    Question Setting the overload on a bitzer



    Hi my question today is what the right way is to set the overload on a reciplicating compressor that only gives the Max operationg amps.3phase motors
    I know with an electrical motor you use the motor amps(or delta) / by root 3.But in refrigeration its not always the same because of the vairible sucion pressure..Is their a formula that you can use with the vairible pressures or do you check the operating amps + 10%?



  2. #2
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Setting the overload on a bitzer

    Say your compressors max current is 8A per phase then i would set the overloads for a bit more e.g. 10% over that, you would need to check with the overload manufacturers if their scale already takes the % into acount.

  3. #3
    Join Date
    May 2007
    Location
    scotland
    Posts
    756
    Rep Power
    19

    Re: Setting the overload on a bitzer

    i have a few bitzer octagon compressors on packs both d4 and d6 d4 is 9.3 amps and the d6 is 10.5 amps

Similar Threads

  1. Bitzer CSH8561-125Y oil sight glass
    By Peter_1 in forum Industrial
    Replies: 40
    Last Post: 26-05-2010, 04:32 PM
  2. Setting Daikin VRV indoor unit fan speed
    By mchild in forum Air Conditioning
    Replies: 8
    Last Post: 24-10-2009, 07:34 AM
  3. Replies: 14
    Last Post: 27-08-2008, 08:57 PM
  4. Compressor Overload setting
    By Chris2005 in forum Commercial
    Replies: 20
    Last Post: 23-06-2008, 03:20 PM
  5. Setting Overload
    By Abe in forum Electrical
    Replies: 11
    Last Post: 06-01-2006, 01:53 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •