Air flow restrictiorn for Trane Koolman
Hello,
Does anyone know what the air flow restrictions are for the propper operation of Trane Koolman mini-chiller? I would like to know if it is correct to place a unit behind another unit or what are the recomendation for a propper installation.
best regards.
-
22-09-2010, 08:39 AM #2
Re: Air flow restrictiorn for Trane Koolman
According to the Trane data booklet
http://www.dalkia.com.au/literature/...N_cgakcgar.pdf
The maintenance space required around the unit is:-
Front, air outlet - 1500mm
Sides - 300mm
Rear, air inlet - 500mm
Top - 500mmBrian - Newton Abbot, Devon, UK
Retired March 2015
-
22-09-2010, 12:15 PM #3
Re: Air flow restrictiorn for Trane Koolman
Make sure that you stick to the minimum free area as Brian has posted. Then, increase as required if the units are in a well. Look out for situations that could cause discharge air recirculation. And for heaven's sake don't discharge one condenser into the other or have the discharge facing each other without controlling the air path!
Consult your local Trane office. After all, they're supposed to know all this stuff!
Similar Threads
-
Really weird refrigerant flow issue
By paul_h in forum Air ConditioningReplies: 43Last Post: 13-04-2010, 05:13 PM -
flow switch connection
By afeef in forum The Trail of TearsReplies: 18Last Post: 23-12-2009, 06:55 PM -
Pulling faster vacuums
By Aranon in forum FundamentalsReplies: 31Last Post: 04-09-2009, 07:32 PM -
Flow Rate through Fan Coil Unit
By deepu in forum Air ConditioningReplies: 4Last Post: 21-07-2009, 06:42 AM -
Capillary Tube Characteristics
By Chef in forum FundamentalsReplies: 9Last Post: 10-03-2009, 01:03 PM