    Connection and Disconnection of Gauges



    Im getting confused with the 'correct' way to connect and disconnect a set of gauges. Im not too sure wether its best to have the system running or off? Please help!



  2. #2
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19

    Re: Connection and Disconnection of Gauges

    hi xeomus, if you back seat the discharge valve, and with the charging line< middle< line connected to a bottle, open both gauge valves and all will equilise to the suction psi, then back seat the suction valve, to go one better , if you have the pisilities to pump down the system before you back seat the suction valve
    a lot of tecs use the quick coupling on the end of the gauge lines but the gas that is trapped in the gauges usually just escapes,
    Last edited by sedgy; 05-10-2010 at 06:21 PM. Reason: made a balls - oops speling pistake

  3. #3
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    712
    Rep Power
    19

    Re: Connection and Disconnection of Gauges

    Ideally the system is better not running as this reduces the pressure your exposing yourself to,
    the method i prefer is to use line with ball valves
    1 close high side ball valve
    2 open manifold to let pressure from the high side to the low side
    3 rub lines to warm refrigerant and remove as much as possible from lines
    4 close low side ball valve
    5 disconnect both lines

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Connection and Disconnection of Gauges

    Just to add a third option... assuming that you have ball valves or a quick connector on the high side..

    Shut the high side ball valve (disconnect quick connector), open the high and low valves on the manifold to reduce the line/gauge pressures back to the lower suction pressure.

    Close valves on manifold and then disconnect from the low side.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Connection and Disconnection of Gauges

    Quote Originally Posted by Brian_UK View Post
    Just to add a third option... assuming that you have ball valves or a quick connector on the high side..

    Shut the high side ball valve (disconnect quick connector), open the high and low valves on the manifold to reduce the line/gauge pressures back to the lower suction pressure.

    Close valves on manifold and then disconnect from the low side.
    4th option
    As Brian said above but then before you disconnect the low side, put the system into pump down (close the liquid line valve) then disconnect your low side gauge when the pressure reaches 2-3 psig.

  6. #6
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Connection and Disconnection of Gauges

    ^^ Good point Frank ^^
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  7. #7
    Join Date
    Jul 2007
    Location
    USA
    Posts
    23
    Rep Power
    0

    Re: Connection and Disconnection of Gauges

    Do they have special manifold gauges with very small inner diameter hoses for use with systems that only holds 250g of refrigerant at most, like home refrigerator?

  8. #8
    Join Date
    Nov 2009
    Location
    UK
    Age
    33
    Posts
    7
    Rep Power
    0

    Talking Re: Connection and Disconnection of Gauges

    Cheers Fellas,

    Sorry i never got back to any of you, my college work has been hectic!

    I appreciate all you explained to me though!

    So thanks again

    Xeomus