    Start Capacitor Avalible



    Hi guys,
    My mate has a compressor (Daewoo HSL27YE-5) which he is using to run a freezer. He only has a i10Honda inverter generater which will only start it if it is a full revs but cant start it at eco idle down. Is there a starting capacitor he could wire in to help during start up loads. If I remember correctly he said he measured the startup amps to be 11, but he can start another compressor that draws 8amps.
    From what I've read sofar there should be a capacitor avalible for it. Or am I wrong?
    Thanks



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Start Capacitor Avalible

    Found some wiring diagrams for that compressor but no details given for the capacitor sizes,... we'll keep looking.

    COMPRESSOR

    Found a fridge service manual which show a 290v / 50 mF capacitor being used.

    Service Manual
    Last edited by Brian_UK; 07-10-2010 at 09:20 PM. Reason: Added a bit.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,762
    Rep Power
    32

    Re: Start Capacitor Avalible

    Quote Originally Posted by crazyman View Post
    Hi guys,
    My mate has a compressor (Daewoo HSL27YE-5) which he is using to run a freezer. He only has a i10Honda inverter generater which will only start it if it is a full revs but cant start it at eco idle down. Is there a starting capacitor he could wire in to help during start up loads. If I remember correctly he said he measured the startup amps to be 11, but he can start another compressor that draws 8amps.
    From what I've read sofar there should be a capacitor avalible for it. Or am I wrong?
    Thanks
    Hi there, a 27YE-5 is a 1/3 HP compressor, same capacity as a Danfoss FR11A. The EU10-I generator is an excellent power source( use it all the time for work) but it is rated at 850watts or 3.7amps/230volts and i would not go pushing its limits. You would be far better off using the EU20-I, that has double capacity.. mike.

  4. #4
    crazyman's Avatar
    crazyman Guest

    Re: Start Capacitor Avalible

    Thanks for your replys.
    Mike, Shouldnt the starting capacitor hold/deliver the required amps during startup? Then the eu10 can idle down and run it easily.

Similar Threads

  1. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  2. run / start capacitor issue
    By mvtop in forum Fundamentals
    Replies: 5
    Last Post: 13-09-2010, 12:36 AM
  3. Carrier 850 MT start problem
    By Maya in forum Transport
    Replies: 5
    Last Post: 18-05-2010, 10:49 PM
  4. Replies: 5
    Last Post: 08-11-2009, 06:10 PM
  5. Hermetic analyzer " ANNIE" how do they work
    By kengineering in forum Tools and Calculators
    Replies: 11
    Last Post: 02-03-2008, 07:10 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •