure fault - help!!

    Quote Originally Posted by Contactor View Post

    Bearing that in mind, whats the best method of gassing up a new job running a blend, I usually charge to a full sight glass, periodically check the SH and SC and leave it at that. Most of my installs are designed by others - i'm never given a charge by weight to use and even if I did then it often wouldn't be much use because there is usually a difference between whats on the final drawing and as installed....
    I came across one the other day that should have been a simple compressor change.

    It was a packaged heat pump where the compressor needed replacing.

    There was no indication on refrigerant charge even on the commissioning report there was no details.

    I recovered the refrigerant and pressure tested the system for leaks which were fine and then recharged with virgin R407c with the same amount that i took out...4.3kg.

    I ran the system up and DP was low at 13b and so i blocked part of the condesor coil to stimulate design conditions.

    Discharge rose to 15 bar (40C SCT) and i proceeded to take the followig figures.

    evap air on 22
    evap air off 14/15
    Subcooling 6k
    superheat 18k
    Suction pressure 4bar/0C
    Discharge 15bar/40C

    The sight glass was flashing and there were no restrictions in the liquid line.

    All filters and coils were clean as well.

    I added refrigerant 250 kg at a time until i had added nearly 2kg all the figures stayed the same apart from the superheat which dropped to between 12-14k.

    However when i held the bulb of the TXV the coil flooded with liquid and the SH dropped dramatically.

    The bulb was placed correctly and was tightly wrapped on the pipe.

    Am i right in thinking this could well be the TXV causing the restriction? Possibly undersized orifice which was a TEZ 2 no5
    The difference between genius and stupidity is that genius has its limits.

    Marc

  22. #22
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Unable to decipher high pressure fault - help!!

    Quote Originally Posted by marc5180 View Post
    However when i held the bulb of the TXV the coil flooded with liquid and the SH dropped dramatically.
    This proves that

    a. There is enough liquid at the TXV inlet to flood the coil and

    b. Sufficient refrigerant is able to flow through the orifice to flood the coil.

    Therefore, adjusting the stem should drop the SH.
    Last edited by Gary; 01-11-2010 at 04:34 AM.

  23. #23
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Unable to decipher high pressure fault - help!!

    Couldn't agree more with Gary. TEV can overflood, so you have enough liquid before it.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  24. #24
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Unable to decipher high pressure fault - help!!

    Before I left I tried adjusting the stem 1 full turn and waited 20 mins but the superheat didn't alter so I turned it back to ts original position.
    Is there a general rule of thumb as to how many degrees you increase/decrease superheat by one turn of the screw?
    The difference between genius and stupidity is that genius has its limits.

    Marc

  25. #25
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Unable to decipher high pressure fault - help!!

    What brand is the TEV? Some need to turn CW and others CCW to open the valve more.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  26. #26
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Unable to decipher high pressure fault - help!!

    It's a danfoss tez2.
    The difference between genius and stupidity is that genius has its limits.

    Marc

  27. #27
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Unable to decipher high pressure fault - help!!

    turn it open completely (CCW) and then back (CW) 3.5 tot 4 turns CW must give you a SH of +/- 7 to 8K.
    3 turns CCW will not harm the compressor.
    If it then doesn't come OK, I should add a little bit refrigerant (200 gr) at once and see if SH and/or evaporating temperature increases.

    Another point: where are you measuring LP and SH because your run on R407c which is a terrible gas to make errors on the readings.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  28. #28
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Unable to decipher high pressure fault - help!!

    Thanks for the help Peter.

    I'm measuring the superheat on the suction port which is about 12" from the compressor inlet and taking the temperature from the same place.

    From the evap outlet to the compressor inlet is about 3foot.
    The difference between genius and stupidity is that genius has its limits.

    Marc

  29. #29
    Join Date
    Apr 2009
    Location
    South Africa
    Age
    49
    Posts
    108
    Rep Power
    16

    Re: Unable to decipher high pressure fault - help!!

    Quote Originally Posted by marc5180 View Post
    Thanks for the help Peter.

    I'm measuring the superheat on the suction port which is about 12" from the compressor inlet and taking the temperature from the same place.

    From the evap outlet to the compressor inlet is about 3foot.
    Always the best to take your suction pressure at the evaporator just before the bulp. Most evaporators have a Schroeder valve there these days.Then do the SH conversion to the chart and u are sure u have the right measurement.
    THE BEST WAY OF LEARNING IS TO DO IT YOURSELF!!!

  30. #30
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Unable to decipher high pressure fault - help!!

    I did look to see if there was a schraeder port just after the evap but there wasn't one.

    I normally do measure the temp close to the compressor inlet which I know is total superheat so I suppose I thought the 3ft of pipe from the evap to the compressor wouldn't increase the superheat that much.
    The difference between genius and stupidity is that genius has its limits.

    Marc

  31. #31
    Join Date
    Apr 2009
    Location
    South Africa
    Age
    49
    Posts
    108
    Rep Power
    16

    Re: Unable to decipher high pressure fault - help!!

    3ft is not much your right, but having problems with the system it is always best to eliminate all the small add ups as far as possible.
    Have u ever worked with Danfoss Adap cool electronic expansion valve systems witch uses the probe or transducer to calculate the SH on the coil?
    THE BEST WAY OF LEARNING IS TO DO IT YOURSELF!!!

  32. #32
    Join Date
    Apr 2009
    Location
    South Africa
    Age
    49
    Posts
    108
    Rep Power
    16

    Re: Unable to decipher high pressure fault - help!!

    3ft is not much your right, but having problems with the system it is always best to eliminate all the small add ups as far as possible.
    Have u ever worked with Danfoss Adap cool electronic expansion valve systems witch uses the probe or transducer to calculate the SH on the coil?
    THE BEST WAY OF LEARNING IS TO DO IT YOURSELF!!!

  33. #33
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Unable to decipher high pressure fault - help!!

    Quote Originally Posted by Lodiev View Post
    Have u ever worked with Danfoss Adap cool electronic expansion valve systems witch uses the probe or transducer to calculate the SH on the coil?
    No i've never come across these.
    The difference between genius and stupidity is that genius has its limits.

    Marc

Similar Threads

  1. 9 superheat & subcooling scenarios
    By nike123 in forum Fundamentals
    Replies: 39
    Last Post: 19-07-2011, 03:16 AM
  2. Replies: 30
    Last Post: 25-04-2010, 12:40 PM
  3. High discharge temp
    By paul_h in forum Air Conditioning
    Replies: 48
    Last Post: 06-05-2009, 11:10 AM
  4. fun quiz
    By Brian23 in forum New to RE
    Replies: 6
    Last Post: 02-10-2007, 10:18 PM
  5. High head pressure no duty
    By LRAC in forum Commercial
    Replies: 15
    Last Post: 23-07-2007, 12:12 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •