    Altherma Error Code A6



    I have a Daikin Altherma HT (ERSQ011AAY1/EKHBRD011AY1) 11kW heat pump.

    I get an Error Code A6 on the display panel and the red LED light on the panel starts blinking. This error already happened twice this week. When it happend, the Central Heating hot water production stops although the Domestic Hot Water production still works.

    I checked the manual and it says M1P pump failure.

    Any ideas if this require professional assistance or if I can fix it?



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Altherma Error Code A6

    Can you access the pump?

    Is it air locked, is it free to rotate ?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Altherma Error Code A6

    Quote Originally Posted by Novecento View Post
    I have a Daikin Altherma HT (ERSQ011AAY1/EKHBRD011AY1) 11kW heat pump.

    I get an Error Code A6 on the display panel and the red LED light on the panel starts blinking. This error already happened twice this week. When it happend, the Central Heating hot water production stops although the Domestic Hot Water production still works.

    I checked the manual and it says M1P pump failure.

    Any ideas if this require professional assistance or if I can fix it?
    It look like diverting valve is having problem or central heating system water filter (if it is separate one) is dirty.

    Every year before start of heating season your system should be examined and started by professional. Pump (and other moving parts on water side) could block after staying still for prolonged period of time (non-heating season) and need to be manualy started (by screwdriver) before start up of system if unit doesnt have prevention of pump blockage.
    Last edited by nike123; 25-09-2010 at 09:03 AM.

  4. #4
    Join Date
    Nov 2007
    Location
    London
    Posts
    461
    Rep Power
    17

    Re: Altherma Error Code A6

    yes i would say a dirty filter..

  5. #5
    Join Date
    May 2005
    Location
    newbury
    Age
    43
    Posts
    13
    Rep Power
    0

    Re: Altherma Error Code A6

    Filter is not to tricky to get to on these units its on the water return towards the bottom left of the unit worth cleaning fairly regular any way. Roger

Similar Threads

  1. Altherma frequent compressor cycling
    By afternine in forum Heat Pumps
    Replies: 80
    Last Post: 29-10-2010, 11:03 AM
  2. Altherma Cooling Performance?
    By pmwillia in forum Heat Pumps
    Replies: 0
    Last Post: 20-08-2010, 03:07 AM
  3. Altherma v Inverter Splits/Mini VRF
    By Makeit go Right in forum Air Conditioning
    Replies: 0
    Last Post: 18-07-2010, 05:33 PM
  4. How are the Daikin Altherma units?
    By LucMan in forum Air Conditioning
    Replies: 11
    Last Post: 15-07-2010, 11:08 PM
  5. Callling everyone with Altherma experience
    By Contactor in forum Heat Pumps
    Replies: 2
    Last Post: 15-07-2010, 10:38 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •