    Dear friends,

    pl help me to find out the problem

    we have installed 20tr glycol chiller with ammonia systems for chilling 10,000ltr/hr milk by alfa laval PHE.

    we designed for chilling milk from 8 degree to 6 degree celcious(i.e 6degree drop)

    but practically we give input milk is 6degree only
    but we getting output milk temp is 3.5degr to 4 degree only(i.e is 2.5 degree drop only)
    we gave the coolant side glycol temp is -5.5 degree to -6 degree
    but we didn't get at least 5 degree drop

    the milk chiller heat transfer area is 3.84m^2

    pl anybody help me
    whether the designed system is correct or not?

    ?????????

    u can send ur idea to my mail box
    munakp@gmail.com

    im very much thankful to you,
    Last edited by chillin out; 24-09-2010 at 07:34 PM.



  2. #2
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Milk chiller problem, pl help me

    And the leaving glycol temperature is?

  3. #3
    Join Date
    Sep 2009
    Location
    india
    Age
    38
    Posts
    16
    Rep Power
    0

    Re: Milk chiller problem, pl help me

    Quote Originally Posted by NoNickName View Post
    And the leaving glycol temperature is?
    it is -2*c only

  4. #4
    Join Date
    Sep 2009
    Location
    india
    Age
    38
    Posts
    16
    Rep Power
    0

    Re: Milk chiller problem, pl help me

    Quote Originally Posted by muna View Post
    it is -2*c only
    we designed for chilling milk from 8 degree to 2 (not 6 degree as i mentioned) i.e 6degree drop

  5. #5
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Milk chiller problem, pl help me

    Milk is approximately heavy as water (1.032 for raw milk).

    On the warm side:
    20TR = 70kW
    70kW with a volume flow of 10000ltr/h gives a dt = 6°C therefore the leaving milk temperature is 2°C, but the wall temperature is -0.91 for a leaving glycol temperature of -1°C, very close to freezing temperature of milk (-0.55).

    In my opinion, the heat exchange in your case is limited by formation of frosted milk on the plates.

  6. #6
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Milk chiller problem, pl help me

    Quote Originally Posted by NoNickName View Post
    Milk is approximately heavy as water (1.032 for raw milk).

    On the warm side:
    20TR = 70kW
    70kW with a volume flow of 10000ltr/h gives a dt = 6°C therefore the leaving milk temperature is 2°C, but the wall temperature is -0.91 for a leaving glycol temperature of -1°C, very close to freezing temperature of milk (-0.55).

    In my opinion, the heat exchange in your case is limited by formation of frosted milk on the plates.
    great minds think alike

  7. #7
    Join Date
    Sep 2009
    Location
    india
    Age
    38
    Posts
    16
    Rep Power
    0

    Re: Milk chiller problem, pl help me

    yes , u are absolutly correct dear, one time we did CIP cleanning with dismandling plates, we seems that there were some milk freezed pieces,
    so we put a automatic temp control actuator valve, it never allowed to freeze the milk, if once touching 2*C it ll stop the glycol flow,

    so tel me what is the input parameter must to cool the 10000ltr/hr milk @6*c input(i need glycol in temp and suface area of pHE)

  8. #8
    Join Date
    Sep 2009
    Location
    india
    Age
    38
    Posts
    16
    Rep Power
    0

    Re: Milk chiller problem, pl help me

    Quote Originally Posted by mad fridgie View Post
    great minds think alike
    thank you so much mad Fridge for your valuable words & advice , pl give me the comple design,

    Thnx in advence

  9. #9
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Milk chiller problem, pl help me

    I think you should not cool the milk at a temperature below 4°C.

  10. #10
    Join Date
    Sep 2009
    Location
    india
    Age
    38
    Posts
    16
    Rep Power
    0

    Re: Milk chiller problem, pl help me

    Quote Originally Posted by NoNickName View Post
    I think you should not cool the milk at a temperature below 4°C.
    hmm, now im getting outlet milk @ 2*C for 6000ltr/hr, but i need same temp for 10,000ltr/hr

  11. #11
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Milk chiller problem, pl help me

    Increase the surface of exchange

  12. #12
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Milk chiller problem, pl help me

    Quote Originally Posted by muna View Post
    it never allowed to freeze the milk, if once touching 2*C it ll stop the glycol flow
    Which fluid are you measuring to get 2C ?

    If its the milk that might be you problem as the outlet temp won't tell you if there is ice on the plates, (ice will act as an insulator so the milk will be touching ice at 0C and not a stainless steel plate at -6C)

    The only glycol chiller system i have seen ran at around -3C and controlled the flow of glycol into the plate cooler based on the temperature of the glycol coming out, the colder the outlet temp the less glycol flow.

    I have installed some ice builder systems that have supplied chilled water at 0C to a two stage plate heatexchanger with mains water to the first stage and our milk outlet temperature was around 2.5C, this was direct from the milking parlour so the milk was at cow body temp, so i'm not sure you necessarily need such a low starting glycol temp.

    The other thing i would ask is are all the plates in the correct way in the plate heat exchanger?

  13. #13
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Milk chiller problem, pl help me

    The two Glycol system I maintain from time to time have milk feeding pumps with speed controlled by the milk outlet temp.
    The Glycol feeding temp is -0.5°C to -2.5°C.

    Increase the surface of exchange
    Thats the right thing to do.

Similar Threads

  1. problem with multistack chiller
    By bright in forum Refrigerants
    Replies: 3
    Last Post: 30-10-2010, 10:43 PM
  2. Carrier chiller basic board problem
    By noushad123 in forum Trouble Shooting
    Replies: 25
    Last Post: 17-06-2010, 06:55 AM
  3. Problem with centrifugal chiller
    By engalmohannad in forum Commercial
    Replies: 0
    Last Post: 19-04-2009, 10:00 PM
  4. York YK Chiller Problem
    By icebox in forum Refrigeration Books
    Replies: 13
    Last Post: 01-07-2008, 06:05 PM
  5. Chiller tripping Problem
    By bhasadu in forum Trouble Shooting
    Replies: 0
    Last Post: 21-06-2008, 09:12 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •