19-09-2010, 10:29 PM #1
log p/h question, flow rate
Cycle R134a, TE =-10°C, TC = 40°C, no SH nor SC, needed 2 kW cooling capacity.
Q: what flow do we need?
-10°C liquid = 186.93 kJ/kg
-10°C gas = 391.32 kJ/Kg
Both saturated from tables
Added in evaporator = 391.32 - 186.93 = 204.39 kJ/kg
Isentropic compression gives us 425 kJ/kg, so 33.68 (425-391.32) was added during compression.
Flow for 2 kW = 2000 W = 2 kJ/s, so we need 2kJ/s
Evaporator takes 204,39 kJ/kg
kJ/s x kg/s = kg/s
2 x 1/204.39 = 0.009785 kg/s or 9.785 g/s flow
Coolpack gives me 14.73 g/s and this varies with altering TC
Where's my fault ?
Then flow rate x heat of compression= needed compression power (kW) kg/s x kJ/kg = kJ/s = kW
0.009785 x 33.68 = 0.329 kW
Coolpack 0.496 kW (due to my erratic flowrate of course).Last edited by Peter_1; 20-09-2010 at 06:25 AM.
It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
19-09-2010, 11:14 PM #2
-
19-09-2010, 11:18 PM #3
Re: log p/h question, flow rate
your liquid is at 40C, needs to be -10C (so a percentage of flow is used to cool itself) then your calcs are right, for evap duty
give those scales a nudge, lolLast edited by mad fridgie; 19-09-2010 at 11:27 PM.
-
20-09-2010, 06:21 AM #4
Re: log p/h question, flow rate
Hope this helps, Peter.
x roundoff, or slight table differences could account for the tiny difference in computed result.Engineering Specialist - Cuprobraze, Nocolok, CD Technology
Rarefied Technologies ( SE Asia )
-
22-09-2010, 08:11 AM #5
Re: log p/h question, flow rate
-
22-09-2010, 08:41 AM #6
Re: log p/h question, flow rate
Thanks to all, clarified now. At least 4 schoolbooks needs to be rewritten after this thread.
3 used a fault from the 1st in their books and so this fault is spread widely.
Many, me included has learn it the wrong way. I became confused because I found that something had to be wrong but the books stated something different.
Thanks guys, never too old to learn something.It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
22-09-2010, 09:20 AM #7
Re: log p/h question, flow rate
Great, Peter. Glad to see that you're on your way forwards again.
Engineering Specialist - Cuprobraze, Nocolok, CD Technology
Rarefied Technologies ( SE Asia )
-
22-09-2010, 05:36 PM #8
Re: log p/h question, flow rate
Continuing on this thread, another problem..here we go again, hope others can benefit from this
Cycle, R404a,
TE-30°C
TC 40°C
SH 7K
SC 5K
Isentropic compression 0.8
No SGHX
2 kW
Cycle specification in Coolpack Statepoints gives for point 6 (entrance evaporator) 104.4 kJ/kg and for point (or 8 or 1) 207.4 kJ/kg
If you draw this cycle on a log p/h under Refrigeration Utilities, you then get 254 kJ/kg and 355 kJ/kg along the enthalpie axis.
Where these differences comes from?
Calculating the massflow via Coolpack gives 0.01942 kg/s where the calculation via the drawn log p/h and the values read in it gives 0.019924 kg/s
Also, value x in Statepoints is 0.49 where in the drawn cycle it is very close to 0.5 (enlarged view)
Using this different figures gives also not forgiving errors when calculating compressor performance and condenser capacity.
My question, where's my fault regarding mass flow?Last edited by Peter_1; 22-09-2010 at 06:15 PM.
It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
22-09-2010, 06:23 PM #9
Re: log p/h question, flow rate
Very interesting observation. I suspect that Coolpack is using different refrigerant tables in the different modules, for some odd reason.
With different tables, sometimes the zero reference points may differ.
I would however expect the value (hsup-h2phase) = h1-h6 to be of similar value using either method. You have found a slight difference here as well. Perhaps Coolpack has a few bugs?
You may want to send your findings to the developer of Coolpack v1.49 & find out exactly what gives.Engineering Specialist - Cuprobraze, Nocolok, CD Technology
Rarefied Technologies ( SE Asia )
-
22-09-2010, 06:36 PM #10
Re: log p/h question, flow rate
Well, I calculated it once the other way.
QEvaporator = m.(1-x).(hg-hf)
If I use the mass flow found in Refrigeration Utilities, 0.01942 kg/s, for a capacity of 2 kW and use for hg 350.26 kJ/kg and for hl 159.17 kJ/kg (tables), then I can extract x which gives me 0.46.
Coolpack gives a calculated x of 0.49
I know now - I hope it in fact - that this is a small fault in Coolpack and that it is not me.
Hey DesA, thanks to you, I was yesterday evening better prepared in classes. Thanks.It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
22-09-2010, 07:10 PM #11
Re: log p/h question, flow rate
^ An absolute pleasure Peter. Any time.
Engineering Specialist - Cuprobraze, Nocolok, CD Technology
Rarefied Technologies ( SE Asia )
-
23-09-2010, 04:56 AM #12
Re: log p/h question, flow rate
desA You are right that coolpack uses different references and the IIR value is the one normally used by the refrigeration industry. It is correct in the utilities package but in coolpack it somehow reverts back to the default value and so gives the wrong enthalpy. R134a and R22 and other gases are correct but some blends are reset to the default.
Care must be taken it seems when using coolpack.
This is from the manual.
IIR - the value of specific enthalpy is set to 200 kJ/kg and the value of specific entropy is set to 1.0 kJ/kg-K for saturated liquid at 0°C (273.15 K). This is the standard reference state for the International Institute of Refrigeration. Note that this option is not applicable to fluids for which the critical temperature is less than 0°C. In this case, the reference will be reset to the default value.
Chef
-
23-09-2010, 05:19 AM #13
Re: log p/h question, flow rate
Thanks Chef. An excellent review.
Engineering Specialist - Cuprobraze, Nocolok, CD Technology
Rarefied Technologies ( SE Asia )
-
23-09-2010, 03:53 PM #14
Re: log p/h question, flow rate
Send a message to Coolpack, will post their reaction here
It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
23-09-2010, 05:13 PM #15
Re: log p/h question, flow rate
Peter, would you like to try the cycle simulation by Solvay (software solkane 7.0).
-
24-09-2010, 12:24 AM #16
Re: log p/h question, flow rate
Didn't know they had something similar.
Will have a look. Just back (1:30 midnight) after a concert of U2 in Brussels. Very good concertIt's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
Similar Threads
-
Evaporator air flow rate
By Bashir01219 in forum FundamentalsReplies: 1Last Post: 08-04-2010, 07:41 AM -
Flow Rate through Fan Coil Unit
By deepu in forum Air ConditioningReplies: 4Last Post: 21-07-2009, 06:42 AM -
Capillary Tube Characteristics
By Chef in forum FundamentalsReplies: 9Last Post: 10-03-2009, 01:03 PM -
high volume flow rate
By cakabo28 in forum Technical DiscussionsReplies: 5Last Post: 04-10-2007, 03:41 AM -
Shell/Tube flow rate?
By reggie in forum FundamentalsReplies: 4Last Post: 17-11-2002, 05:41 PM