Re: Liebert vacuum testing
You cannot exceed system design pressure for long time.
Some components are not designed to withstand highest pressure of system. As you know, compressors are usually having stated low and high pressure which cannot be exceeded. Sometimes, for example, low side cannot bare more than 11Bar (160 PSIG) of pressure.
Last edited by nike123; 23-09-2010 at 10:08 AM.
-
23-09-2010, 10:50 AM #2
Re: Liebert vacuum testing
Hi Nike,
do you need to do two pressure tests in this case then? One only the pipework and indoor at high pressure and one for the wole system at low pressure?
If R410a then 11 bar is way under the high pressure cut out of around 40bar or system running pressure in heating of around 28 bar.
Sumsor
-
23-09-2010, 11:06 AM #3
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Liebert vacuum testing
Yes!
If R410a then 11 bar is way under the high pressure cut out of around 40bar or system running pressure in heating of around 28 bar.
Sumsor
Depending on other components in system, that could be even lower.
Similar Threads
-
Vacuum Pump Questions
By position1 in forum FundamentalsReplies: 7Last Post: 08-10-2009, 02:33 AM -
Vacuum cleaner as a vacuum pump
By chemi-cool in forum Chit Chat & Service StoriesReplies: 18Last Post: 14-08-2009, 10:11 PM -
Troubleshooting a vacuum pump and gauge set.
By Old Codger in forum FundamentalsReplies: 7Last Post: 08-08-2008, 05:13 PM -
inverters pulling vacuum
By bangoman in forum Air ConditioningReplies: 2Last Post: 05-02-2008, 09:12 PM -
Vacuum test
By Peter_1 in forum FundamentalsReplies: 15Last Post: 13-10-2006, 09:04 PM