    measure sub-cooling



    Can anybody tell me,which is the correct point to take high pressure to measure sub-cooling.At compressor discharge valve or at liquid line before the expansion valve???



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: measure sub-cooling

    For checking that you have enogh subcooling to prevent flash gas before TXV, at liquid line before expansion valve.
    For checking refrigerant charge, at condenser outlet.
    Pressure should be measured where temperature is measured. If not possible, than you need to take in consideration pressure drop from measuring point of pressure to measuring point of temperature.
    Last edited by nike123; 24-09-2010 at 07:03 PM.

  3. #3
    Join Date
    Dec 2008
    Location
    greece
    Age
    47
    Posts
    227
    Rep Power
    16

    Re: measure sub-cooling

    How can you calculate pressure drop nike??

  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: measure sub-cooling

    Quote Originally Posted by HARRY 7 View Post
    How can you calculate pressure drop nike??
    You could use Cool-pack.
    But, if length of pipes and number of fittings are small you could round that pressure loss or ignore it, if you could picture in your head how much approximately that would be.
    Try with excersizeing on real examples from your work by noting pipe diameters, pressures and temperatures, power of system and then calculate in Cool-pack. That will give you feeling.

  5. #5
    Join Date
    Dec 2008
    Location
    greece
    Age
    47
    Posts
    227
    Rep Power
    16

    Re: measure sub-cooling

    What is coolpack?

  6. #6
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,444
    Rep Power
    37

    Re: measure sub-cooling

    Nike,

    You're very patient

  7. #7
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: measure sub-cooling

    Quote Originally Posted by HARRY 7 View Post
    What is coolpack?
    http://www.et.web.mek.dtu.dk/Coolpack/UK/index.html

  8. #8
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: measure sub-cooling

    Quote Originally Posted by r.bartlett View Post
    Nike,

    You're very patient
    Yep!.......

  9. #9
    Join Date
    Dec 2008
    Location
    greece
    Age
    47
    Posts
    227
    Rep Power
    16

    Re: measure sub-cooling

    Thanks for the information nike

Similar Threads

  1. Cooling problem with VRV REYQ24M7.
    By cool#9 in forum Air Conditioning
    Replies: 3
    Last Post: 07-02-2010, 12:20 PM
  2. measure sub cooling properly
    By johnny cool in forum Fundamentals
    Replies: 7
    Last Post: 24-03-2009, 05:43 PM
  3. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM
  4. Cooling tower evaporation, blowdown, makeup and cycles
    By miltbeychok in forum Industrial
    Replies: 5
    Last Post: 14-10-2005, 06:34 PM
  5. Cooling tower evaporation, blowdown, makeup and cycles
    By miltbeychok in forum Fundamentals
    Replies: 0
    Last Post: 13-10-2005, 05:14 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •