    Chiller tripped main breaker



    got a McQuay chiller running on autotrans, everytime it starts, it will trip the main breaker. Have remove the cables to meg the motor, it showed a range from 20Mohms to 100Mohms. The cables showed 2Mohms from motor to autotrans.
    Not sure whether this will cause the trip, or any problem with the autotrans? any ways to check the autotrans? Thanks...



  2. #2
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Chiller tripped main breaker

    A breaker can't trip.
    Is it a thermal switch, magnetic switch or differential switch?

  3. #3
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Chiller tripped main breaker

    Is it ever worked satisfactory?

  4. #4
    Join Date
    May 2010
    Location
    singapore
    Posts
    6
    Rep Power
    0

    Re: Chiller tripped main breaker

    my apologies, it is a MCB....

  5. #5
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Chiller tripped main breaker

    Yes, but MCBs can either be thermal switches or magnetic switches. Which one?
    What model is it?
    What are the LRA and MRA of the compressor?

  6. #6
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: Chiller tripped main breaker

    Quote Originally Posted by chiller prince View Post
    got a McQuay chiller running on autotrans, everytime it starts, it will trip the main breaker. Have remove the cables to meg the motor, it showed a range from 20Mohms to 100Mohms. The cables showed 2Mohms from motor to autotrans.
    Not sure whether this will cause the trip, or any problem with the autotrans? any ways to check the autotrans? Thanks...
    Hi :
    at what stage of starting does it trip the breaker?
    what is the voltage?
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

Similar Threads

  1. process chiller help
    By talon771 in forum Industrial
    Replies: 8
    Last Post: 12-01-2011, 08:42 PM
  2. Problems in r22 chiller design
    By umeshpradhan in forum Technical Discussions
    Replies: 9
    Last Post: 06-07-2010, 10:39 AM
  3. Absorption Chiller VS Mech. Chiller
    By Intern in forum Industrial
    Replies: 20
    Last Post: 30-05-2009, 08:31 AM
  4. Trane CVHE 450 R11 Centrifugal Chiller
    By albertjoseph in forum Air Conditioning
    Replies: 4
    Last Post: 06-10-2008, 03:23 PM
  5. samsung blows main breaker
    By cross in forum Electrical
    Replies: 1
    Last Post: 16-01-2008, 01:15 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •