Thread: Walk-in Cooler

  1. #1
    ajd1550's Avatar
    ajd1550 Guest

    Walk-in Cooler



    I have a walk-in cooler and just replaced the compressor. I can not get ***** to flow. The pressure will go up to 90 on the suction side and that is it. The site glass shows nothing. Could this be a dryer problem or what else would cause this?



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Walk-in Cooler

    And on the discharge side ?

    90 of what?

    A few more clues as to what you have might help.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: Walk-in Cooler

    replaced the compressor but not the drier it seems.good one fella
    mmm to beer or not to beer...........lets drink breakfast

  4. #4
    Join Date
    Feb 2006
    Location
    derbyshire
    Posts
    610
    Rep Power
    19

    Re: Walk-in Cooler

    took the rubber bung out ?

  5. #5
    Join Date
    Oct 2010
    Location
    NJ, U.S.A.
    Posts
    8
    Rep Power
    0

    Re: Walk-in Cooler

    agree with post # 2 about provding more info ... or maybe calling someone actually qualified . . . no offense

  6. #6
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Walk-in Cooler

    The original poster dropped in without introducing him first and expected and answer with 1 post, even no feed-back.
    The suction goes up to 90...feet.Attach the unit firmly to the ground with big and strong bolts I should suggest.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  7. #7
    Join Date
    May 2009
    Location
    New Zealand
    Age
    46
    Posts
    16
    Rep Power
    0

    Re: Walk-in Cooler

    Screw comp, Phase rotation ? Watched a tradesman do it the otherday, got called to a job I quoted because the comp wouldn't pump...

  8. #8
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Walk-in Cooler

    why do people not change driers/contactors/relays-always take the cheap route and then wonders why it bites them on the a**e.
    was it pressure tested after the change as this could have proved flow though the system .
    introduce nitro through the hi side then observe the low side gauge to see it rise.-as long as the discharge valve is shut to prevent it flowing through the compressor.
    was the system vacced out if so to what and for how long.any backdrop?.is the compressor actually running.why did the previous compressor fail?

  9. #9
    Join Date
    Nov 2011
    Location
    Canada
    Posts
    1
    Rep Power
    0

    Re: Walk-in Cooler

    So , lets have some more detailed info/background . or if the problem is solved let us know what the cause turned out to be? (unless your afraid to show your fallibility)

  10. #10
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Walk-in Cooler

    Quote Originally Posted by madblack View Post
    So , lets have some more detailed info/background . or if the problem is solved let us know what the cause turned out to be? (unless your afraid to show your fallibility)
    With a one post wonder I wouldn't bother with any more comments.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  11. #11
    Join Date
    Jul 2010
    Location
    manchester
    Posts
    212
    Rep Power
    15

    Re: Walk-in Cooler

    I agree with install monkey

    changing the drier and contactor is SOP
    some people put a new pot on and find out the contactor is u/s i beg to differ if the pot was u/s in the first place in some cases.
    your only as good as your last job

  12. #12
    tcsbill's Avatar
    tcsbill Guest

    Re: Walk-in Cooler

    Quote Originally Posted by install monkey View Post
    why do people not change driers/contactors/relays-always take the cheap route and then wonders why it bites them on the a**e.
    was it pressure tested after the change as this could have proved flow though the system .
    introduce nitro through the hi side then observe the low side gauge to see it rise.-as long as the discharge valve is shut to prevent it flowing through the compressor.
    was the system vacced out if so to what and for how long.any backdrop?.is the compressor actually running.why did the previous compressor fail?
    ..Meanwhile in Greece...
    I'm so sorry to inform you that most time customers do'nt want to pay an extra 15-20 euros for a filter..or a nitrogen system cleaning..
    Customers always want to do the best for them..in the cheapest way though !!!
    Right then is when you try to find other ways to clean up a system for example..or find cheaper quality parts for replacing....

  13. #13
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Walk-in Cooler

    Compressor is on backwards hth.
    Mostly found in Oxfordshire, UK :)

  14. #14
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Walk-in Cooler

    why dont u fit 2nd hand compressors just to ensure it f**ks up then,and you can be cheaper in your quotes,really keep em happy,also offer a 15minute warranty too,for peice of mind
    Quote Originally Posted by tcsbill View Post
    ..Meanwhile in Greece...
    I'm so sorry to inform you that most time customers do'nt want to pay an extra 15-20 euros for a filter..or a nitrogen system cleaning..
    Customers always want to do the best for them..in the cheapest way though !!!
    Right then is when you try to find other ways to clean up a system for example..or find cheaper quality parts for replacing....

  15. #15
    tcsbill's Avatar
    tcsbill Guest

    Re: Walk-in Cooler

    ok,just a different frequency of communication

  16. #16
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Walk-in Cooler

    theres no logic in fitting a £130+ component and risking that the drier will be ok,and the electrics havent been damaged with handling a siezed/down to earth compressor,after youve done all the hard work,changing a pot and when u switch on and run it,it doesnt perform,then youll have to degass it to fit a drier,maybe a return visit,and it costs you more because the owner is too tight and doesnt know best, its like you ordering a kebab and finding the bread mouldy,you wouldnt accept it,and hes wasted time putting salad and meat on it,only to have to give you another kebab-they need to accept that the fridgie knows best,you dont tell him how to cook,he shouldnt tell u that he doesnt need a drier.

  17. #17
    Join Date
    Jul 2010
    Location
    manchester
    Posts
    212
    Rep Power
    15

    Re: Walk-in Cooler

    i totally agree i wouldnt eat a mouldy kebeb well maybe depends how drunk i am !!!!!!!
    your only as good as your last job

  18. #18
    Join Date
    Jul 2010
    Location
    manchester
    Posts
    212
    Rep Power
    15

    Re: Walk-in Cooler

    replacing driers, and contactors when replacing compressors is a must !!! it may not come back like a boomerang on the occassion but as many of you are aware it will and not doing this is poor workmanship.
    and fitting a compressor backwards is definatly a no no !!!!! or brazing the capillary into the suction on a compressor how on earth this guy did this i seen once i dont know he must have had a mouldy kebab and not gone straight home.
    your only as good as your last job

  19. #19
    Join Date
    Jul 2010
    Location
    manchester
    Posts
    212
    Rep Power
    15

    Re: Walk-in Cooler

    and if some of you are sat there scratching your heads yes capillary into the suction directly into the danfoss compressor.
    he crimped the suction connection on the pot and f!!!n BRAZED IT.
    and to make double sure brazed the end of the suction up back from the evap.
    YES SCARY AND FU!!!!N BIZZARE what a TOOL.
    your only as good as your last job

  20. #20
    Join Date
    Jun 2008
    Location
    gloucester
    Age
    44
    Posts
    72
    Rep Power
    16

    Re: Walk-in Cooler

    Thats mad mate

Similar Threads

  1. Walk in cooler & walk in coolers
    By henrymark in forum Commercial
    Replies: 3
    Last Post: 18-08-2010, 02:43 AM
  2. Walk in cooler running 48degrees
    By cbslueck in forum Commercial
    Replies: 11
    Last Post: 16-04-2010, 05:00 AM
  3. Design td on walk in cooler
    By IMSTIEN in forum Technical Discussions
    Replies: 2
    Last Post: 01-10-2009, 10:18 PM
  4. Replies: 3
    Last Post: 02-07-2009, 04:47 PM
  5. walk in cooler EVAPORATOR coil icing up
    By kurt854 in forum Fundamentals
    Replies: 5
    Last Post: 14-06-2007, 07:28 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •