    Milk chiller problem



    Dear friends,

    pl help me to find out the problem

    we have installed 20tr glycol chiller with ammonia systems for chilling 10,000ltr/hr milk by alfa laval PHE.

    we designed for chilling milk from 8 degree to 6 degree celcious(i.e 6degree drop)

    but pratically we give input milk is 6degree only
    but we getting output milk temp is 3.5degr to 4 degree only(i.e is 2.5 degree drop only)
    we gave the coolent side glycol temp is -5.5 degree to -6 degree
    but we didn't get atleast 5 degree drop

    the milk chiller heat transfer area is 3.84m^2

    pl anybody help me
    whether the designed system is correct or not?

    ?????????

    u can send ur idea to my mail box
    munakp@gmail.com

    im verymuch thankful to you,



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Milk chiller problem

    There is no need to post your question in multiple threads.

    we designed for chilling milk from 8 degree to 6 degree celcious(i.e 6degree drop)
    From 8 to 6 is 2 degree drop.
    If it is 6 degree drop than, if 8°C at enter mean that on exit will be 2°C.
    Which is your case?

    What is PHE model#?
    What is measured glycol flow rate? What glycol type is inside and what concentration.
    What is measured milk flow rate? Is it 10m^3/hr?
    20 TR should be sufficent to cool 20% propilene glycol 5°C if flow is about 12000l/h
    __________________
    Last edited by nike123; 24-09-2010 at 08:10 AM.

  3. #3
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Milk chiller problem

    What are the input and output temperatures on the glycol side of the PHE?

  4. #4
    Join Date
    Sep 2009
    Location
    india
    Age
    38
    Posts
    16
    Rep Power
    0

    Re: Milk chiller problem

    thank you nike,

    Sorry for the multi post, I am new to this RE, so i didn't read the rules im verysorry
    we designed for chilling milk from 8 degree to 2degree celcious(i.e 6degree drop)
    M10 not Exact,

    Glycol flow rate is 27360 Ltr/hrMilk flow rate is 10,000 LTR/hr

  5. #5
    Join Date
    Sep 2009
    Location
    india
    Age
    38
    Posts
    16
    Rep Power
    0

    Re: Milk chiller problem

    Glycol input is -6*c
    output is -2 *c

  6. #6
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Milk chiller problem

    Quote Originally Posted by muna View Post
    thank you nike,

    M10 not Exact,

    Glycol flow rate is 27360 Ltr/hrMilk flow rate is 10,000 LTR/hr
    Are you sure that you have counter-flow of milk/glycol in PHE. Check connections and flow directions. It must be counter-flow.

    What is glycol concentration and type?

  7. #7
    Join Date
    Sep 2009
    Location
    india
    Age
    38
    Posts
    16
    Rep Power
    0

    Re: Milk chiller problem

    Quote Originally Posted by nike123 View Post
    Are you sure that you have counter-flow of milk/glycol in PHE. Check connections and flow directions. It must be counter-flow.

    What is glycol concentration and type?
    yes you are correct it is counter flow only, glycol and water concentration is about 30%

  8. #8
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Milk chiller problem

    Quote Originally Posted by muna View Post
    Glycol flow rate is 27360 Ltr/hrMilk flow rate is 10,000 LTR/hr
    Is that measured flow with measuring device?

    With that flow rate you stated above and temperature diference of 4K (-6--2) that qlycol is taking from HE about 40TR which is not possible.
    So something is wrong. Either flow rate or measured temperatures.
    Last edited by nike123; 24-09-2010 at 08:29 AM.

  9. #9
    Join Date
    Sep 2009
    Location
    india
    Age
    38
    Posts
    16
    Rep Power
    0

    Re: Milk chiller problem

    Quote Originally Posted by nike123 View Post
    Is that measured flow with measuring device?

    With that flow rate you stated above and temperature diference of 4K (-6--2) that qlycol is taking from evaporator about 40TR which is not possible.
    So something is wrong. Either flow rate or measured temperatures.
    milk side we get measure by milk silo scale and pumping time
    but
    glycol we took pump designed output for 14mtr head i.e is 7.6ltr/sec
    our assumption the glycol flo rate not less than 20,000ltr/hr

    so guide me, what i have to do?

  10. #10
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Milk chiller problem

    Quote Originally Posted by nike123 View Post
    Is that measured flow with measuring device?

    With that flow rate you stated above and temperature diference of 4K (-6--2) that qlycol is taking from HE about 40TR which is not possible.
    So something is wrong. Either flow rate or measured temperatures.
    Or all of the above.

  11. #11
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Milk chiller problem

    Quote Originally Posted by muna View Post
    milk side we get measure by milk silo scale and pumping time
    but
    glycol we took pump designed output for 14mtr head i.e is 7.6ltr/sec
    our assumption the glycol flo rate not less than 20,000ltr/hr

    so guide me, what i have to do?
    With what instrument you are measuring temperature?

    Adjust flow (reduce) until you get 5K temperature difference at glycol side. That will give you maximum heat transfer to you PHE. Than check milk side.

  12. #12
    Join Date
    Sep 2009
    Location
    india
    Age
    38
    Posts
    16
    Rep Power
    0

    Re: Milk chiller problem

    Quote Originally Posted by nike123 View Post
    With what instrument you are measuring temperature?

    Adjust flow (reduce) until you get 5K temperature difference at glycol side. That will give you maximum heat transfer to you PHE. Than check milk side.
    thanks a lot, your reply makes me thinking in depth,
    we are using digital temp indiacator as wel as analog thermo meter with 0.5 *c error

    you mean 5k, how much *c ?? we need minimum 5*celcious in milk side

  13. #13
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Milk chiller problem

    Quote Originally Posted by muna View Post
    thanks a lot, your reply makes me thinking in depth,
    we are using digital temp indiacator as wel as analog thermo meter with 0.5 *c error

    you mean 5k, how much *c ?? we need minimum 5*celcious in milk side
    What kind of temperature measuring device. (IC, surface probe, Pt100 Pt1000, K-type etc..)?
    It should be measured with Pt1000 probe which is in copper sleeve inside glycol pipe or with some very accurate surface probe at some distance of HE (about 25-50 cm from HE). Or with this kit:
    http://www.yellowjacket.com/images/p...atKit_case.jpg

    5K (upper case) means 5 Kelvin
    Kelvin is same as Centigrade degree when it is used as temperature difference unit. And, according to SI unit system, it is preferable unit to use when there is temperature difference in game.
    Last edited by nike123; 24-09-2010 at 09:06 AM.

  14. #14
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Milk chiller problem

    Glycol is to cold, or milk velocity is to low.
    Is the milk flow consistant?

  15. #15
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Milk chiller problem

    If you want that your PHE is at maximum exchange capacity, than you need introduce concept of thermal length.
    That mean if you want temperature drop on milk side of 6K, than you also need temperature drop on glycol side of 6K. You do that by changing flow of glycol to get same "thermal length".

    Edit: Ignore this since I forgot to care about frost.
    Last edited by nike123; 24-09-2010 at 10:07 AM.

  16. #16
    Join Date
    Sep 2009
    Location
    india
    Age
    38
    Posts
    16
    Rep Power
    0

    Re: Milk chiller problem

    Quote Originally Posted by mad fridgie View Post
    Glycol is to cold, or milk velocity is to low.
    Is the milk flow consistant?
    hmm, yes milk flow rate is consistant,but now we can't cool the 10000ltr/hr milk with is PHE, bcoz ifigive 10000ltr as a inputmilk i could get only 1 to 2 *c drop, so i adjust the flow rate of milk which for 4*c drop

  17. #17
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Milk chiller problem

    Quote Originally Posted by muna View Post
    hmm, yes milk flow rate is consistant,but now we can't cool the 10000ltr/hr milk with is PHE, bcoz ifigive 10000ltr as a inputmilk i could get only 1 to 2 *c drop, so i adjust the flow rate of milk which for 4*c drop
    Install, 3 port valve, supply full flow of glycol at a higher temperature!

  18. #18
    Join Date
    Sep 2009
    Location
    india
    Age
    38
    Posts
    16
    Rep Power
    0

    Re: Milk chiller problem

    Quote Originally Posted by mad fridgie View Post
    Install, 3 port valve, supply full flow of glycol at a higher temperature!
    ya alredy it has been installed, and gave it to full force full open in glycol side @-6*C and as well as 10,000ltr/hr of milk @ 6*C as input, but milk output is only 2*C drop(i.e 4*)
    so pl give the correct parameter for chilling the milk 6*C to 2*C,
    so im greatful to uuu

  19. #19
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Milk chiller problem

    Quote Originally Posted by muna View Post
    ya alredy it has been installed, and gave it to full force full open in glycol side @-6*C and as well as 10,000ltr/hr of milk @ 6*C as input, but milk output is only 2*C drop(i.e 4*)
    so pl give the correct parameter for chilling the milk 6*C to 2*C,
    so im greatful to uuu
    Glycol is to cold, full force say at -2C not -6C

  20. #20
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Milk chiller problem

    With that surface of PHE and flow rates you presented you could only go with -4°C glycol at inlet and 1°C at outlet (13,2 m^3/h) if you wish that 10000l/h milk is cooled from 8°C to 2°C (1K approach).



    If you increase surface to 5,9m^2 than you could go with -2°C glycol at inlet and 1°C (22m^3/h)at outlet if you wish that 10000l/h milk is cooled from 8°C to 2°C (1K approach).

    Last edited by nike123; 24-09-2010 at 02:50 PM.

  21. #21
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Milk chiller problem

    Everyone seems to be in agreement that -6C is too cold. The glycol should not be colder than -4C.
    Last edited by Gary; 24-09-2010 at 07:10 PM.

Similar Threads

  1. problem with multistack chiller
    By bright in forum Refrigerants
    Replies: 3
    Last Post: 30-10-2010, 10:43 PM
  2. Carrier chiller basic board problem
    By noushad123 in forum Trouble Shooting
    Replies: 25
    Last Post: 17-06-2010, 06:55 AM
  3. Problem with centrifugal chiller
    By engalmohannad in forum Commercial
    Replies: 0
    Last Post: 19-04-2009, 10:00 PM
  4. York YK Chiller Problem
    By icebox in forum Refrigeration Books
    Replies: 13
    Last Post: 01-07-2008, 06:05 PM
  5. Chiller tripping Problem
    By bhasadu in forum Trouble Shooting
    Replies: 0
    Last Post: 21-06-2008, 09:12 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •