    expansion valve with MOP



    hi

    i am having an intermitting prob with the circuit on a tecnair downflow!!!
    every couple of weeks the evaporator ices up restricting flow causing high room tev,when i arrive to site the tev main boby is iced up also.
    the external equalise line is frosted a little near the compressor side but nothing towards tev.
    i noticed from previous threads that the power head must be warmer than the bulb to prevent mop..

    this is a comms room with a 20 degree setpoint!!!

    is there a good way to test these, as when a normal tev goes, it goes!!

    i am thinking moisture also..

    any thoughts ??

    rgrds p



  2. #2
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: expansion valve with MOP

    Hi Phil.
    Just out of interest, what make TEV is it you have?
    I have seen Danfoss ones where the "O" ring on the orifice cage is passing and causing the External Balance line to freeze up.
    When that occurs we normally just change the orifice assy!
    Grizzly
    Last edited by Grizzly; 15-09-2010 at 08:34 PM.

  3. #3
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: expansion valve with MOP

    Sorry, can you please explain once again where is the external equalisation? Surely it shouldn't be where you said it is.

    Secondly, can you please inform us about the pressure and temperatures, including superheating and subcooling?

  4. #4
    Join Date
    May 2008
    Location
    Malta
    Age
    68
    Posts
    67
    Rep Power
    16

    Re: expansion valve with MOP

    A TXV valve with Mop means that the bulb instead of being liquid filled contains only a small amount of liquid limiting the amount of force that the diaphragm can exert being used to limit compressor load, so as you have rightly said the liquid can migrate to the diaphragm if it gets too cold causing the valve to close.What I would suggest is that you replace this valve with one without Mop as it is a coms room the load does not have great variations so Mop is not needed.

  5. #5
    Join Date
    Feb 2007
    Location
    SIDE OF THE ROAD
    Posts
    262
    Rep Power
    18

    Re: expansion valve with MOP

    Thanks for replies

    The make I think is Sporlan griz, also the usual restriction symptom of low back pressure with high super heat and high subcool... This is happening on 4 units so it all common with this batch of units!!!

    Equalise line is located at the end of evaporate coil, there is no reason why these systems should go into mop.. Head pressure 19 bar @ liquid 38c... Back pressure as 4 bar with 4 c temp...


    Any thoughts??

Similar Threads

  1. Lg mps system ( expansion valve location)
    By hussain2002cab in forum Air Conditioning
    Replies: 6
    Last Post: 18-03-2010, 10:19 PM
  2. Actual Expansion Valve Process
    By AastroGuru in forum Fundamentals
    Replies: 11
    Last Post: 03-02-2009, 09:53 AM
  3. Setting of Hand expansion valve
    By Iceehot in forum NH3
    Replies: 7
    Last Post: 10-09-2008, 01:25 AM
  4. the function of the electronic expansion valve
    By Crystal-426 in forum Fundamentals
    Replies: 10
    Last Post: 22-06-2008, 12:29 PM
  5. Need Divine Intervention - plugged drier or expansion valve?
    By archibaldtuttle in forum Trouble Shooting
    Replies: 4
    Last Post: 08-06-2008, 06:52 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •