    Dehumidifier capacity



    We need a portable dehumidifier unit for a production room; room volume is 50 m3, humidity range need to control 40 to 45%, temperature 20 to 24 is controlled by FCU (fan coil unit).
    We need to calculate dehumidifier capacity? & how can we calculate it? Formula?
    Is their any thumbs rule?



  2. #2
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Dehumidifier capacity

    What's the moisture ingress?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  3. #3
    Join Date
    Mar 2010
    Location
    Bangladesh
    Age
    40
    Posts
    151
    Rep Power
    15

    Re: Dehumidifier capacity

    Its come with the cooled air of Fan Coil Unit.

  4. #4
    Join Date
    Nov 2004
    Location
    China
    Posts
    176
    Rep Power
    20

    Re: Dehumidifier capacity

    A FCU does not make humidity. There must be other sources. Fresh air supply, people, processes that produce moisture. Look for these in order to calculate moisture production.

  5. #5
    Join Date
    Mar 2010
    Location
    Bangladesh
    Age
    40
    Posts
    151
    Rep Power
    15

    Re: Dehumidifier capacity

    Quote Originally Posted by charlie n View Post
    A FCU does not make humidity. There must be other sources. Fresh air supply, people, processes that produce moisture. Look for these in order to calculate moisture production.
    Actually most of the time our environment contain humidity around RH:72%, and cooling system for the room can decrees humidity level around RH:60% (as if its only for cooling not humidifying) but our requirement is below RH:45 %,hope its clear you.

  6. #6
    Join Date
    Jul 2009
    Location
    uae
    Age
    40
    Posts
    4
    Rep Power
    0

    Re: Dehumidifier capacity

    hi, you need maintain low RH at low temp.so you must go through dessicant type.i calculate with your info. To maintain 20c 40%rh at this atmos condition 46c dbt and 30c wbt with 2 people load. you should remove moisture from room is 51 lit/day.just visit our web.(bryair.com)

  7. #7
    Join Date
    Mar 2010
    Location
    Bangladesh
    Age
    40
    Posts
    151
    Rep Power
    15

    Re: Dehumidifier capacity

    Quote Originally Posted by kumar243 View Post
    hi, you need maintain low RH at low temp.so you must go through dessicant type.i calculate with your info. To maintain 20c 40%rh at this atmos condition 46c dbt and 30c wbt with 2 people load. you should remove moisture from room is 51 lit/day.just visit our web.(bryair.com)
    Thanks, it will help me lot

  8. #8
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Dehumidifier capacity

    Kumar,

    How can you calculate if you don't know what the moisture ingress is? You don't know the conditions from the incoming air (VERY important) and you even don't know what's extracted out of this room.

    40% at 20° C can easily be maintained with a condensation dryer but I suspect you that Bryair doesn't make these units, only desiccant types.

    An I bet Bryair's smallest model is a 51l/day.

    For a room like this, normal conditions, I should guess 10l/day, not even worth calculating this.

    BTW, making publicity is not allowed
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  9. #9
    Join Date
    Jul 2009
    Location
    uae
    Age
    40
    Posts
    4
    Rep Power
    0

    Re: Dehumidifier capacity

    we calculate return condition is room condition.If any one need proper solution,they should give proper details.Like what is the application,surrounding condition,construction of room,fresh air condition and people load. then bryair smallest model is 28 lit/day on normal comfort condition. condensation dryer you means ref type dehumidifier,if you meens,dew point in that condition is 6 c.if you go to low temp it will form ice.if not you will raise the air changes.its more difficult to do 20 c 40% rh.incase you want 24c 40% its very easy to maintain through ref type and that is economical also.

Similar Threads

  1. Replies: 3
    Last Post: 29-04-2010, 10:30 AM
  2. How to increase pool heater capacity?
    By Drew in forum Commercial
    Replies: 104
    Last Post: 13-06-2009, 05:25 AM
  3. Sensible Heat Factor / capacity of Inverter split Systems at part load?
    By Greengrocer in forum Technical Speculations
    Replies: 31
    Last Post: 09-02-2009, 04:57 PM
  4. R-407C and Coil Capacity
    By glabah in forum Refrigerants
    Replies: 5
    Last Post: 03-06-2006, 11:36 AM
  5. TEV capacity related to pressure drop
    By DaBit in forum CPU Overclockers
    Replies: 8
    Last Post: 06-12-2002, 05:11 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •