05-10-2010, 03:25 AM #1
short cycling compressor
i have a walk in freezer problem it is short cycling the head preesure is 150 psig the thermostat is new and is closed contacts the liquid line solenoid is energized yet the compressor is cycling the gauges read low side on at 15psig off at 3psig and it just keeps cycling off and on the head pressure gauge is at 150 psig i disconnected the condenser fans and the head pressure went up to 250 and also the suction pressure rose to 30 psig then the unit acted normal i reconnected condenser fans and the unit ran normal for a couple of days what did i do by doing this i have been told its a bad head master control but i dont understand if the head preesure is 150 psig at the service port that is after the reciever i dont get it can you help me
-
05-10-2010, 09:42 AM #2
Re: short cycling compressor
hi red green,
giving us the psi , and not the gas you are on, dose not give us much to work on ,
your problems could be, low on gas faulty stat, over condencing< is there con, fan controle?< but could do with ambiant temp .room temp air on - air off just to start with ,
-
05-10-2010, 10:13 AM #3
Re: short cycling compressor
there could just be a shut valve somewhere that youv'ed missed by accident, hows the expansion device? not blocked?
-
05-10-2010, 11:54 PM #4
Re: short cycling compressor
Redgreen, unit cycles on low pressure because of insufficient refrigerant flow or volume so by increasing head pressure, your forcing more volume through the circuit. sounds to me like expansion valve restriction.. mike.
-
06-10-2010, 12:20 AM #5
Re: short cycling compressor
I'm with the others. Without a refrigerant type, I'm left mostly guessing.
Given the information that you've given us, though, I'd first look at a low charge condition.
Does the unit have a sightglass?
-
06-10-2010, 09:44 AM #6
Re: short cycling compressor
sounds like its on 507?
-
08-10-2010, 05:41 AM #7
Re: short cycling compressor
You didn't say when the problem started. Was the unit recently serviced? I would double check all service valves and make sure low side valves are not closed or partially shut down if you are taking low pressure control access from a takeoff that should be open at all times to read constant pressure. I did exactly that once myself. Had a multi-valve takeoff on a service valve port that was closed so far it just went up and down ....on and off. Hey.....we all miss something.
Don't leave it like you found it.....Leave it like it should be !!!
Similar Threads
-
Daikin split short cycling after leak repaired
By Tayters in forum Air ConditioningReplies: 16Last Post: 17-06-2010, 12:23 PM -
Short Cycling
By ferret82 in forum CommercialReplies: 4Last Post: 12-12-2009, 10:49 PM -
compressor / electrical problem
By Northdude in forum CommercialReplies: 6Last Post: 17-01-2009, 10:24 AM -
Compressor Cycling
By nlester in forum CommercialReplies: 2Last Post: 22-05-2007, 04:20 PM -
Walk in Cooler (short cycling)
By Brandon in forum Trouble ShootingReplies: 11Last Post: 05-05-2003, 11:43 AM