19-09-2010, 08:58 AM #1
air flow metering
Hi
what is the most suitable way of air flow metering in a duct and at a diffuser outlet.
Please let me have your oppinion
-
19-09-2010, 09:10 AM #2
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: air flow metering
Last edited by nike123; 19-09-2010 at 09:51 AM.
-
20-09-2010, 07:07 PM #3
Re: air flow metering
how practical is it to use a pitot tube to determine the velocity (velocity pressure) in a duct? i.e if the pitot tupe is not held 100% perpendicular to the flow?
-
20-09-2010, 10:55 PM #4
Re: air flow metering
The pitot tube is the most reliable method that has been used for years.
You have to be a long way off line before the readings go silly, most people are able to hold the tube steady while the readings are being taken.
Just make sure that you set up the duct traverse points correctly.Brian - Newton Abbot, Devon, UK
Retired March 2015
-
15-11-2010, 07:49 PM #5
Re: air flow metering
how about a hotwire anemometer, or is the pitot tube more acurate?
-
15-11-2010, 10:14 PM #6
Re: air flow metering
Pitot tube and manometer would be the most accurate of those two.
It also depends on how accurate you need to be for the application involved.Brian - Newton Abbot, Devon, UK
Retired March 2015
-
16-11-2010, 01:48 AM #7
Re: air flow metering
At the outlet and on a coil a velocity grid is the most accurate and reliable. This is used by many air balancing companies and some manufacturers now have them built into the duct. For one off measurement in the duct the pitot tube is used.
-
16-11-2010, 04:55 PM #8
Re: air flow metering
Apropos the air flow metering at difusers outlet.
Have made a use of this instrument recently
http://www.kimo.fr/?rt=index/getFt&id=430
Was turning open a difuser - it showed growing flow. Screwed the diffuser off at all - flow rate shown dropped almost by half!
-
16-12-2010, 02:19 AM #9
Re: air flow metering
Testo meters all the way, they have proven themselves in the Hvac field
Similar Threads
-
flow switch connection
By afeef in forum The Trail of TearsReplies: 18Last Post: 23-12-2009, 06:55 PM -
Pulling faster vacuums
By Aranon in forum FundamentalsReplies: 31Last Post: 04-09-2009, 07:32 PM -
Flow Rate through Fan Coil Unit
By deepu in forum Air ConditioningReplies: 4Last Post: 21-07-2009, 06:42 AM -
Capillary Tube Characteristics
By Chef in forum FundamentalsReplies: 9Last Post: 10-03-2009, 01:03 PM -
High Liquid Line Temperature
By airefresco in forum CommercialReplies: 37Last Post: 11-02-2009, 04:36 PM