Thread: Pressure testing
-
02-07-2005, 05:32 PM #1
Pressure testing
A few days ago I was pressure testing a run of cabinets.I noticed some white mist coming out the armo flex on the suction.I stripped it back all the way down to a oil trap between two cabinets,the armo flex was pooled with oil so obviously the leak was here.
I have never seen this mist before. Is it common,there was also uv dye in the oil.
Regards Bernard
-
02-07-2005, 05:41 PM #2
Re: Pressure testing
The mist is droplets of oil pushed out by the OFN.
Must have been a big leak.
Chemi
-
02-07-2005, 08:36 PM #3
Re: Pressure testing
Silly question, but had the cabinets been moved or re-positioned.
it's only a fridge, fix it. ;)
-
03-07-2005, 09:54 AM #4
Re: Pressure testing
Hi chillyhamster
No not that I am aware of,why do you ask.The leak was a pin hole on the braze,leak dectectors didn,t pick it up
Regards BernardLast edited by bernard; 03-07-2005 at 01:27 PM.
-
21-05-2006, 12:10 AM #5
Re: Pressure testing
What is OFN. Is this another name for dry nitrogen which is what we use for pressure testing for leaks?
-
21-05-2006, 09:01 AM #6
Re: Pressure testing
oxygen free nitrogen,got me wondering here bernard,why would a leak detector pick up on nitrogen anyway,? the pressure test can only give a visule and time test,unless there are leak detectors that pick up nitrogen whitch i never have heard off.or am i reading the thread wrong?
-
21-05-2006, 10:39 AM #7
Re: Pressure testing
Nitrogen is 72% of the air we breath. Nitrogen detectors would be useless in open air.
-
21-05-2006, 01:02 PM #8
Re: Pressure testing
Originally Posted by old gas bottleBrian - Newton Abbot, Devon, UK
Retired March 2015
-
21-05-2006, 02:56 PM #9
Re: Pressure testing
Well,what ever bernard was using his good old eye sight was what found that leak.
Am not too familler on the ultra sound detectors do u but on head phones and listen for leaks is that it.
-
21-05-2006, 05:25 PM #10
Re: Pressure testing
Hi Jamcool
Have a read of this http://www.superiorsignal.com/usndacr.pdf
-
21-05-2006, 09:33 PM #11
Re: Pressure testing
Hi Guys
Job well done bernard . Jamcool, OGB agree with you guys. Leak detectors usually backfires and not 100% accurate , I've used bloodhounds,tiffs,halide lamp and uvs. Best method six sense, ofn with soap and water. If you can't locate the leak than use that soapy solution for masturbating
Cheerio guys.
Don't worry be happy
-
22-05-2006, 04:20 PM #12
Re: Pressure testing
look...bernard din't mention anything about using nitrogen during the leak test. It was chemi-cool who suspected he using nitrogen. Assuming bernard is not using nitrogen, then i would believe that probably what he is seeing is in fact liquified ***** escaping through the hole. either the system was overcharged with gas and thus returning lots of unevaporated gas or probably the evaporator (or fan coil) is so badly choked up that the gas did not evaporate. But above all, like all of you guys, I'm also speculating because I don't know if bernard is introducing nitogen into the system or not. Cheers!
Similar Threads
-
Pressure testing for leaks on split a/c systems
By mrchatts in forum Air ConditioningReplies: 46Last Post: 08-04-2010, 10:02 AM -
Pressure testing
By Chopper in forum IndustrialReplies: 8Last Post: 24-10-2005, 06:40 PM -
Building a wine cabinet
By Rory in forum Technical DiscussionsReplies: 38Last Post: 13-07-2004, 08:28 PM -
Pressure Testing
By Derek in forum Technical DiscussionsReplies: 6Last Post: 09-07-2001, 07:11 PM