TXV problem
I have this unit using TXV and my question is does a starving TXV can cause the evaporator to frost up or sign of undercharged?
-
22-09-2010, 08:48 AM #2
Re: TXV problem
Evaporator frost it is a possibility because the suction pressure will be lower and so the firsts parts of the circuit will feeling that effect (lower evaporation temperature).
About sign of undercharged not necessary.To make progress is never good enough, I want to do better and better and better
-
22-09-2010, 09:30 AM #3
Re: TXV problem
thanks for your quick response!
my analysis was undercharged beacause it only happen during full load and i think TXV operate 100% during full loads. and other thing the unit had no liquid receiver.
-
22-09-2010, 02:36 PM #4
Re: TXV problem
By the facts you presented is much possible the undercharged of the system. But if it happens at full load (much heat load) and the compressor has its capacity unchanged (so the suction pressure is higher) I don't see the reason to frost. Or the compressor have any kind of capacity control.
To make progress is never good enough, I want to do better and better and better
Similar Threads
-
MFI AMP6855 defrost problem
By gliderpilot47 in forum DomesticReplies: 4Last Post: 12-01-2011, 12:11 PM -
A strange problem
By MuhengineeR in forum Air ConditioningReplies: 14Last Post: 27-10-2010, 05:21 PM -
Fujitsu Multi problem
By BMS1 in forum Heat PumpsReplies: 15Last Post: 02-09-2010, 06:41 AM -
problem with GE air con power problem
By Richie101 in forum Air ConditioningReplies: 6Last Post: 05-11-2009, 04:00 PM -
Hot start problem on VRV REYQ14M7W1B
By cool#9 in forum Air ConditioningReplies: 9Last Post: 20-04-2007, 08:09 PM