    Iliketolearn's Avatar
    Iliketolearn Guest

    COP in catalogue vs actual (VRF)



    I try to compare COP between VRF inverter and VRF digital scroll. Basically I check from catalogue. COP of Daikin VRVIII are quite higher than Digital scroll but I receive some actual test data from Emerson Copeland to show that COP of digital scroll is better.
    There is one comment that the power consumption in catalogue is not included the inverter loss because they test VRF inverter by suppling power to compressor with fix frequency (no inverter loss as per the actual usage). I check details in Daikin VRV III technical manual, it has remark - Power Input : kW(Comp.+Outdoor fan motor). Do anyone can confirm the fact for this? If COP in catalouge are actually not included inverter loss, then how much the additional power consumption for inverter loss by approximately.



  2. #2
    Join Date
    Oct 2008
    Location
    Philippines
    Age
    46
    Posts
    10
    Rep Power
    0

    Re: COP in catalogue vs actual (VRF)

    I think that the inverter base vrf or vrv finally found their match with the digital scroll base vrf..thanks to copeland. I have attended seminar on either of this technology and either of them is poking on each other.
    I'll put my bet on the digital scroll (though the term digital is quite confusing..since both are digitally manipulated) because its the newer technology and should post as the better one.
    Hope someone can post a factual data on this two variation of vrf technology..

    Keep up the good work guys!!

  3. #3
    Join Date
    Feb 2010
    Location
    England
    Age
    59
    Posts
    243
    Rep Power
    16

    Re: COP in catalogue vs actual (VRF)

    Quote Originally Posted by Iliketolearn View Post
    I try to compare COP between VRF inverter and VRF digital scroll. Basically I check from catalogue. COP of Daikin VRVIII are quite higher than Digital scroll but I receive some actual test data from Emerson Copeland to show that COP of digital scroll is better.
    There is one comment that the power consumption in catalogue is not included the inverter loss because they test VRF inverter by suppling power to compressor with fix frequency (no inverter loss as per the actual usage). I check details in Daikin VRV III technical manual, it has remark - Power Input : kW(Comp.+Outdoor fan motor). Do anyone can confirm the fact for this? If COP in catalouge are actually not included inverter loss, then how much the additional power consumption for inverter loss by approximately.

    What you have to remember is COP is measuring energy imparted in the compression cycle (work done) not total energy consumed.

    Do not confuse COP with EER (energy effiency ratio)

    COP only compares Refrigeration Effect divided by Work Done or Heat Rejected divided by Work Done..

    EER compares total cooling capacity divided by Total Energy used or Heating capacity divided by Total Energy used.

    All the best

    coolrunnings

    .
    Last edited by cool runings; 16-10-2010 at 10:06 PM.

  4. #4
    mortan's Avatar
    mortan Guest

    Re: COP in catalogue vs actual (VRF)

    hello this is mortan I really like your site.

  5. #5
    Join Date
    Aug 2008
    Location
    OMAN
    Age
    46
    Posts
    16
    Rep Power
    0

    Re: COP in catalogue vs actual (VRF)

    really interesting

  6. #6
    Join Date
    Mar 2007
    Location
    INDIA
    Age
    41
    Posts
    31
    Rep Power
    0

    Re: COP in catalogue vs actual (VRF)

    Hi,

    The invertor loss can be 3 to 5 % depends on the drive design.

    Ravi

Similar Threads

  1. Actual air-conditioning operation and its cycle
    By narongwit12 in forum Air Conditioning
    Replies: 6
    Last Post: 03-02-2011, 12:09 AM
  2. Actual Expansion Valve Process
    By AastroGuru in forum Fundamentals
    Replies: 11
    Last Post: 03-02-2009, 10:53 AM
  3. HCFC and HFC mix. Whats the actual detriment?
    By TheGinjaNinja in forum Technical Discussions
    Replies: 1
    Last Post: 02-12-2008, 02:21 PM
  4. CARRIER product catalogue.
    By Jacek in forum Refrigeration Books
    Replies: 2
    Last Post: 30-03-2007, 06:27 PM
  5. Determining the actual pumping efficiency
    By shogun7 in forum Training
    Replies: 0
    Last Post: 24-01-2005, 03:13 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •