    Mitsubishi Heavy E01 Fault code (OLD sYSTEM)



    Hi All,

    I have a problem with a mitsubishi heavy showing E01,

    Both indoor cassettes are flashing e01 with the green led on board lit constantly,
    Normal green led is flashing on outdoor unit.
    I have checked wiring and everthing looks ok, reset power but cannot seem to find out whats causing the problem.

    The system is R22
    Model Outdoor FDC504HES2
    Model of indoors FDTN505HES2

    Regards

    chris



  2. #2
    Join Date
    May 2006
    Location
    Isle of Wight, Uk
    Age
    47
    Posts
    424
    Rep Power
    20

    Re: Mitsubishi Heavy E01 Fault code (OLD sYSTEM)

    I think it's communication error - check connections, could be a high level trip in external condensate pump, if fitted.
    I assume it is a twin split system. If it is a twin you could swap the indoor pcb's, and alter the address setting.
    How old is it? I don't recognize that series/model number.

    Andy

  3. #3
    Join Date
    Jan 2005
    Location
    N.Ireland
    Age
    48
    Posts
    177
    Rep Power
    20

    Re: Mitsubishi Heavy E01 Fault code (OLD sYSTEM)

    Hi Andy,

    The units are about ten years old,
    The system has two outdoor units running two indoor units which are connected together through A+B terminals,

    I looked aboved the suspended ceiling and there is a external pump I will check it when I go back.

    If it turns out not to be pump but faulty pcb will the second unit run with the faulty pcb and master with good pcb?

    Both indoor units are flashing the same code E01 and green light is on both constant

    Regards

    Chris

  4. #4
    Join Date
    May 2010
    Location
    Russia
    Posts
    168
    Rep Power
    15

    Re: Mitsubishi Heavy E01 Fault code (OLD sYSTEM)

    Hi Chris2005,
    E1 - communication error remocon <-> indoor unit. For FDTN remocon it's display panel.
    Green LED on PCB indoor/outdoor units it's monitor communication line indoor<->outdoor.
    A-B it's SuperLink (MHI LAN).

    If only green LEDs flash constant (red LEDs OFF, and power supply reset not helped then indoor PCB defective.

    P.S.
    Fresh idea. But at her other symptoms. Sequence of phases can be broken.
    Last edited by bigor_2; 12-10-2010 at 11:54 AM.

  5. #5
    Join Date
    Jan 2005
    Location
    N.Ireland
    Age
    48
    Posts
    177
    Rep Power
    20

    Re: Mitsubishi Heavy E01 Fault code (OLD sYSTEM)

    Hi Bigor,

    I went back to system today to check the unit, I noticed the controller today when turned on had to lights on constant one for reset filter and check but no display.

    I took the controller apart to check it abnd found the back of board all black like somebody had put it straight to mains.(The controller has a transformer behind it in the wall connected to the mains then theres a black and white wire to controller.

    Do you know what voltage should be at A+B terminals on controller?

    The man who owns the place said its been 4 or 5 years since units worked, they were in an old room that they have just done up and kept the old a/c.

    Regards

    Chris

  6. #6
    Join Date
    May 2010
    Location
    Russia
    Posts
    168
    Rep Power
    15

    Re: Mitsubishi Heavy E01 Fault code (OLD sYSTEM)

    Controller is it Center Console SLA-1-E?
    Attached Images Attached Images
    Last edited by bigor_2; 18-10-2010 at 09:28 AM.

  7. #7
    Join Date
    Jan 2005
    Location
    N.Ireland
    Age
    48
    Posts
    177
    Rep Power
    20

    Re: Mitsubishi Heavy E01 Fault code (OLD sYSTEM)

    Hi All,

    The 2 indoor pcbs were defective , The reason being when they had the place renovated the electrician took the MC control network off the wall which has a transformer in the wall behind it but when he put it back on he connected the 240v to a+b blowing the hard wired controller and the 2 indoor boards.

    I have put 2 indoor boards in now and the unit works fine when I press the on off button on the facia panel of indoor unit but It will not work on the hand held remote,

    Is there any switch that has to be changed to make it work on hand held instead of hard wired,( which I have disconnected)

    from the info I can find the wired controller was an optional extra for this unit and only had a wireless when new.

    Thanks

    Chris

    I have dicconnected the hard wired controller

Similar Threads

  1. Mitsubishi 1500 fault code fault
    By pie man in forum Air Conditioning
    Replies: 9
    Last Post: 06-05-2010, 09:30 PM
  2. ARY30 RLA with a fault code
    By james cherry in forum Air Conditioning
    Replies: 3
    Last Post: 17-01-2010, 08:41 PM
  3. Mitsubishi electric fault code
    By robin r33 gtr in forum Air Conditioning
    Replies: 2
    Last Post: 14-08-2009, 08:17 PM
  4. Mitsubishi Electric Intermittent fault
    By marc5180 in forum Air Conditioning
    Replies: 28
    Last Post: 15-01-2009, 10:19 PM
  5. split a/c fault code
    By ksvinod in forum Air Conditioning
    Replies: 1
    Last Post: 04-07-2007, 02:12 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •