    R134a convert to R507



    Hi onboard my ship we are going to convert our provision cooling plant from R134a to R507.

    We are told this will give us more cooling power.

    Does anyone know how many % more we get from this convertion ?



  2. #2
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,044
    Rep Power
    19

    Re: R134a convert to R507

    If you have 100 kW you can count about 150 kW, depending on the regime the compressors are working on.

    Pay attention to the compressor motors and the condenser (with R507 there will be more needs of that elements).
    To make progress is never good enough, I want to do better and better and better

  3. #3
    Join Date
    Jun 2010
    Location
    Denmark
    Posts
    12
    Rep Power
    0

    Re: R134a convert to R507

    We are going to mount a cooling pump with larger flow.
    Is the motor going to use more amps ?

    (is this due to higher pressure or what)

  4. #4
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,044
    Rep Power
    19

    Re: R134a convert to R507

    What motor you are talking about? Compressor motor?
    To make progress is never good enough, I want to do better and better and better

  5. #5
    Join Date
    Jul 2009
    Location
    Brisbane
    Age
    67
    Posts
    79
    Rep Power
    15

    Re: R134a convert to R507

    The motor if sized corectly for R134a will be too small for R507 due to the increased mass flow. If you are using a shell and tube condenser it may still not be suitable even with increased pump flow and may also need changing. If you are using medium temperature you are better to stick with R134a and upgrade the plant. You may also find R507 hard to obtain in some ports.

Similar Threads

  1. Freeze Spray -- Venting R134a Illegal?
    By Z2TT in forum Chit Chat & Service Stories
    Replies: 10
    Last Post: 29-07-2010, 09:29 PM
  2. R507 in an R134a compressor: any danger?
    By DaBit in forum Technical Speculations
    Replies: 30
    Last Post: 21-12-2009, 01:44 AM
  3. convert r134a to R-404a
    By proby in forum Refrigerants
    Replies: 5
    Last Post: 08-06-2009, 01:20 AM
  4. [Autocascade] Only a project ATM
    By before in forum CPU Overclockers
    Replies: 1
    Last Post: 07-05-2009, 11:13 AM
  5. R507 in an R134a compressor: system design
    By DaBit in forum Technical Speculations
    Replies: 17
    Last Post: 01-05-2003, 09:25 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •