    Hi all....especially the oldies who might have an answer!

    Just been to a local butchers to look at one of his coldrooms. Gauge (LP) pressure with system off did not tally with what I was expecting (R12 ?) .....pressure was too high.
    A quick butchers (no pun intended!) at the TEV showed it was on Methyl Chloride.
    This is my first run in with the gas, but I do know that it is one to be wary of...toxicity and flammable......turns out the system has been in since shop was built in the '60s. The old fridgidare condensing unit is still working sweet

    Symptoms at first glance were possible shortage of gas, but sight glass was clear, so a quick pump down showed charge was probably OK and pointed to the TEV.

    Adjusting the superheat has temporarily got the system cooling again, but now to the question of what to do next.

    Are any of the currently available TEV's liable to work satisfactorily with the R40? (R12 for example).

    What oil is likely to be in the system?.....Mineral?

    Any suggestions for a drop in conversion? I haven't (as yet) found a P-T chart for R40 as my books don't go back that far, so direct comparison is currently difficult, but I guess that R12 might be close so possibly a R12 drop in would work.

    Thanks, ECM



  2. #2
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: R40 (Methyl Chloride) Alternatives

    Quote Originally Posted by Electrocoolman View Post
    Hi all....especially the oldies who might have an answer!

    Just been to a local butchers to look at one of his coldrooms. Gauge (LP) pressure with system off did not tally with what I was expecting (R12 ?) .....pressure was too high.
    A quick butchers (no pun intended!) at the TEV showed it was on Methyl Chloride.
    This is my first run in with the gas, but I do know that it is one to be wary of...toxicity and flammable......turns out the system has been in since shop was built in the '60s. The old fridgidare condensing unit is still working sweet

    Symptoms at first glance were possible shortage of gas, but sight glass was clear, so a quick pump down showed charge was probably OK and pointed to the TEV.

    Adjusting the superheat has temporarily got the system cooling again, but now to the question of what to do next.

    Are any of the currently available TEV's liable to work satisfactorily with the R40? (R12 for example).

    What oil is likely to be in the system?.....Mineral?

    Any suggestions for a drop in conversion? I haven't (as yet) found a P-T chart for R40 as my books don't go back that far, so direct comparison is currently difficult, but I guess that R12 might be close so possibly a R12 drop in would work.

    Thanks, ECM
    Helllo Electrocoolman

    R12 would often be charged into methyl chlorine systems, I would try an R12 valve. I have seen bottles of methyl chlorine in BOC a few years back, so your system should still be viable. Mineral oil, 4GS from memory.

    Kind Regards Andy D
    If you can't fix it leave it that no one else will:rolleyes:

  3. #3
    Join Date
    Sep 2008
    Location
    Newcastle upon tyne
    Age
    75
    Posts
    80
    Rep Power
    16

    Re: R40 (Methyl Chloride) Alternatives

    Hello

    I can remember working back in the 60s on Methyl Chloride and SO2 systems but cant remember retrofitting.

    Can remember that it can get very dangerous somehow if system is retrofitted and it is not perfectly clean.

    I would make more enquiries on this 1.

    There was a definite risk retro fitting these gases.

    Aww

  4. #4
    Join Date
    Oct 2006
    Location
    Bucks, U.K.
    Age
    71
    Posts
    604
    Rep Power
    18

    Re: R40 (Methyl Chloride) Alternatives

    Thanks Andy and Alan,

    Although I've not tried to get hold of any Andy, you might be correct in thinking that its still available. Not sure whether its covered under Montreal Protocol as it doen't contain Fluorine. Does anyone know anything further regarding this point?

    Thats a good point Alan regarding retrofitting. I'll have to do more research.

  5. #5
    Join Date
    Nov 2006
    Location
    UK
    Age
    50
    Posts
    708
    Rep Power
    23

    Re: R40 (Methyl Chloride) Alternatives

    I know its very potent stuff to your respirator system and that its heavier than air

    please tread carefully

Similar Threads

  1. calcium Chloride with NH3 absorption
    By happyjay75 in forum Refrigeration Books
    Replies: 2
    Last Post: 11-09-2008, 11:53 AM
  2. calcium Chloride with NH3 absorption Area
    By happyjay75 in forum Refrigeration Books
    Replies: 0
    Last Post: 28-07-2008, 09:18 PM
  3. Insulation alternatives
    By fishmonger in forum Commercial
    Replies: 3
    Last Post: 02-01-2007, 03:09 PM
  4. Can I use calcium chloride in propylene system?
    By joanna in forum Hydrocarbons
    Replies: 1
    Last Post: 23-12-2006, 10:18 PM
  5. Methol Chloride
    By Andy in forum Refrigerants
    Replies: 11
    Last Post: 03-08-2002, 09:44 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •