Results 1 to 10 of 10
Thread: Refrigeration effect
14-10-2010, 10:38 PM #1
Hi Guys, are there any additives that can be injected the refrigerant cycle - To improve system refrigeration effect? For ACs and all.
14-10-2010, 10:42 PM #2
Re: Refrigeration effect
No, I mean an additive that is injected into the refrigerant to improve its cooling effect.
14-10-2010, 10:51 PM #3
No, some firms claim miracles but the only thing that should be inside the pipes is oil and refrigerant.
14-10-2010, 10:58 PM #4
If there was anything better than the refrigerant then the refrigerant manufacturer would use it as the refrigerant.
The only thing that should be in with the refrigerant is the oil and we tolerate the oil only because it stops the comp from seizing up.
coolrunnings
.Last edited by chemi-cool; 31-10-2010 at 06:26 PM.
15-10-2010, 06:02 PM #5
Keep the condenser coils clean and clear of obstructions that could impede airflow.
Keep the evaporator clean and ensure good airflow. Keep the filter clean!!!
As long as the refrigerant charge is correct, then she's doing the best she can!If at first you DO succeed, try to hide your astonishment!!
31-10-2010, 02:00 PM #6
The system efficiency can be maintained only by proper maintenance... It cannot be improved by ant external additive...
31-10-2010, 06:29 PM #7
31-10-2010, 07:27 PM #8
01-11-2010, 11:14 AM #9
Not by adding anything, but looking more at your process, clean filters, condensers etc. Installing your condenser in the coolest place also helps. For every 1 deg C you lower your condensing temp, you have 3 % more capacity and use 3 % less energy. These changes cost reletively little. After that there are things like subcoolers etc, with higher cost.
08-11-2010, 01:28 PM #10
I agree, it would be extremely difficult to optimize further a properly designed, installed, and maintained system by adding another fluid. There are products out there that make claims but the data supporting those claims is severly lacking in my opinion.
advanced refrigeration technology
By Lc_shi in forum FundamentalsReplies: 10Last Post: 16-02-2011, 05:22 PM -
Net Refrigeration Effect.
By Burrah Boy in forum FundamentalsReplies: 1Last Post: 20-10-2008, 01:38 PM -
Evaporator TD and refrigeration effect
By nambiandy in forum FundamentalsReplies: 2Last Post: 11-10-2008, 11:39 AM -
Negative Refrigeration Cooling effect
By Kenny Pollin in forum FundamentalsReplies: 7Last Post: 26-03-2007, 03:53 PM