    Is there any problem with servicing an ll float switch by removing the see thru cover. It warns you not to.



  2. #2
    Join Date
    Jul 2006
    Location
    USA
    Age
    73
    Posts
    865
    Rep Power
    26

    Re: Parker ammonia float switch

    If you mean servicing the switch inside the cover I do not believe you can. The cover does not come off. It is well sealed and if you break that seal moisture will be certain to get in.
    But for the last several years they have been installing a fuse on the bottom of the switch which is easy to miss. Check that first.

  3. #3
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: Parker ammonia float switch

    Quote Originally Posted by NH3LVR View Post
    If you mean servicing the switch inside the cover I do not believe you can. The cover does not come off. It is well sealed and if you break that seal moisture will be certain to get in.
    But for the last several years they have been installing a fuse on the bottom of the switch which is easy to miss. Check that first.

    Very informative NH3LVR!
    Many Thanks Grizzly.

  4. #4
    JONSY's Avatar
    JONSY Guest

    Re: Parker ammonia float switch

    I have a feeling that the float switch I am dealing with is fine, but the housing underneath it we believe to be clogged with oil which is effecting its operation, do you know of any way to remove the oil without dismantling the float assembly.

  5. #5
    Join Date
    Nov 2004
    Location
    China
    Posts
    176
    Rep Power
    20

    Re: Parker ammonia float switch

    These float balls don't like cold oil. this has to be isolated, warmed up and drained. The float chamber is a welded assembly & can't be opened without cutting the steel.
    Is there a drain valve on the liquid column or is the lower connection sloped to a drain?

Similar Threads

  1. ammonia refrigeration system
    By Lc_shi in forum Fundamentals
    Replies: 48
    Last Post: 25-06-2010, 10:03 AM
  2. Trane chiller HP Switch
    By Kirky in forum Air Conditioning
    Replies: 4
    Last Post: 27-10-2009, 09:02 PM
  3. Pump out accumulator on an HP Float system (ammonia)
    By benji in forum Trouble Shooting
    Replies: 26
    Last Post: 21-07-2009, 04:21 AM
  4. Hermetic analyzer " ANNIE" how do they work
    By kengineering in forum Tools and Calculators
    Replies: 11
    Last Post: 02-03-2008, 06:10 PM
  5. Parker levels in ammonia systems
    By Friobernal in forum Industrial
    Replies: 3
    Last Post: 04-08-2005, 03:46 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •