    AHU investigation



    I need too investigate an exist ducted air con system that is not conforming (cooling capacity insufecient)
    the duct system is served by means of a chilled water AHU.
    Any tips on where to start my investigation?
    see attached scada image. please note that it was taken not on a hot day therfor the temperatures don't seem to high.
    my concerns is:
    -high delta T (10C) over coil

    what is the recomended / typical supply air temperature (range) if the required room temperature is 23C?



  2. #2
    Join Date
    Aug 2010
    Location
    windhoek
    Posts
    41
    Rep Power
    0

    Re: AHU investigation

    see attachment
    Attached Files Attached Files

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: AHU investigation

    First question: Has the system worked to specification in the past?

    If not, what has changed?

    Check water flow rates, temperatures etc.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: AHU investigation

    The key temperature is the air leaving the cooling coil. This needs to be 11K lower than the target room temp in order to maintain 50% humidity in the room. Since your target room temp is 23C, the cooling coil air off temp should be 23-11=12C.

  5. #5
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: AHU investigation

    Assuming the 7C and 17C are the entering and leaving water temps, it looks like a water flow problem.

  6. #6
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    52
    Posts
    1,083
    Rep Power
    23

    Re: AHU investigation

    Hi mechman
    Making a few assumptions here - It looks like (from the SAT GUI) that the Supply Air Temp is 16.34°C and the Supply Air Temp Set Point is 16.38°C, so the cooling is doing what the controller is commanding. My first check would be some of the GUIs show oper (operator) while others show (none) - is this the control priority? in a Siemens system operator is the highest and none is the lowest priority. This would indicate these operator values are overriding the normal program. Has some one been playing with the controls here? I dial into BMSs every day and interrogate them - as Gary wrote above it could be lack of cooling. If you right click (or double left click) on the graphics page (with the operators logg on) on the supply air temp another window may pop up where you could click on none then command and see if this solves the problem.
    Last edited by Tesla; 28-09-2010 at 08:52 AM. Reason: added value

  7. #7
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: AHU investigation

    Quote Originally Posted by Gary View Post
    Assuming the 7C and 17C are the entering and leaving water temps, it looks like a water flow problem.
    Gotcha, but only half of it. The control signal is 5.67 V, that is 56% of opening. It looks like there is a control problem, that causes half of water flow across of the valve.
    But ahead of that, why a two way valve? Is there an inverter pump? Or is it just a misrepresentation?

  8. #8
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    52
    Posts
    1,083
    Rep Power
    23

    Re: AHU investigation

    Miss-interpretation - the majority of chilled water systems with AHUs use a two way valve using a chilled water byspass or decouple pipe bypass to maintain flow across the chiller.

  9. #9
    Join Date
    Jun 2010
    Location
    Ireland
    Posts
    168
    Rep Power
    15

    Re: AHU investigation

    Agree with Gary, insufficient water flow to coil, check the valve.

    Failing that look at the rest of the system, is pump ok? ... is something else on system starving this coil of water (commissioning issue)?

    Flowing in at 7 you want to be coming off at 12 (in design conditions).

  10. #10
    TRASH101's Avatar
    TRASH101 is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Mar 2007
    Location
    england
    Posts
    394
    Rep Power
    18

    Re: AHU investigation

    I think it may well be an airflow problem as all areas are above setpoint except the cooling which is "bang on".

    Do the six offices have individual heaters?

    Is there seperate extracts for the "bulk cash" and "note sorting" rooms ?

    As there is no humidification system note well Garys' advice as paper is noticabley hygroscopic (assuming that is an issue)

    More importantly I refer to Brians question

    Has the system worked to specification in the past?
    Know what the system was built to do before saying what it can or can't do.
    Quidvis Recte Factum Quamvis Humile Praeclarum.

    Latine dictum, sit altum videtur.

    Si hoc comprehendere potes, gratias age magistro Latinae.

  11. #11
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: AHU investigation

    The insufficient water flow through the coil could simply mean the controls have reduced the flow. It could be just a matter of adjusting the settings.

  12. #12
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: AHU investigation

    Quote Originally Posted by Gary View Post
    The insufficient water flow through the coil could simply mean the controls have reduced the flow. It could be just a matter of adjusting the settings.
    I second that.

  13. #13
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: AHU investigation

    Consider this psychrometric chart:

    http://www.uigi.com/UIGI_SI.PDF

    Find where 12C intersects the 100%RH line. Follow horizontally to the right where it intersects the 23C line. The RH at this intersection is slightly over 50%.

    IOW, if the air leaving the coil (12C@100%RH) is warmed to 23C, the RH will be about 50%.

    If the air leaving the coil is 16C@100%RH, then at 23C the RH will be about 65%.
    Last edited by Gary; 28-09-2010 at 02:06 PM.

  14. #14
    Join Date
    Aug 2010
    Location
    windhoek
    Posts
    41
    Rep Power
    0

    Re: AHU investigation

    thks chaps
    how can I verify the water flow, no installed metering device.
    what is the recomended meter to install?

  15. #15
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

  16. #16
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: AHU investigation

    Try an ultrasonic flow meter.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  17. #17
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: AHU investigation

    I would monitor the coil air off temp and adjust the SA control until the air off temp is 12C.

  18. #18
    Join Date
    Jun 2010
    Location
    saudi arab
    Age
    41
    Posts
    82
    Rep Power
    14

    Re: AHU investigation

    Hello All Dear,
    i am new user & first post here.i have a question & hope.you can solve it.suppose 11k what is mean of ` k ` ?

  19. #19
    Join Date
    Aug 2010
    Location
    windhoek
    Posts
    41
    Rep Power
    0

    Re: AHU investigation

    what is recommended allowance of fresh air in the basement 7l/s per person with a minimum numer of air changes as there is very litlle occupancy in the basement

    how many air changes than , 0.5?

  20. #20
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: AHU investigation

    It depends on the activity done in the room. If it's a gym, at least 20 vol/h, if it's a kitchen 30 vol/h.
    If it's all office space I would say 6 to 8 vol/h with 20% fresh air.

  21. #21
    Join Date
    Jun 2010
    Location
    Ireland
    Posts
    168
    Rep Power
    15

    Re: AHU investigation

    Shaaf, k is degrees kelvin. Like degrees centigrade but starts at absolute zero. Often used when comparing temperature or measuring a differential. example: air on temp 32 oC air off temp 37 oC; temperature difference is 5 K.

    This is not to confuse with 5oC (which is a 'cold' temperature)

  22. #22
    Join Date
    Jun 2010
    Location
    saudi arab
    Age
    41
    Posts
    82
    Rep Power
    14

    Re: AHU investigation

    thanks my dear

Similar Threads

  1. 5H86 Failure Investigation Results - Comments Wanted
    By 5H86User in forum Technical Discussions
    Replies: 2
    Last Post: 17-07-2009, 01:52 PM
  2. Tamahere Fire
    By fridgeedave in forum Hydrocarbons
    Replies: 14
    Last Post: 26-01-2009, 11:58 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •