    Differential pressure switch testing them?



    hi all

    could anyone tell me the best way of testing these if you think one may be acting faulty.

    i know they have the two tubes one for example on one side of a fan and one on the other side. from removing the tubes from the switch. My question is should the tube before the fan be sucking and the tube after the fan be blowing/

    i was trying to test one on site today but unsure?

    cheers lee
    Attached Images Attached Images



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Differential pressure switch testing them?

    [quote=moondawn;206455 My question is should the tube before the fan be sucking and the tube after the fan be blowing?[/quote]
    That's correct.

    I normally check that the switch is making/breaking by using a length of tube on one port and suck/blow on the tube. Either use a meter across the contacts and/or listen for the switch changing over.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Apr 2005
    Location
    Manchester England
    Age
    43
    Posts
    332
    Rep Power
    20

    Re: Differential pressure switch testing them?

    Hi Brian thanks for the response.

    The Switch i was testing was clearing sucking on the ducting before the fan however it only made a contact when i blew through the tube. can anyone explain why that would be?

    cheers lee

  4. #4
    Join Date
    Mar 2008
    Location
    England
    Posts
    232
    Rep Power
    20

    Re: Differential pressure switch testing them?

    Quote Originally Posted by moondawn View Post
    Hi Brian thanks for the response.

    The Switch i was testing was clearing sucking on the ducting before the fan however it only made a contact when i blew through the tube. can anyone explain why that would be?

    cheers lee
    Differential pressure is the answer, now what was the question?

  5. #5
    Join Date
    Apr 2005
    Location
    Manchester England
    Age
    43
    Posts
    332
    Rep Power
    20

    Re: Differential pressure switch testing them?

    Quote Originally Posted by B G Scott View Post
    Differential pressure is the answer, now what was the question?
    hi there my question was i was looking at one of pressure these switches on a job to check it over. I withdrew the tubing from the ducting which was before the fan arrows facing towards the fan on the plastic mounting on the duct. once it was withdrew i put a piece of paper on the plastic mounting and observed it was sucking.

    i then sucked down the tube which was connected to the pressure switch and no contact made.
    I then blew down it and the contact made
    I would of thought that it would make when i sucked but this was not the case... Why????

    cheers lee

  6. #6
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Differential pressure switch testing them?

    Tubing on the wrong port of the switch or did you have the other tube still connected to the fan discharge side?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  7. #7
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Differential pressure switch testing them?

    No, not wrong. If the switch is measuring clogged filter, then it shall switch on high differential, that's correct.
    But, it also depends on the microprocessor logic (normally open or normally closed contacts) make or break alarm.

  8. #8
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Differential pressure switch testing them?

    Try a magnehelic gauge in each circuit to read the pa readings.

  9. #9
    Join Date
    Apr 2005
    Location
    Manchester England
    Age
    43
    Posts
    332
    Rep Power
    20

    Re: Differential pressure switch testing them?

    brian : Yes when the side i was sucking the other side of the tubing was connected, so what your saying is i should disconnect both tubes. apply a tube to before the fan side (negative) and suck if it makes contact its good, then apply tube to after the fan (positive) side and blow. if it makes its good.??

    no nickname: it depends on the pressure differential switch whether its open or closed switch?

    magoo: just looking for a simple test to do on site with the switch to check it works okay.

    thanks all

  10. #10
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Differential pressure switch testing them?

    Quote Originally Posted by moondawn View Post

    no nickname: it depends on the pressure differential switch whether its open or closed switch?
    These days, those switches have both NO and NC contacts.

Similar Threads

  1. Daikin high pressure switch. E3 fault
    By weidit in forum Air Conditioning
    Replies: 2
    Last Post: 21-04-2010, 09:14 PM
  2. Capillary Tube Characteristics
    By Chef in forum Fundamentals
    Replies: 9
    Last Post: 10-03-2009, 01:03 PM
  3. oil pressure differential switch shut down
    By tarcau mihai in forum Supermarket Refrigeration
    Replies: 44
    Last Post: 10-11-2008, 10:27 AM
  4. Benji
    By benji in forum Trouble Shooting
    Replies: 29
    Last Post: 30-01-2008, 01:25 PM
  5. Oil Pressure Switch
    By Abe in forum Commercial
    Replies: 9
    Last Post: 15-03-2003, 11:18 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •