    Screw compressor failure



    Hi everybody! I am examining a case of a J&E HallSrew HS2028 compressor that failed. The cast body of the compressor cracked/fractured into pieces destroying all of the internal parts of the compressor (stars, slide valves etc). The claim is that large amounts of liquid refrigerant entered the compressor from the liquid injection line (used to cool the oil) due to a fault of the controller that closes the solenoid valve.
    Has anybody faced the similar problems and if yeas what was the cause of the failure?
    Thanks!



  2. #2
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,044
    Rep Power
    19

    Re: Screw compressor failure

    Quote Originally Posted by christossev View Post
    due to a fault of the controller that closes the solenoid valve.
    Thanks!
    If the solenoid liquid is closed how could liquid refrigerant have entered to the compressor by that way?
    To make progress is never good enough, I want to do better and better and better

  3. #3
    christossev's Avatar
    christossev Guest

    Re: Screw compressor failure

    Quote Originally Posted by Sandro Baptista View Post
    If the solenoid liquid is closed how could liquid refrigerant have entered to the compressor by that way?
    The solenoid remained open not closed!

  4. #4
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    52
    Posts
    2,554
    Rep Power
    24

    Re: Screw compressor failure

    Yes, the compression of liquid between the rotors causes the two to separate and grind the housing.
    But J&E have single screw and two daisies (stars), so I don't think that large amount of liquid could cause that.

  5. #5
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: Screw compressor failure

    Quote Originally Posted by NoNickName View Post
    Yes, the compression of liquid between the rotors causes the two to separate and grind the housing.
    But J&E have single screw and two daisies (stars), so I don't think that large amount of liquid could cause that.
    Good points, also there is a restricting orifice to flash off the liquid if I remember correctly.

    I suppose it's possible that the liquid refrigerant level in the compressor could increase.
    Due to the solenoid remaining open. But surely the crankcase heater would boil off the refrigerant.

    I would be looking at your system level controls for high levels.
    Resulting in Suction line liquid carry over.

    I am at a loss as to how you could create such a huge amount of damage otherwise.
    The one Benifit of Hall screws is that the star wheels are Sacrificial.
    And easily replaced.

    What you are describing christossev sound more like huge thermal shock damage.
    But all the Hallscrews that I used to look after were well maintained and never failed the way you describe.
    Their own manual even states after 25yrs running check the main bearings for wear.

    There is more to this than you are saying?
    Grizzly

Similar Threads

  1. VSD on screw machines
    By Mike Hopkins in forum New Technologies
    Replies: 14
    Last Post: 20-02-2011, 01:10 AM
  2. R22 - R417 (RetroFit) Screw set A.C
    By Chris_Atlantic in forum Trouble Shooting
    Replies: 3
    Last Post: 23-04-2010, 06:53 PM
  3. Compressors - screw or reciprocating?
    By Josip in forum Industrial Compressors
    Replies: 18
    Last Post: 27-01-2009, 11:36 PM
  4. Replies: 7
    Last Post: 23-09-2008, 09:24 AM
  5. Mono or twin screw
    By Nirmalya in forum Industrial Compressors
    Replies: 43
    Last Post: 12-09-2006, 03:19 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •