    Smile Liquid hammering problem on screw compressor in ammonia refrigeration system



    Dear friends in one of my plant there 6 nos. SB series Grasso make screw compressors in which 4 nos. has been running since 10 years and 2 compressor are new just added to the system.All of them are connected by -2 deg c and -5 deg c common header.Suppose i have select 2 existing compressor and 1 new compressor on -5 deg c system. At the same time 1 existing and 1 new compressor are running but the ammonia liquid comes on the existing compressor only.their discharge temp falls down and compressor make abnormal noise while the new compressor are running well. Kindly gives yours valuable suggestion as earliest as posible.



  2. #2
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: Liquid hammering problem on screw compressor in ammonia refrigeration system

    Liquid carry over due to greater swept volume from the comps?
    Try lowering your Surge / inter cooler Drum working level.
    Is the affected comp nearest the drum suction?

    Just a complete guess given the little information you give.
    What's a refrigeration executive?
    Grizzly

  3. #3
    Join Date
    Dec 2008
    Location
    usa
    Age
    83
    Posts
    34
    Rep Power
    0

    Re: Liquid hammering problem on screw compressor in ammonia refrigeration system

    I agree with Grizzly about possible increase in swept volume causing liquid carryover. If you lower liquid level it might help. If it is a low pressure pump receiver be careful not to lower level too much and cause pump[s] to cavitate.

    Did you add more end users that required you to add compressors. If so, do any of the end users cause violent flood back of liquid to low presure receiver causing slopover.

Similar Threads

  1. Autocascade refrigeration system: design verification needed
    By DaBit in forum Technical Speculations
    Replies: 3
    Last Post: 07-02-2010, 08:48 AM
  2. Replies: 29
    Last Post: 02-10-2008, 09:48 PM
  3. liquid hammering on pumped liquid line R717
    By VEYSEL DURLU in forum Trouble Shooting
    Replies: 20
    Last Post: 27-03-2008, 06:19 PM
  4. Migrate Oil problem - Medium Refrigeration System
    By lurioda in forum Fundamentals
    Replies: 0
    Last Post: 24-02-2004, 07:20 AM
  5. Refrigeration system proposal; comments please.
    By DaBit in forum Technical Speculations
    Replies: 13
    Last Post: 01-01-2003, 04:42 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •