    Re: Bitzer oil problem



    The Bitzer screws I've seen had an oil pressure control but not an oil level.


    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  2. #52
    Join Date
    Apr 2008
    Location
    UK
    Posts
    215
    Rep Power
    17

    Re: Bitzer oil problem

    I think it's a oil level switch.

    Harry, have you checked the superheat in cooling, both at the expansion valve & compressor suction ??
    Are you familiar with how to do this ??

  3. #53
    Join Date
    Dec 2008
    Location
    greece
    Age
    47
    Posts
    227
    Rep Power
    16

    Re: Bitzer oil problem

    Here you can see in bottom the oil level switch.
    Yes gingerair, i know how to do this,but the compressor works only for one minute,then it stops.
    Attached Images Attached Images

  4. #54
    Join Date
    Jul 2008
    Location
    KENYA
    Age
    49
    Posts
    35
    Rep Power
    0

    Re: Bitzer oil problem

    Quote Originally Posted by Andy View Post
    Hello Harry,

    add enough oil to bring you to the minimum operating level.
    Run the plant on either cooling or heating, the cycle that you have no oil problems in.
    Watch the oil level until it reaches the highest running level that you can see.
    Stop the plant, drain the oil.
    Start the plant run allow the oil level to rise again. Repeat until you take out the oil you put in.


    Kind Regards Andy D

    Makes the most sense to me.... you need to obtain more information in the safest possible way and that means... add the oil and run the system and see the behaviour.... does the oil run out again ? does it trip on the oil pressure switch ?if it does .. at what temperature does it happen ? ...

  5. #55
    Join Date
    Jul 2009
    Location
    Brisbane
    Age
    67
    Posts
    79
    Rep Power
    15

    Re: Bitzer oil problem

    I think Andy might be on the money. If the oil comes back on cooling you may need to check condenser design for cooling and or put a timer set to bring on the cooling mode occasionaly to return the oil.

  6. #56
    Join Date
    Dec 2008
    Location
    greece
    Age
    47
    Posts
    227
    Rep Power
    16

    Re: Bitzer oil problem

    Hello to everybody.I went to the chiller today.I put oil in the system about 20lt.[The compressor takes 22lt].
    The oil level switch was reset,but i cannot see the oil level in the sight glass.I was watching it during the filling.What could had happened?

    I started the system for about twenty minutes,still no level in sight glass,and have the
    below measurements in heating:

    HP=260PSI
    LP=42,4PSI
    SUPERHEAT AT SUCTION VANE=9C
    SUBCOOLING AT FILTER DRIER=8.7C
    ENTERING WATER=37.7C
    LEAVING WATER=39.7C
    DISCHARGE TEMP=80C
    OUTDOOR TEMP=10C

    I checked the oil return from the accumulator.No restriction or oil there.

  7. #57
    Join Date
    Oct 2007
    Location
    malaysia
    Posts
    8
    Rep Power
    0

    Re: Bitzer oil problem

    Hi Harry,

    Just a concern have your problem solved?

  8. #58
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Bitzer oil problem

    I'm interested too Harry
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  9. #59
    Join Date
    Dec 2008
    Location
    greece
    Age
    47
    Posts
    227
    Rep Power
    16

    Re: Bitzer oil problem

    Hello guys!Sorry for not answering!I put oil in compressor but the alarm was still engaged.So i replaced the oil level switch and the problem solved!Thanks everybody for the help!

Page 2 of 2 FirstFirst 12

Similar Threads

  1. MFI AMP6855 defrost problem
    By gliderpilot47 in forum Domestic
    Replies: 4
    Last Post: 12-01-2011, 12:11 PM
  2. A strange problem
    By MuhengineeR in forum Air Conditioning
    Replies: 14
    Last Post: 27-10-2010, 05:21 PM
  3. Bitzer screw - not pumping down
    By charkkol in forum Trouble Shooting
    Replies: 11
    Last Post: 05-10-2010, 01:07 AM
  4. Danfoss ICAD/ICM Valve problem
    By piewie in forum NH3
    Replies: 3
    Last Post: 11-09-2010, 09:20 AM
  5. problem with GE air con power problem
    By Richie101 in forum Air Conditioning
    Replies: 6
    Last Post: 05-11-2009, 04:00 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •