    Walk in coldroom defrost problem



    I am getting a bit of grief with a coldroom in a restaurant we look after. About 3 months ago a probe went and the evap turned into a block of ice. Changed probe and defrost operated as normal. I got a call during the week went in and the control switch on the front of the panel was broken I bypassed the switch left running. A few days later they called me to say it was iced up again. Went in again defrosted evaporator. I put the unit on a manual defrost. All the heaters came on and with the help of a terbo torch I melted the ice. Checked the defrost settings. It comes on defrost every 4hours. Duration for 35 min. Defrost stop temp is 16C. Probes working. Unit pumping down. Solenoid ok. expansion valve is new. Everything seemed ok. Got a call again last night to say she had iced up again. I did notice last night the lads in the kitchen had set the fridge temp to -2. They are always complaining that its not cold enough in there even though fridge will pull down to 0c with no problem. Its a really busy kitchen and they are constantly opening the doors. The coldroom is designed for holding only and not pull down and they do put warm product in there the odd time. Has anyone any ideas why she keeps icing up? Thanks for your help



  2. #2
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,090
    Rep Power
    33

    Re: Walk in coldroom defrost problem

    can you lock the controller to stop it being set below 2 degrees c and set the diff to 3 degrees

  3. #3
    Join Date
    Nov 2008
    Location
    Ireland
    Posts
    55
    Rep Power
    16

    Re: Walk in coldroom defrost problem

    I can lock controller so they can't change temp. Do you think that's anything to do with defrost problem?

  4. #4
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,730
    Rep Power
    32

    Re: Walk in coldroom defrost problem

    Ah,am i missing something Crypton? Why are there defrost heaters in a coldroom? Anyway, sounds like high humidity and heatload+ long run cycle. Is the plant old and inefficient, clean coils etc... mike

  5. #5
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Walk in coldroom defrost problem

    Initiate manual defrost and see if it is terminated by evaporator temperature or time (not when it is blocked by ice, do that when is normally frosted).
    Than take these measurements after cold-room reach 3-4°C.


    Evap air/water in temp
    Evap air/water out temp
    Low side pressure or saturation temp
    Suction line temp at evap outlet
    Suction line temp at compressor inlet

    Cond air/water in temp
    Cond air/water out temp
    High side pressure or saturation temp
    Liquid line temp at receiver or condenser outlet
    Liquid line temp at TXV inlet
    The more information provided the more accurate the diagnosis.
    Last edited by nike123; 28-09-2010 at 12:54 AM.

  6. #6
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Walk in coldroom defrost problem

    If a +2 'C chiller setup the LP switch to cycle off at desired temp, and back on after air defrost and clear coil. The staff can set controler at what ever they want, the LP switch will over ride controller. Then forget about the electric defrost. Knowing that chefs will leave door open all the time and kitchens are hot and steamy. you will be in control. Perhaps a door swithch and an annoying buzzer alarm will prompt them to close the door quicker.

  7. #7
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,730
    Rep Power
    32

    Re: Walk in coldroom defrost problem

    Magoo, i like the buzzer idea, have to put it out of sight so they can't wack it with a broom, then maybe off the same door switch cycle the evap fans...mike.

  8. #8
    Join Date
    May 2007
    Location
    scotland
    Posts
    756
    Rep Power
    20

    Re: Walk in coldroom defrost problem

    make sure you fitted the correct probe type, i got called to a zannotti room where a engineer had replaced the evap probe with what he thought was the right probe, except the original was ptc and he fitted ntc probe, so the probe reads out with the desired termination probe temperature therfore never goes onto defrost, worth checking out!!

  9. #9
    Join Date
    Nov 2008
    Location
    Ireland
    Posts
    55
    Rep Power
    16

    Re: Walk in coldroom defrost problem

    Thanks for your help lads. I am heading into restaurant tonight to do another job so I will have a good look at it. I have to say I like the buzzer idea. It would wreck their heads. I just presummed the probe was ok once there wasnt an E1 fault. I will check it out. The last time the evap was cleared was Sunday night so this evening I will have a good idea of how the coil is. I will post back up tomorrow if there has been any change. Thanks again for your help.

  10. #10
    barryjustin's Avatar
    barryjustin Guest

    Re: Walk in coldroom defrost problem

    I had this similar problem. What brand of controller is the defrost? We had a late model dixell on ours, it was only about 6 months old, but every now and again it wouldnt switch to defrost properly. We changed the controller, and never had this problem again.

Similar Threads

  1. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  2. Thermoking defrost logic
    By bessershmit in forum Transport
    Replies: 4
    Last Post: 06-09-2010, 05:49 AM
  3. walk in freezer wont drop under 20 degrees
    By Deniver45 in forum Trouble Shooting
    Replies: 11
    Last Post: 31-08-2010, 09:41 PM
  4. Defrost problem.
    By scorpx in forum Technical Discussions
    Replies: 12
    Last Post: 13-08-2010, 10:08 PM
  5. Suction pressure problem during defrost
    By Etienne in forum Fundamentals
    Replies: 6
    Last Post: 05-01-2007, 06:48 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •