    york chiller Solid state starter starting current



    Hi all. I 'm new at this site. I need your helps.
    I want to know
    How much current is occur when I start York 400t chiller with solid state starter.
    chiller spec says that the rated amps is around 300A, but when I start it, it looks like use much more than 300A.
    Anybody know about starting current, please help me



  2. #2
    Join Date
    Aug 2008
    Location
    UAE
    Posts
    5
    Rep Power
    0

    Re: york chiller Solid state starter starting current

    You need to check the motor datasheet and look for the Locked Rotor amps value (LRA). A typical solid state starter inrush will in the 45 to 50% of the LRA value

  3. #3
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: york chiller Solid state starter starting current

    most soft starters have adjustable ramp up times. DOL starting is something like 10 times the LRA.
    Last edited by Magoo; 29-09-2010 at 01:35 AM.

Similar Threads

  1. Maximum Starting Current
    By weeliang82 in forum Air Conditioning
    Replies: 4
    Last Post: 29-04-2010, 04:15 AM
  2. York Reciprocating Chiller - %Motor Current
    By subdude in forum Trouble Shooting
    Replies: 4
    Last Post: 28-07-2009, 05:49 PM
  3. Solid State Starter
    By pinto joseph in forum Technical Discussions
    Replies: 4
    Last Post: 04-02-2009, 05:32 PM
  4. York Solid State Starter Fault
    By Bill at 101 in forum Trouble Shooting
    Replies: 10
    Last Post: 04-12-2008, 06:01 AM
  5. York Water cooled solid state starter?
    By Dave the Fridge in forum Trouble Shooting
    Replies: 6
    Last Post: 27-03-2007, 05:03 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •