    Contactor Bouncing or Hammering



    Hello,

    I have looked at a few units in the past where the contactor for the compressor has constanly bounced when power is applied to the coil to bring on the contactor. I have changed the contactor in the past and this has cured the problem. But sometimes it hasn't and the PCB has been faulty or the compressor What causes the contactor to bounce? Is it the coil no longer producing the same pull or can the current passing the contactor somehow effect the coil? The power to the coil has not been fluctuatiing on my testers.

    Any help is greatfully received.



  2. #2
    Join Date
    Oct 2004
    Location
    uk
    Age
    56
    Posts
    194
    Rep Power
    20

    Re: Contactor Bouncing or Hammering

    in general, if the coil is causing the contactor to chatter, it usually means, in the absence of controls fault, that the coil connections are loose/corroded. sometimes i have found dry connections on pcbs that only show up on visual checks and do not show as voltage fluctuations.

  3. #3
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: Contactor Bouncing or Hammering

    Quote Originally Posted by charlie dart View Post
    The power to the coil has not been fluctuatiing on my testers.

    Any help is greatfully received.
    Have you also looked at the neutral connection?

    Contactors invariably chatter if the supply voltage drops below the pull in threshold, or the neutral connection is loose/corroded. (Assuming mains voltage) The volt drop can be caused by various things, one of which is loose connections.

    Contactors 'buzzing' while pulled in is a sign that dirt/swarfe has found it's way into the inside of the coil.

  4. #4
    Join Date
    Aug 2006
    Location
    england
    Age
    49
    Posts
    3,874
    Rep Power
    46

    Re: Contactor Bouncing or Hammering

    Quote Originally Posted by frank View Post

    Contactors 'buzzing' while pulled in is a sign that dirt/swarfe has found it's way into the inside of the coil.
    Learn something new every day!

    There was me thinking that it needed hitting with something till it stopped buzzing

    Next time i get the chance i'll take a buzzy one apart and see what gotten in there.

    Jon

  5. #5
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: Contactor Bouncing or Hammering

    Careful Jon, in your case it just might be cow s**t!!

  6. #6
    charlie dart's Avatar
    charlie dart Guest

    Re: Contactor Bouncing or Hammering

    Thanks guys that has helped. I shall look forward to my next chattering contactor and take a good look at it

    Thanks again.

  7. #7
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: Contactor Bouncing or Hammering

    When the contactor is energised by LP pressure control, check the contacts. I have seen this a few times and it was caused by bad contacts in the pressure control.

Similar Threads

  1. liquid hammering on pumped liquid line R717
    By VEYSEL DURLU in forum Trouble Shooting
    Replies: 20
    Last Post: 27-03-2008, 06:19 PM
  2. refrigeration hammering
    By mahesh in forum NH3
    Replies: 4
    Last Post: 05-11-2006, 10:38 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •