    Has anyone had any problems with the Danfoss KVL12 crankcase pressure regulating valve running with R404a, leaking or sticking?
    I have had a few give these problems in Zanotti stradle fridge units, and I have now seen that Zanotti are using the Sporlan CRO6 in their new equipment!!.
    Regards.
    *****don.



  2. #2
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Danfoss KVL valves.

    I had one some months ago, a Danfoss KVL
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  3. #3
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Danfoss KVL valves.

    Do they stick open or closed?

    Jon

  4. #4
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Danfoss KVL valves.

    mine remained sticked in a certain position after pressurizing the system while searching for a leak.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  5. #5
    Join Date
    Feb 2009
    Location
    Scotland
    Age
    69
    Posts
    6
    Rep Power
    0

    Re: Danfoss KVL valves.

    Hi Jon.
    The ones we have had problems with have tended to stick shut, or just leak out through the adjusting screw.
    Don.

  6. #6
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Danfoss KVL valves.

    I was just wondering as a Zannoti unit i put a new comp on seemed to have a lower than expected suction pressure but i can never tell with cap tube systems, they always run lower than i would think!

  7. #7
    Join Date
    Feb 2009
    Location
    Scotland
    Age
    69
    Posts
    6
    Rep Power
    0

    Re: Danfoss KVL valves.

    Any reason for the loss of the compressor?
    If not I would have a check of the valve, I am asuming that the unit you repaired has one fitted.
    I have one on test at the presrent, at -20 sucction is about 5 psig, which is about 10 psig lower than I would expect, but seems to be running ok.
    We use them for dual temp, so I am going to let it warm up and run it on the chill setting soon, let you know what I get latter.
    Don.

  8. #8
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Danfoss KVL valves.

    The start relay had burnt out where the neutrals all connect up, (it had suffered a similar burn about a year ago) put a new relay and capacitors on and it lasted a week before it failed.
    I am planning to cut the old one open and see whats gone wrong with it, but i suspect its electrical rather than mechanical.

    The new one was running about 15/18 psi on R404A and i think the room was at -12/14c.

Similar Threads

  1. Danfoss Solenoid Valves
    By ice_cold in forum Commercial
    Replies: 4
    Last Post: 15-12-2009, 04:57 AM
  2. Too dependent on Danfoss Valves
    By kelvin_27_84 in forum Industrial
    Replies: 8
    Last Post: 24-01-2009, 08:33 PM
  3. Danfoss EKC315a ETX Valves
    By LesClem in forum Technical Discussions
    Replies: 2
    Last Post: 14-12-2006, 11:26 PM
  4. Danfoss AKV10 valves
    By David PS in forum Fundamentals
    Replies: 18
    Last Post: 28-07-2006, 03:56 AM
  5. Danfoss AKV Valves
    By Budokan in forum Supermarket Refrigeration
    Replies: 8
    Last Post: 05-04-2004, 07:20 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •