Thread: overloads

  1. #1
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    overloads



    Motor contactor overloads.do we need them ?
    Last edited by lowcool; 13-10-2010 at 05:47 AM.


    mmm to beer or not to beer...........lets drink breakfast

  2. #2
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: overloads

    Why would you dispute their necessity?
    Without them you would see far more welded contacts and excessive fire / arching damage.
    Grizzly

  3. #3
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: overloads

    sorry grizzly i will edit and make it motor contactor overloads.
    the reason for my thought was it has always been best practice especially were warranty is concerned.have seen alot of a/c units with contactor and relying on the internal overload of say the hermetic types compressor motor windings.
    Circuit protection is more adequate than in previous times and overloads should trip in your scenario with an uneven leg load but usually dont causing the welded contacts as its application is winding protection.i cant think of any internal compressor motor that has caused welded contacts,ive seen the results of explosions of contactors caused by a compressors.

    just thought it might make interesting discussion.
    i can go jump in the lake if anyone insists
    Last edited by lowcool; 13-10-2010 at 06:12 AM.
    mmm to beer or not to beer...........lets drink breakfast

  4. #4
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: overloads

    Having explained further, Your questions are indeed Valid!
    No need to search out Water just yet!
    Grizzly

  5. #5
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: overloads

    Here in the UK, it is a requirement of BS7671-2008 (552.1.2) that all electric motors having a rating exceeding 0.37kW shall be provided with control equipment incorporating means of protection against overload of the motor. So a motor overload is mandatory if your installation is to comply with the regs.

    Another little known fact is the requirement to provide a main bonding conductor to air conditioning systems (411.3.1.2). How many comply with this I wonder?

  6. #6
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: overloads

    Regardless of the legalities I would always weigh up the cost difference of paying for an overload or a burnt out motor due to some form of overload condition.

    Take the case of a ventilation fan motor that starts to run over current because there is excess air being handled by the fan - access door left open eg. Overload stops the motor running before it is damaged or killed.

    They will also give an early warning of pending failure by tripping prior to total shut-down. (Well, sometimes)
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  7. #7
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: overloads

    what if the motor had its own internal overload or thermistor.wouldnt mind hearing from a manufacturer on this one.it was an earlier post on setting a bitzer overload that got me rethinking about this.

    frank pardon my ignorance but what is a main bonding conductor
    Last edited by lowcool; 14-10-2010 at 02:27 AM.
    mmm to beer or not to beer...........lets drink breakfast

  8. #8
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: overloads

    main bonding conductor

    Earth wire to the rest of us!
    Also known as the CPC I believe?
    Is that correct Frank?
    Grizzly

  9. #9
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: overloads

    Quote Originally Posted by lowcool View Post
    what if the motor had its own internal overload or thermistor.wouldnt mind hearing from a manufacturer on this one.it was an earlier post on setting a bitzer overload that got me rethinking about this.

    frank pardon my ignorance but what is a main bonding conductor
    I guess you are familiar with electrical installations?

    It is the conductor between the main earthing terminal (sometimes the copper earthing busbar) and say, the gas main, water main, steelwork structure .....

  10. #10
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: overloads

    Quote Originally Posted by Grizzly View Post
    main bonding conductor

    Earth wire to the rest of us!
    Also known as the CPC I believe?
    Is that correct Frank?
    Grizzly
    The CPC (Circuit Protective Conductor) is the earth conductor on a 'circuit' Grizzly.
    The Main Earthing Conductor is the earth cable from the Main Earthing Terminal (MET) (copper busbar or earthing terminal in the dist board) and the point where the supply enters the premises (meter)
    A Main Bonding Conductor connects the gas, water, steelwork to the MET.

    Sorry Grizzly, no lolipop this time

  11. #11
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: overloads

    Quote Originally Posted by frank View Post
    The CPC (Circuit Protective Conductor) is the earth conductor on a 'circuit' Grizzly.
    The Main Earthing Conductor is the earth cable from the Main Earthing Terminal (MET) (copper busbar or earthing terminal in the dist board) and the point where the supply enters the premises (meter)
    A Main Bonding Conductor connects the gas, water, steelwork to the MET.

    Sorry Grizzly, no lolipop this time
    Sorry Frank
    I was so eager to answer, I forgot the basics.
    I was once questioned by a MEB inspector as to why the sink draining board was not Earth Bonded.
    In fairness to him in those days composite ones that looked like metal were pretty rare.
    It was the same job as to where my mate the sparky.
    Blew his favourite "Elliot Lucas" pliers up. Cutting out old cables.
    When the main incoming 100a fuse had been removed.
    Discuss!
    Grizzly

  12. #12
    Join Date
    Nov 2006
    Location
    UK
    Age
    50
    Posts
    708
    Rep Power
    23

    Re: overloads

    Quote Originally Posted by Grizzly View Post
    I was once questioned by a MEB inspector as to why the sink draining board was not Earth Bonded.

    Grizzly
    Now that is a supplementary bonding conductor or even an equipotential conductor depending on the installation and or test results

    Earthing if all goes well it is never used but god forbid when its in need your glad its there

  13. #13
    Join Date
    Sep 2008
    Location
    england
    Posts
    427
    Rep Power
    20

    Re: overloads

    [quote=lowcool;206496]what if the motor had its own internal overload or thermistor.wouldnt mind hearing from a manufacturer on this one.it was an earlier post on setting a bitzer overload that got me rethinking about this.


    Thermistors are ok for detection of heat build up in motors up caused by cooling problems or excessive load etc but in my experience they`re no good for phase failure or motor stalling as by the time the thermistors pick up high temperatures the damage has been done.
    If thermistors are only used I like to fit an oveload and wire them in series. That way the motor`s protected for stalling AND gradual overtemperature problems.

  14. #14
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: overloads

    Quote Originally Posted by Grizzly View Post
    It was the same job as to where my mate the sparky.
    Blew his favourite "Elliot Lucas" pliers up. Cutting out old cables.
    When the main incoming 100a fuse had been removed.
    Discuss!
    Grizzly
    Main incoming live and neutral round the wrong way so the 100A fuse was in the neutral.....

    Jon

  15. #15
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: overloads

    not allowed to earth bond to pipe steelwork etc here.its an earth stake in the ground
    mmm to beer or not to beer...........lets drink breakfast

  16. #16
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: overloads

    Quote Originally Posted by lowcool View Post
    not allowed to earth bond to pipe steelwork etc here.its an earth stake in the ground
    You must be on a TT system then, the same as our caravan parks.

  17. #17
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: overloads

    Quote Originally Posted by monkey spanners View Post
    Main incoming live and neutral round the wrong way so the 100A fuse was in the neutral.....

    Jon
    On the main incomer before the meter. Highly unlikely!
    This was on a 1930s Cottage with a PME system if I remember correctly.
    Anyway the sparky involved was a fully indentured highly competent Guy.
    We reckoned at the time that there was a supply "Tapped of of the adjoining cottage.
    As ours was semi detached.
    We never did find out for sure. Made a nice hole in his side cutters/ pliers though.

    Grizzly

  18. #18
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: overloads

    Quote Originally Posted by Grizzly View Post
    "Tapped of of the adjoining cottage"
    Grizzly
    More than likely tapped off the lampost outside
    Then again, maybe you don't live on our estate

  19. #19
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: overloads

    I've seen main live and neutral into the fuse box round the wrong way on farms a few times, 100A fuses replaces with nails, other fuses with fencing wire or tin foil, once a whole steel framed parlour and dairy was live when the genny change over switch shorted out, earth leakage trips with bypass switches because it wouldn't stay on when it rained....

    Nothing would surprise me

    Jon

Similar Threads

  1. Merycon Overloads
    By claretandblue in forum Electrical
    Replies: 2
    Last Post: 04-04-2010, 01:21 PM
  2. identifying merycon overloads
    By claretandblue in forum Trouble Shooting
    Replies: 0
    Last Post: 01-04-2010, 03:31 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •