    Climaveneta - Modbus communication



    Hello,

    My name is Davide, I work in the Republic of Ireland as Site Engineer for a pharma company.

    I'm trying to setup MODBUS communication between our ABB DCS system and a Climaveneta FOCS unit equipped with the 485 MODBUS comm card on their W3000 controller without success: is there any body that did manage to link up with a Climaveneta unit through 485?

    I'm not looking for somebody to sort the problem for me, i would just like to know if there is anybody that actual setup such communication or if it is just theory written on the manual.

    Thanks

    Davide



  2. #2
    Join Date
    Oct 2006
    Location
    Bucks, U.K.
    Age
    71
    Posts
    604
    Rep Power
    18

    Re: Climaveneta - Modbus communication

    Hi Davide,

    Just a few thoughts......

    What length cable? Correct cable impedance?
    Correct termination?
    1 to 1 or are there other RTUs on system?
    2 wire or 4 wire ?
    Only Earth Screen at one end and daisy chain units.
    Only 1 Master.

    ECM

  3. #3
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Climaveneta - Modbus communication

    What are your problems? Hardware of software? Do you get any ascii transmitted or nothing at all?

  4. #4
    Join Date
    Oct 2010
    Location
    Cork, Ireland
    Age
    44
    Posts
    5
    Rep Power
    0

    Re: Climaveneta - Modbus communication

    Hi,

    Thanks for answering so quickly.

    So far i'm pretty sure that all the main setting/parameters are ok:
    - termination looks correct (Txd/Rxd/Shield)
    - 120 Ohm resistor
    - cable length 80 meters, AWG 22 twisted and shielded
    - 2 wire
    - at the moment the chain just consists in 1 master and 1 slave (chiller), if it works i will then look into adding other 8 salves (energy meters)
    - address and baud rate set consistently
    - as far as i can understand there is no communication at all, the master times out after polling the slave. If we connect a different device that supports 485 in place of the chiller we are instead able to see it on the DCS

    ...it might be the comm card on the chiller controller being faulty, i'm just trying to find out here if i'm missing something big and obvious for somebody expert in the field before ordering a spare that might not even solve the problem

    ...by the way, i must really congratulate with who is responsible of this forum and to the people that write on it: i found it through Google, i had a look around in the last hour and i must say it is a very valuable source of information, especially for those like me who are not refrigeration engineers.

    Davide

  5. #5
    Join Date
    Oct 2006
    Location
    Bucks, U.K.
    Age
    71
    Posts
    604
    Rep Power
    18

    Re: Climaveneta - Modbus communication

    Hi Davide,

    Do you have to 'enable' comms on the climaventa unit at all?
    Are you using a valid data address? Off the top of my head, 3000 up are Modbus read locations

  6. #6
    reff's Avatar
    reff Guest

    Re: Climaveneta - Modbus communication

    Hi!
    I already did it some times on W3000. Problems was not. What exactly does not work?
    For search of variables use chipkin.com/cas-modbus-scanner
    Further OPC-server and Scada
    In parametres check up it is included "USER"\Serial line configuration- enabl.

  7. #7
    Join Date
    Oct 2010
    Location
    Cork, Ireland
    Age
    44
    Posts
    5
    Rep Power
    0

    Re: Climaveneta - Modbus communication

    Hi

    Yes, on the W3000 (onboard PLC, i just discovered it is a PLC from CAREL) you actually have to enable the serial communication specifying from "supervisor" - which we did from the start - then you enter the ID address and the baud rate.

    The more i read you're replies the more i think it is just the card (or part of the PLC code related to the serial comm) not working properly, so probably the best solution is trying with a new comm card and see if it works.

    Thanks for your suggestions and for the link to the chipkin modbus scanner, if i manage to get a result i'll post the solution here...even if it will probably take few weeks

    Thanks again

  8. #8
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19

    Re: Climaveneta - Modbus communication

    hi davide,
    you are site engineer , right, is it your job to wire in this controle sytstem , are you qualified and experianced to do this job? have YOU done this before?

  9. #9
    Join Date
    Oct 2010
    Location
    Cork, Ireland
    Age
    44
    Posts
    5
    Rep Power
    0

    Re: Climaveneta - Modbus communication

    Hi sedgy,

    It is not my job to wire and set-up the communication.
    Unfortunately, here we are a very small staff: it is enough to do what is strictly needed but if you want to go a bit further you get to do a bit of everything.

    In this case I am just trying to understand where the problem is and what can be done to solve it beacuse the Automation contractor says the problem is on the chiller while the refrigeration contractor says it is on the DCS... it is not a vital issue as we run the chiller on time bands with two different set-points, so the process is not affected at all by this comm problem.

    I want to have total control of the chiller from the DCS so that we can achieve a more precise regulation of the set-point in relation to the particular production step: this would then result in saving a significant amount of power every week by increasing the T set-point whenever possible. Time bands are great but are not too flexible.

    Davide

  10. #10
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Climaveneta - Modbus communication

    Quote Originally Posted by sedgy View Post
    hi davide,
    you are site engineer , right, is it your job to wire in this controle sytstem , are you qualified and experianced to do this job? have YOU done this before?
    If you are not ready to help people, just browse away, and please don't annoy us with stupid answers.

  11. #11
    AusMech's Avatar
    AusMech Guest

    Re: Climaveneta - Modbus communication

    Had same probs communicating to 3000 controller. Set address and baud rate the same on controller and laptop program but still not communicating. Tried using carell default settings and is now ok. Even if controller settings differ set these figures onto laptop program and should work. These are address 77000 and baud rate 38600. If requested carel default password 1234. Strange that it works with addresses and rates being different from controller to laptop program but it did.
    CHEERS

  12. #12
    Join Date
    Oct 2010
    Location
    Cork, Ireland
    Age
    44
    Posts
    5
    Rep Power
    0

    Re: Climaveneta - Modbus communication

    Thanks AusMech but it really looks the problem here is on the comm card on the carel controller.
    I'm waiting for a service engineer to come onsite towards the end of November with a new card... hope that will work

    Davide

  13. #13
    AusMech's Avatar
    AusMech Guest

    Re: Climaveneta - Modbus communication

    There should be LED lights flashing (green) on field card on controller. If not flashing card not inerted correctly ( they can be tricky) or faulty serial card.

Similar Threads

  1. Climaveneta WRAT SL 1804 Problem
    By hitmanzak in forum Trouble Shooting
    Replies: 5
    Last Post: 29-07-2010, 07:11 AM
  2. Mini-Split Communication
    By Husky250 in forum Air Conditioning
    Replies: 2
    Last Post: 22-05-2010, 02:38 PM
  3. Looking for CLIMAVENETA chillers electrical diagram
    By Pan.nik in forum Air Conditioning
    Replies: 0
    Last Post: 13-11-2009, 08:23 AM
  4. Climaveneta MID 0021 FC - wiring diagram.
    By k_k_krastev in forum Trouble Shooting
    Replies: 1