    Unhappy Flare nuts



    I carry out regular ppm on a vast range of equipment but never before have I came across the strange phenomenon of flare nuts cracking.Especially on air-con units.
    The equipment I am referring to is of a well known manufacturer.The kit is 3 pipe vrf (R407C).
    Every now & again during maintenance checks I will come across oil patches on ceiling tiles or fault codes initiated @ remote controllers.Upon inspection of fan coil (ducted type) it is always the 1/2" gas pipe flare that cracks, though on other occassions I have also found the 3/8" liquid line flare cracked on the c/h box. As you can imagine, the process for repairs on this kit is rather expensive and in turn the customers can become very irritated
    I am sure that the manufacturer is aware of this problem as I have conversed with an engineer from their technical team whom had informed me of this type of problems on various sites in the u.k.
    Unfortunately though nothing has ever been done about it and as the old saying goes 'it's been swept under the carpet'.
    It has been a while now without a cracked flare on this kit but, recently I have came across cracked flares on split-type a/c (2 other well known manufacturers).
    The 1st split had the 3/8" liquid line flare cracked @ indoor cassette and the 2nd split had the 3/4" suction line flare cracked @ condensing unit.Very strange.
    So,I am now thinking if there is some sort of link with flare nuts and R407C as the split-type units are also operating on this refrigerant!
    I am also now thinking that this job aint what it all cracked up to be

    Regards

    Jase



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Flare nuts

    Hi Jase,

    I have seen many times these cracked nuts on small splits.

    I don't have a clue why does it happened, the only thing that I can think of, is the expanding and shrinking of the brass during heating or cooling.

    Chemi

  3. #3
    Join Date
    Jun 2005
    Location
    Stoke on Trent
    Age
    62
    Posts
    588
    Rep Power
    19

    Re: Flare nuts

    I have had it many times on R22 over the years particular on wall mounts and they are always real difficult to repair after installation. Every single wall mount I install with no exceptions, I cut the flare nuts from the back of the wall mount and solder the pipes instead. It is the expansion and contraction of the materials and as most materials are recycled..........

  4. #4
    Join Date
    Aug 2001
    Location
    UK
    Posts
    1,046
    Rep Power
    24

    Re: Flare nuts

    The use of flares should not only be discouraged but eradicated completely. It can be done.
    ________
    marijuana strains
    Last edited by Argus; 07-02-2011 at 08:22 AM.

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Flare nuts

    Yep, suction flares are the worst; moisture gets under the threads and freezes when in cooling. Expansion then works of the nut and over time......

    The use of something like Leak Lok on the threads will stop the ingress of moisture and prolong its life.

    The other problem is the installation guy overtightening the joint and cracking the nut on day one. The leak starts after he has left !
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  6. #6
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Flare nuts

    Quote Originally Posted by Brian_UK
    The other problem is the installation guy overtightening the joint and cracking the nut on day one. The leak starts after he has left !
    That's also my experience Brian. If a flare nut is over tightened, it tends to be over stressed which leads to a fracture. AC manufacturers give guidelines as to the torque that these fittings should be tightened to. The use of a torque wrench is the way to go but most installers just "give 'em a little bit more" just to make sure.

    Maybe the installation guys should do a spot of call out and maintenance to see the rewards of their work

  7. #7
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Flare nuts

    Yes, agreed Frank. The fact that they recommend (insist??) that R410 flares should be tightened with a torgue spanner may perhaps begin the trend which will, hopefully, reduce the problem.

    Also, throwing away the installers set of Stilsons may also help
    Last edited by Brian_UK; 05-07-2005 at 10:36 PM. Reason: Spelling errors (doh)
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  8. #8
    Join Date
    Oct 2004
    Location
    Scotland
    Age
    46
    Posts
    1,454
    Rep Power
    21

    Re: Flare nuts

    Couldn`t agree more install lads get it easy, they just fit brand new parts usually during normal working hours and even if they do overtime its planned well in advance.

    The use of flares should not only be discouraged but eradicated completely.
    This could only come from somebody other than a service tech. Braizing parts in is a complete pain in the behind.

    Its not nice having to braize in tevs or driers when its 2am. Especially when you try and have nitro flowing to stop oxodisation.
    Pump a pack down, reclaim all left over gas, break vac with nitro, set up nitro to flow, braize in part, vac system, top up gas..... all this while 20 cases are alarming out...no thanks.
    IF AT FIRST YOU DON`T SUCCEED.
    DESTROY ALL EVIDENCE THAT YOU TRIED!
    and go get a cuppa

  9. #9
    Join Date
    Jun 2005
    Location
    Aberdeen, Scotland
    Age
    61
    Posts
    45
    Rep Power
    0

    Re: Flare nuts

    Cracked Nuts!

    Sounds serious. I would go and see a doctor.

    PIST

  10. #10
    Join Date
    Apr 2005
    Location
    edinburgh
    Age
    57
    Posts
    29
    Rep Power
    0

    Re: Flare nuts

    yea i have had the same problem on daikin vrv at the royal bank of scotland. it was funny that about all the 8 vrvs had the same problem and only at this site . i think it is faulty batch of flare nuts my self.

    cheers dougie.

  11. #11
    Join Date
    Jun 2005
    Location
    Aberdeen, Scotland
    Age
    61
    Posts
    45
    Rep Power
    0

    Re: Flare nuts

    Dougie, I think I think I know the job you speak of. You probably work for the same company as me and Jase.

    I think there its a combination of things and the bottom line is that materials, eg flare nuts are not of the same quality they used to be and therefore can't stand stand that extra turn.

    I suppose we better ask the chiefs for torque wrenches.

    PIST

  12. #12
    Join Date
    Mar 2005
    Location
    Birmingham U.K.
    Age
    70
    Posts
    54
    Rep Power
    20

    Re: Flare nuts

    Hi everyone

    I was told many years ago that the fractures on flare nuts was being caused by the chemicals within the most usefull leak finding substance --- fairy liquid- and the reaction on the brass of the Fl nut .

    On pressure testing of the system, the installer will go around and check the flare joints with watered down fairy liquid but he will never wash down the joints with clean water, years later the flare nut will crack open.

    This however just could be a fairy tale.

    Bobjob

  13. #13
    Join Date
    Apr 2001
    Location
    UK
    Posts
    2,099
    Rep Power
    27

    Re: Flare nuts

    Either a faulty batch or an exuberant techi who on installation tightened over the torque limits, thus hastening their demise
    Any opinions, statements and facts expressed in this message do not constitute legal advice in any shape or form and is given for a general outlook in nature. You are advised to seek appropriate and specific professional assistance from a regulated and authorised advisor for definitive advice.

  14. #14
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Flare nuts

    Quote Originally Posted by bobjob
    This however just could be a fairy tale.
    You could be right BobJob, Fairy Liquid, and other washing liquids, contain salt as a wtaer softening agent and salt, of course, corrodes metals.

    That is why the Gas Authority does not allow the use of washing liquids as a leak detector anywhere near a gas meter and it's associated pipework.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  15. #15
    Join Date
    Jun 2005
    Location
    Aberdeen, Scotland
    Age
    61
    Posts
    45
    Rep Power
    0

    Re: Flare nuts

    Very interesting eh Jase. I think the subbies who installed that system may very well use fairy liquid even though we provide them with proper leak detection spray.

    I shall try and find out but you know they'll never admit it.

    PIST

  16. #16
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Flare nuts

    Hi Jase

    Are you the same Jase that posted this problem on the IOR forum?

  17. #17
    Join Date
    Feb 2005
    Location
    Aberdeen
    Age
    48
    Posts
    168
    Rep Power
    20

    Re: Flare nuts

    Hi Frank

    Yes it is indeed me
    Why you ask?

    Jase

  18. #18
    Join Date
    May 2004
    Location
    Scotland
    Age
    51
    Posts
    4
    Rep Power
    0

    Re: Flare nuts

    Hi Guys,

    talking of torque wrenches, does anyone know where i can get a 3/4 head for my refco set or if it is available because the supplier told me if i want 3/4 i have to file down my 5/8 head. Great eh!! The suction nut on the indoor R410a Mitsibishi are 3/4. Or are there other sets available with a 3/4 head.
    cheers in advance
    Greg

Similar Threads

  1. To flare or not to flare?
    By worthington in forum Commercial
    Replies: 15
    Last Post: 13-03-2010, 07:36 PM
  2. Flaring
    By cikku in forum Air Conditioning
    Replies: 5
    Last Post: 19-12-2005, 10:18 PM
  3. Why Is It? - Seeing round corners
    By Brian_UK in forum Chit Chat & Service Stories
    Replies: 6
    Last Post: 08-12-2004, 06:51 PM
  4. solder V Flare Driers
    By Latte in forum Technical Discussions
    Replies: 45
    Last Post: 23-05-2004, 09:22 AM
  5. Flare Fittings - Illegal?
    By Derek in forum Technical Discussions
    Replies: 6
    Last Post: 18-07-2002, 06:22 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •