Pressure monitors
My query is regarding the location of the pressure monitoring sensors to be installed in the Operation room of a Hospital. The initial design was to monitor the pressure between the OR and the Clean core area which are both at positive pressure and are clean areas. I would like to change the location of pressure
monitors to monitor the pressure between OR and the adjoining corridors or otherwise known as Dirty corridor. Is this permissible?
or am I missing something here?
-
22-09-2010, 04:10 PM #2
Re: Pressure monitors
You can fit equipment to monitor whatever pressures/rooms that you want to.
As long as you can prove that the pressure differential is correct across the various rooms/areas then all should be well.Brian - Newton Abbot, Devon, UK
Retired March 2015
-
02-10-2010, 08:09 PM #3
Re: Pressure monitors
Thanks for the reply Brian..