    Toshiba



    Hi

    Is it just toshiba who solder a 5 amp fuse on there P.C.B. board.So annoying,I think it is a real con,so I soldered a fuse holder in place,do they really expect people to buy a new P.C.B board?Why is there also a resistor with a glass case round it.


    Regards Bernard



  2. #2
    Join Date
    Jan 2005
    Location
    england
    Age
    48
    Posts
    64
    Rep Power
    20

    Re: Toshiba

    Hi

    I have been told you can get "piggy back" fuse holders from somewhere like RS.
    Thse clip onto the connections of the broken fuse and you then insert a new fuse.

  3. #3
    Join Date
    Dec 2004
    Location
    Australia
    Age
    52
    Posts
    519
    Rep Power
    20

    Re: Toshiba

    No not just Toshiba...

    Daikin are soldering fuses on the boards of their latest inverter wall mounts. 3.15a

    Also found an LG with a soldered on fuse.

    Just solder on a new fuse.

    Usually if fuse is blown then board is probably no good.Varistor might be shorted or various other problems.

  4. #4
    Join Date
    Mar 2004
    Location
    UK
    Posts
    624
    Rep Power
    21

    Re: Toshiba

    Hi

    Its not so easy to solder a new fuse in as you tend to find the solder within the fuse melts even with a heat sink.If you buy a new board and that fuse blow it can become expensive.

    Regards Bernard

  5. #5
    Join Date
    Oct 2004
    Location
    Scotland
    Age
    46
    Posts
    1,454
    Rep Power
    21

    Re: Toshiba

    Hi Bernard

    Why not just take the old fuse off and solder in some 5amp fuse wire?
    IF AT FIRST YOU DON`T SUCCEED.
    DESTROY ALL EVIDENCE THAT YOU TRIED!
    and go get a cuppa

  6. #6
    Join Date
    Jan 2005
    Location
    england
    Age
    48
    Posts
    64
    Rep Power
    20

    Re: Toshiba

    Why not use my idea,am I invisible?

  7. #7
    Join Date
    Mar 2004
    Location
    UK
    Posts
    624
    Rep Power
    21

    Re: Toshiba

    Who said that?

    Sorry I couldn,t resist it,I had a quick look through R.S cat today but could not see them,they would be ideal.

    Regards Bernard

  8. #8
    Join Date
    Jul 2005
    Location
    Ireland
    Age
    56
    Posts
    164
    Rep Power
    19

    Re: Toshiba

    Hi B
    normally when a unit has a soldered fuse on the board there is a second plug for the offending cable or cables on the secondary side of the fuse IE. u get one chance if u blow the fuse u can bypass it. If the Varistor is blown just break it off the board its only there to blow in case of an overload or bad wiring. Manufacturers don't usually tell you this. Dont know how many mitsu boards i changed until I learned this simple fact. Mitsu dont use soldered fuses but the Varistors do blow.
    C Ya
    T

Similar Threads

  1. Toshiba Digital Inverter range?
    By Slim R410a in forum Air Conditioning
    Replies: 19
    Last Post: 18-10-2010, 02:45 PM
  2. Toshiba Warranty
    By gwilliamson in forum Air Conditioning
    Replies: 1
    Last Post: 17-05-2006, 05:59 PM
  3. Replies: 1
    Last Post: 19-02-2006, 12:08 AM
  4. Toshiba A/C Compressor size
    By Chris2005 in forum Air Conditioning
    Replies: 9
    Last Post: 10-04-2005, 09:21 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •