    Re: Liebert vacuum testing

    Quote Originally Posted by sumsor View Post
    Hi Guesstimator,

    160 psi sounds a bit light for a pressure test. What refrigerant are the units running on?
    I usually test R410a systems with 550 to 600 psi for at least 24hrs, better 48.

    sumsor
    You cannot exceed system design pressure for long time.
    Some components are not designed to withstand highest pressure of system. As you know, compressors are usually having stated low and high pressure which cannot be exceeded. Sometimes, for example, low side cannot bare more than 11Bar (160 PSIG) of pressure.

    Last edited by nike123; 23-09-2010 at 10:08 AM.

  2. #2
    Join Date
    Jan 2009
    Location
    NZ
    Age
    48
    Posts
    35
    Rep Power
    0

    Re: Liebert vacuum testing

    Quote Originally Posted by nike123 View Post
    You cannot exceed system design pressure for long time.
    Some components are not designed to withstand highest pressure of system. As you know, compressors are usually having stated low and high pressure which cannot be exceeded. Sometimes, for example, low side cannot bare more than 11Bar (160 PSIG) of pressure.

    Hi Nike,

    do you need to do two pressure tests in this case then? One only the pipework and indoor at high pressure and one for the wole system at low pressure?
    If R410a then 11 bar is way under the high pressure cut out of around 40bar or system running pressure in heating of around 28 bar.

    Sumsor

  3. #3
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Liebert vacuum testing

    Quote Originally Posted by sumsor View Post
    Hi Nike,

    do you need to do two pressure tests in this case then? One only the pipework and indoor at high pressure and one for the wole system at low pressure?
    Yes!

    If R410a then 11 bar is way under the high pressure cut out of around 40bar or system running pressure in heating of around 28 bar.

    Sumsor
    Usualy R410 systems are designed to bare with high pressures. Scroll compressor for R410 as Copeland ZP180KCE has low side pressure restricted to 29,5 Bar and high side pressure to 45. therefore you cannot pressure test it on low side with more than 29,5 Bar.
    Depending on other components in system, that could be even lower.

Similar Threads

  1. Vacuum Pump Questions
    By position1 in forum Fundamentals
    Replies: 7
    Last Post: 08-10-2009, 02:33 AM
  2. Vacuum cleaner as a vacuum pump
    By chemi-cool in forum Chit Chat & Service Stories
    Replies: 18
    Last Post: 14-08-2009, 10:11 PM
  3. Troubleshooting a vacuum pump and gauge set.
    By Old Codger in forum Fundamentals
    Replies: 7
    Last Post: 08-08-2008, 05:13 PM
  4. inverters pulling vacuum
    By bangoman in forum Air Conditioning
    Replies: 2
    Last Post: 05-02-2008, 09:12 PM
  5. Vacuum test
    By Peter_1 in forum Fundamentals
    Replies: 15
    Last Post: 13-10-2006, 09:04 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •