    Comments Please

    The limit to any compressor discharge temperature is 225 degrees F. If the discharge temperature gets higher than 225 degrees, the system may start to fail from worn rings, acid formations, and oil breakdown. Remember, if the discharge temperature is 225 degrees, the actual discharge valve will be about 75 degrees hotter. This will bring the actual compressor’s discharge valve to 300 degrees. It is a known fact that most oil may start to break down and vaporize at 350 degrees. If this occurs, serious overheating problems will happen. And, since compressor overheating problems are today’s most serious compressor field problems, service technicians must always monitor compressor discharge temperatures and keep them under 225 degrees. You can record superheat at any time but the biggest effect is when your fully loaded, you can always put a recorder with the senseo mounted about 6" from the discharge service valve. Some of the reasons for high compressor discharge temperatures are:

    High condensing pressures;
    Low suction pressures;
    High compression ratios; and
    High compressor superheats.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Superheat

    Quote Originally Posted by frank
    Comments Please
    NO !

    Oh, OK, it seems to be a valid comment and something that we should all be aware off.

    One is tempted to ask whether additional safeties should be fitted to compressors to monitor discharge temperatures to protect the compressor. Yes, I am aware that they are fitted but is that ALL compressors ?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Jun 2005
    Location
    California
    Posts
    394
    Rep Power
    19

    Re: Superheat

    Botrous: When your in superheat there is no PT relationship so head pressure cutout is not the answer you need to put a tenperature control with a senser about 6" from service valve to cutout the compressor and set it for about 250*F

Similar Threads

  1. TXV Superheat
    By Gary in forum Trouble Shooting
    Replies: 15
    Last Post: 24-04-2011, 02:51 PM
  2. Carrier 23xl chiller-Low discharge superheat alarms
    By Bradysmill in forum Trouble Shooting
    Replies: 7
    Last Post: 25-04-2010, 07:43 PM
  3. TEV superheat setting and low temperatures
    By DaBit in forum Fundamentals
    Replies: 11
    Last Post: 01-03-2010, 02:11 AM
  4. Superheat debate
    By zolar1 in forum Technical Discussions
    Replies: 5
    Last Post: 08-02-2008, 09:57 PM
  5. Superheat
    By shogun7 in forum Fundamentals
    Replies: 24
    Last Post: 23-08-2004, 05:54 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •