05-10-2010, 05:14 PM #1
Bitzer oil problem
I have a heat pump water chiller with two bitzer screw
CSH8561-125Y-40D.The one compressor shows alarm with loss of oil.I cannot see oil in sight glass.Where do you beleive that the oil have gone?R407C in the system.
-
05-10-2010, 08:23 PM #2
Re: Bitzer oil problem
Hi Harry
You'll have to give more info, but if the loss occurs in heating possibly the condenser..
-
06-10-2010, 10:34 AM #3
Re: Bitzer oil problem
Have you tried looking around, above or below? If no oil is on the walls, ceiling or floor, then it must be in the circuit.
-
06-10-2010, 03:01 PM #4
Re: Bitzer oil problem
Hello guys. There is no oil outside the system.
The chiller is working in cooling.
LP= 4 bar
HP= 16 bar
-
06-10-2010, 04:43 PM #5
Re: Bitzer oil problem
Is there a liquid receiver? How big it is?
-
06-10-2010, 04:46 PM #6
Re: Bitzer oil problem
Hi nonickname.There is only a suction acumulator.
-
06-10-2010, 06:10 PM #7
-
06-10-2010, 06:35 PM #8
Re: Bitzer oil problem
The system stops from oil alarm.
What should i do?Fill with oil and monitor the system?
-
07-10-2010, 06:21 PM #9
Re: Bitzer oil problem
No, don't add any oil. The oil is in the system. You just need to drain it out the accumulator.
-
07-10-2010, 06:38 PM #10
Re: Bitzer oil problem
If he drains the accmulator, it may fill again. You need to find out why the accumulator filled, or you need to add an oul return tube from the bottom of the accumulator to the suction pipe near the comnpressor if thereisn't a proper oil return design now.
-
07-10-2010, 06:42 PM #11
Re: Bitzer oil problem
Hello guys.Thanks for replies.
There is a return line in suction accumulator.
-
07-10-2010, 06:46 PM #12
Re: Bitzer oil problem
Could that problem appeared if the system is overcharged?
-
08-10-2010, 08:39 AM #13
Re: Bitzer oil problem
I think that this problem is more likely to happen in a system with low suction superheat.
-
08-10-2010, 01:03 PM #14
Re: Bitzer oil problem
Maybe you are right nonickname.
But what is the solution??I cannot drain the accumulator.
-
08-10-2010, 04:07 PM #15
Re: Bitzer oil problem
Warm up the accumulator and start the compressor, crossing your fingers that it doesn't seize. Eventually some oil will start returning.
-
08-10-2010, 07:22 PM #16
Re: Bitzer oil problem
I have to bypass the oil floter control.How much time should i do that??
-
08-10-2010, 11:01 PM #17
Re: Bitzer oil problem
Least possible.
Listen up: you are going to trash the compressor, you know that, don't you?
-
09-10-2010, 10:25 AM #18
Re: Bitzer oil problem
Yes nonickname.Any other option??
-
09-10-2010, 12:23 PM #19
Re: Bitzer oil problem
Drain the oil.
-
10-10-2010, 08:57 AM #20
Re: Bitzer oil problem
Hello Harry,
add enough oil to bring you to the minimum operating level.
Run the plant on either cooling or heating, the cycle that you have no oil problems in.
Watch the oil level until it reaches the highest running level that you can see.
Stop the plant, drain the oil.
Start the plant run allow the oil level to rise again. Repeat until you take out the oil you put in.
If the problem is in heating limit the amount of heating time and add an oil harvest or a perriod of cooling to bring back the oil.
Best check what way the condenser is circuited as an evaporator during heating, this may be a problem, or as nonickname state you may need to fit the suction accumulator on the evaporator is of the four way reversing valve.
Kind Regards Andy DIf you can't fix it leave it that no one else will:rolleyes:
-
10-10-2010, 09:10 AM #21
Re: Bitzer oil problem
Hi Andy.Thanks for reply.
I will add oil and check the operation.Do you know where i can find oil CPI SOLEST 170??
-
10-10-2010, 05:49 PM #22
Re: Bitzer oil problem
If there is a drain line on the suction accumulator, install a 3/8" solenoid valve in the line and bring it back to the suction before the compressor.
Let the solenoid valve only be energised when the compressor is running.
If this does not help, install an oil seperator in the discharge line with the oil return line before the compressor suction fitting. Install a solenoid valve in the oil return line.
Install an unequal repeating timer to operate the solenoid valve. 3 seconds on, 10 - 15 seconds off. This circuit must also be in operation only when the compressor is running. Had the same problem and got this information from Bitzer South Africa.
Another alternative is to raise your condensing temperature by about 10 deg. C, to try to get the oil back, even through the suction accumulator. This is only a temporarily solution, as you want to keep your condensing temperature to design criteria.
Try your local Bitzer office/agent for oil or go to CPI Engineering.
Please remember! If there are no oil leaks, the oil is in the system. Do not add oil that can overfill a system. Monitor your oil levels for the first few days and remove excess oil.
Good Luck!I am not always right, but I'm never wrong!
-
10-10-2010, 06:04 PM #23
Re: Bitzer oil problem
Hi Eeram.As i said before there is a line that connects the bottom of the accumulator with suction before compressor but without a solenoid valve.There is another one compressor in circuit with no problem.The compressor stops from oil level alarm.So i have to put oil in system to start.
-
10-10-2010, 09:27 PM #24
Re: Bitzer oil problem
Not sure if its same set up , but had similar problem & found main oil line to compressor solonoid suspect .
When cycled off oil migated into compressor & suction line
-
10-10-2010, 10:06 PM #25
Re: Bitzer oil problem
If you fit a solenoid in the oil return line from the accumulator also fit a sight glass after it so that oil flow, or lack of it can be observed..
-
11-10-2010, 06:30 PM #26
Re: Bitzer oil problem
Are the two compressors controlled by one controller? Are they running as lead & lag? What capacity control do they use?
I am not always right, but I'm never wrong!
-
11-10-2010, 06:39 PM #27
Re: Bitzer oil problem
They are controlled by one controller.They work both together or one at a time.Their capacity is minimum 50% and above.
-
11-10-2010, 07:06 PM #28
Re: Bitzer oil problem
How many expansion valves / liquid line solenoid valves do you have in your system ?
-
11-10-2010, 07:13 PM #29
Re: Bitzer oil problem
I have one expansion valve for cooling,two for heating.No liquid line solenoid valve
-
11-10-2010, 08:41 PM #30
Re: Bitzer oil problem
suspecting some sort of restriction on or near the expansion valve... does the oil return when the system is off ? or is it constantly low ?
-
11-10-2010, 08:52 PM #31
Re: Bitzer oil problem
Hi Ima.No it doesn't return.
-
11-10-2010, 09:06 PM #32
Re: Bitzer oil problem
Nonickname gets it right when he says the oil is in the system.(if it was there originally and there is no visible trace of it coming out). question is where ?.... was leaning to the idea of an overcharged system...the expansion valve closes sharply, oil migrates from compressor to condenser as the suction side moves to very low pressure.. but has to be ruled out as normally if that was the case.. the oil would return back to the compressor in the off cycle..
-
11-10-2010, 09:15 PM #33
Re: Bitzer oil problem
unless the expansion valve itself, depending on the cycle you are using, was blocked or restricted
-
12-10-2010, 06:52 AM #34
Re: Bitzer oil problem
I am more inclined the problem is at the oil separator, either the check vav after oil separator is allowing liquid to develop in separator during off cycle or else the separator heater is not keeping the oil hot, the oil will disappear into system real quick with either problem.
-
12-10-2010, 12:24 PM #35
Re: Bitzer oil problem
There is no oil separator in system maggoo.
That bitzer model has an internal one.
-
12-10-2010, 05:30 PM #36
Re: Bitzer oil problem
Yes, there is a separator, which incidentally is built in. Magoo advices are good.
-
12-10-2010, 06:22 PM #37
Re: Bitzer oil problem
The compressor with the oil problem, does it run lower on capacity than the other one? Still needs to know how the controller operates.
Are they both running, then one compressor cycles off and the one with the oil problem runs and goes down to 50%?
What is the oil pressure and what is the discharge/condensing pressure?
Can you tell the operating hours of these compressors?I am not always right, but I'm never wrong!
-
12-10-2010, 07:14 PM #38
Re: Bitzer oil problem
That is what i meant nonickname it has a buid in separator.
Magoo i will check what you said.Eeram the compressors run together ,one stops the other continues until it catches the set point.Then when the temp rises the other begins to work.The controller distributes the time and starts exactly the same.The minimum working capacity of both compressors is 50%.I do not have the working hours of the compressors.The working pressures of machine are:
LP:60PSI
HP:230PSI
R407C
-
12-10-2010, 08:31 PM #39
Re: Bitzer oil problem
Just to clarify Harry,
Is it a common discharge & suction lines, inc one common suction accumulator, for both compressors ??
-
12-10-2010, 08:36 PM #40
Re: Bitzer oil problem
Hi Gingerair!Two different circuits.
-
13-10-2010, 12:13 AM #41
Re: Bitzer oil problem
Ok, so you've got 2 completely independent circuit's, 2 x condensers, 2 evaps or 1 x split evap ?
Is the oil in the faulty system definitely the correct type ?
Is the oil heater working ?
Does the oil loss occur in both heating & cooling ?
If you're going to run the compressor that looses oil, make sure the oil level is above the min level before starting. Do not do this too many times as any excess oil will have to be drained.
Also do not either start or allow a compressor with excess oil in to run..
As i said, if you can't get the 'missing' oil to return, don't keep trying to run the compressor.
You're then going to have to drain it from wherever it is in the system, even if this means a decant..
-
13-10-2010, 06:52 AM #42
Re: Bitzer oil problem
2 independent circuits,1 evaporator split to two circuits,two condensers.Oil heater is working.Oil loss occured in cooling.Oil is the correct type.The above pressures are in cooling.The system stops from oil level control.
-
13-10-2010, 09:19 AM #43
Re: Bitzer oil problem
Does the oil loss also occur in heating ?
Is the oil loss a new problem or has it always occurred ?
How fast is the oil loss when the comp runs ?
Your going to have to start taking temperatures & pressures to check that the plant is operating correctly..Last edited by Gingerair; 13-10-2010 at 09:31 AM.
-
13-10-2010, 02:52 PM #44
Re: Bitzer oil problem
It is the first time the alarm occured.I cannot see oil in the oil sight glass,even if the machine is stopped.The pressures of the system are the above for about 1 minute of work until it stoppes from alarm.
-
13-10-2010, 09:07 PM #45
Re: Bitzer oil problem
Are the pressures for both machines or only the machine which has the oil problem ?
-
13-10-2010, 09:08 PM #46
Re: Bitzer oil problem
Sorry... Have you checked the pressure indicated is coming from the circuit having the oil problem ?
-
13-10-2010, 09:17 PM #47
Re: Bitzer oil problem
The pressures are from the faulty system.
-
14-10-2010, 09:51 AM #48
Re: Bitzer oil problem
TEV's or EEV's as expansion valves?
Brand of machine?It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
14-10-2010, 09:53 AM #49
Re: Bitzer oil problem
Is the oil alarm coming from the special screw-Kriwan?
It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
14-10-2010, 03:50 PM #50
Re: Bitzer oil problem
Hi peter.There is an oil level mechanism in the side of the compressor near the sight glass.
Similar Threads
-
MFI AMP6855 defrost problem
By gliderpilot47 in forum DomesticReplies: 4Last Post: 12-01-2011, 12:11 PM -
A strange problem
By MuhengineeR in forum Air ConditioningReplies: 14Last Post: 27-10-2010, 05:21 PM -
Bitzer screw - not pumping down
By charkkol in forum Trouble ShootingReplies: 11Last Post: 05-10-2010, 01:07 AM -
Danfoss ICAD/ICM Valve problem
By piewie in forum NH3Replies: 3Last Post: 11-09-2010, 09:20 AM -
problem with GE air con power problem
By Richie101 in forum Air ConditioningReplies: 6Last Post: 05-11-2009, 04:00 PM