    nitrogen test fail



    im a plumber by trade,grabed by the nuts and thrown into a hvac system ive never heard of(lg sync 2) been told the basics of the system, and no problem with the piping, first test of the piping will not maintain pressure. all braze joints,schrader valves,flare joint,test rigs have been soap tested more time than i care to discuss.is there an issue with pressure fluctuation that i wasnt told about? any info will be greatly appreciated.



  2. #2
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: nitrogen test fail

    yay a plumber that doesnt test with water.if you leave your gauges on for a 24 hour period your likely to see a fluctuation up to 8 psi from my observations on smaller systems.best thing is to check around same time of day at about the same ambient temperature.its a bit rude when they tell you its an inert gas even with total system evacuation,using it when you weld etc you will get fluctuations.
    mmm to beer or not to beer...........lets drink breakfast

  3. #3
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,045
    Rep Power
    35

    Re: nitrogen test fail

    Nitrogen leaking past the service valves and into the outdoor unit?
    If there is a port inside then check the standing pressure. If it's too high then there's yer answer.

    There is an old chinese saying: He who pressure test A/C to 650psig has never had valves leak by.

    Arivadetchi,

    Andy.
    Health and safety first..........unless I'm in a hurry.

  4. #4
    Join Date
    Jul 2009
    Location
    Brisbane
    Age
    67
    Posts
    79
    Rep Power
    15

    Re: nitrogen test fail

    Get a qualified refrigeration Mechanic and stick to plumbing

  5. #5
    karas's Avatar
    karas Guest

    Re: nitrogen test fail

    basically test pressure would 150 psi-250psi enough for me.

  6. #6
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: nitrogen test fail

    Quote Originally Posted by karas View Post
    basically test pressure would 150 psi-250psi enough for me.
    It may be enough for you but is not enough to comply with our regulations.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  7. #7
    Join Date
    Dec 2008
    Location
    West Yorkshire
    Posts
    63
    Rep Power
    16

    Re: nitrogen test fail

    Amazes me how people will even discuss such a dangerous thing as nitrogen pressure testing, with a complete novice.
    Stick to fawcetts and you won't kill yourself.

  8. #8
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,445
    Rep Power
    37

    Re: nitrogen test fail

    Quote Originally Posted by sparkatan View Post
    Amazes me how people will even discuss such a dangerous thing as nitrogen pressure testing, with a complete novice.
    Stick to fawcetts and you won't kill yourself.
    Fawcetts are a car dealership in our area?
    http://www.fawcettsvolvo.co.uk/

  9. #9
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,045
    Rep Power
    35

    Re: nitrogen test fail

    I thought it referred somehow to the field where the mighty New Milton Town F.C. play football and also inspire the junior team, The New Milton Eagles.

    Andy.
    Health and safety first..........unless I'm in a hurry.

Similar Threads

  1. Leak Testing?
    By Thana in forum Trouble Shooting
    Replies: 36
    Last Post: 31-08-2010, 02:57 PM
  2. Daikin VRV II Test Mode Failure
    By KISS KISS BANG in forum Air Conditioning
    Replies: 8
    Last Post: 30-05-2010, 08:54 PM
  3. moisture test
    By SkyWalker in forum Fundamentals
    Replies: 10
    Last Post: 13-04-2010, 08:49 AM
  4. Nitrogen Condensing by Temperarture
    By Reflexive in forum Technical Discussions
    Replies: 0
    Last Post: 21-12-2008, 01:23 AM
  5. Triple evacuation on split system
    By batfink in forum Technical Discussions
    Replies: 10
    Last Post: 05-10-2008, 01:11 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •