Thread: 407C running parameter
-
15-09-2010, 11:26 AM #1
407C running parameter
respected sir
im working on DAIKIN AIr conditioning system (air cooled DX system) sir i want to know thw running parameter of 407C for air cooled DX system i dnt have any guide on site please help and if v not use a external equalising line compresor wil burn? or what is the disadvantage of not using equalising line to thermal expansion valve ?
i hope u wil reply soon
regards
ameen
-
15-09-2010, 03:01 PM #2
Re: 407C running parameter
Hi Ameen,
I don't know what you mean by running parameter. Do you mean pressures?
All Daikin systems i have worked on have been charged by weight of refrigerant and not pressure, there is factory charge (marked on data sticker) and then an aditional charge may be nessecary depending on any pipe work on site, unless this is a big chiller then i would not know as i don't work on them.
What size and type of system is it?
You need a thermal expansion valve with a equalising line if the evaporator outlet pressure is more than a few psi lower than the inlet pressure.
If you don't know if it is or not then best to fit an externally equalised valve, it won't harm the system and may do some good.
Jon
Similar Threads
-
parameter of 407c refrigerant
By ameen pasha in forum RefrigerantsReplies: 3Last Post: 12-09-2010, 03:24 PM -
Typical running amps
By acnerd in forum FundamentalsReplies: 8Last Post: 08-09-2009, 11:54 PM -
Problems with compressor running too cold
By abrando1 in forum Trouble ShootingReplies: 8Last Post: 12-05-2009, 10:08 PM -
R22 TEV suitable to use on a 407c charge?
By danielt_smith in forum Trouble ShootingReplies: 9Last Post: 19-11-2008, 02:12 PM -
Walkin cooler running to warm need help
By The Butcher in forum Trouble ShootingReplies: 7Last Post: 03-08-2007, 09:19 PM