    Check valve going off



    Hello lads,

    I have a chilled water system with Copeland scroll compressors. After replacing a compressor and refilling it the compressor started up nicely. After running for a while normally i got a bit concerned with a lot of condensation on the outside of the compressor compared with the other ones. After about 5 minutes of running it started opening the built in check valve and starts releasing first about every 10 seconds then gets more frequent down to about 3 seconds. This happens with the operating pressures at normal levels.

    Advice would be very much appreciated.



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Check valve going off

    Define "operating pressures at normal levels".

    Have you checked the currant drawing?

  3. #3
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: Check valve going off

    Did you Vacuum the system first and weigh the charge in?
    Grizzly

  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Check valve going off

    It look like liquid floodback.
    What is suction superheat?
    Describe how did you determined refrigerant charge.
    Last edited by nike123; 16-09-2010 at 07:25 AM.

  5. #5
    Kollason's Avatar
    Kollason Guest

    Re: Check valve going off

    Hello boys thanks for a quick reply,

    I did not vacuum the system before installing the compressor no. Just closed the inlet and the outlet valves of compressor.

    Logged operating pressures for this system have been 18 bar HP and 3.2 bar suction.

    When re filling kept filling until sight glass was full. I have no real indication on how much is actually in the system as i unfortunately do not have a vacuum pump or a scale on board.

    I checked the suction superheat and it is about 13°C colder than the other compressors or about -2°C.
    What could possibly cause this?

  6. #6
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Check valve going off

    Quote Originally Posted by Kollason View Post
    Hello boys thanks for a quick reply,

    I did not vacuum the system before installing the compressor no. Just closed the inlet and the outlet valves of compressor.

    Logged operating pressures for this system have been 18 bar HP and 3.2 bar suction.

    When re filling kept filling until sight glass was full. I have no real indication on how much is actually in the system as i unfortunately do not have a vacuum pump or a scale on board.

    I checked the suction superheat and it is about 13°C colder than the other compressors or about -2°C.
    What could possibly cause this?
    Overcharge!

    Recover refrigerant until you got 8,5°C subcooling and than check superheat at evaporator outlet.

    Did you said that you did not vacuumed compressor (and system) at all before recharging it?
    Last edited by nike123; 16-09-2010 at 05:39 PM.

  7. #7
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: Check valve going off

    Ouch!!!
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  8. #8
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: Check valve going off

    I would stick to the marine engineering
    Kollason!
    Because you are not doing anyone any favours ignoring the basics!
    Grizzly

  9. #9
    Join Date
    Feb 2009
    Location
    Australia
    Posts
    272
    Rep Power
    16

    Re: Check valve going off

    Probably hasn't got a vac pump.

  10. #10
    Join Date
    Aug 2009
    Location
    USA
    Age
    62
    Posts
    44
    Rep Power
    0

    Re: Check valve going off

    I will give you this! YOU CERTAINLY ARE AN HONEST GUY, and that for sure has it's plusse's. definitelly OVERCHARGED, ( and NON-CONDENSABLES)

    I knew it when you said "lot of condensation on the outside'.......... I think you may have liquid in the suction line going back into the compressor. = no superheat since your gauge temp and line temp will almost be identical in a situation like this.

    It is not uncomon to have ice on a suction line in commercial refrigeration. BUT, HOW COULD YOU NOT PULL A VACUUM? Did you change the dryer?

    MAN! it is SO EASY to do this right; in fact it is AS EASY to do it right, and you did this all wrong.

    I would OPEN the system back up before the moisture ( non-condensables) eat away at your new scroll and PUT A NEW DRYER INTO THE SYSTEM AS WELL. Pull 500 microns on a vacuum gauge; any lower and you could boil out some of the oil in the compressors base.

    WHO has a document they have new customers sign to agree to pay?

    Thanks,
    "NEVER assume it is only ONE problem!"

  11. #11
    Join Date
    Aug 2009
    Location
    USA
    Age
    62
    Posts
    44
    Rep Power
    0

    Re: Check valve going off

    Quote Originally Posted by Kollason View Post
    Hello boys thanks for a quick reply,

    I did not vacuum the system before installing the compressor no. Just closed the inlet and the outlet valves of compressor.

    Logged operating pressures for this system have been 18 bar HP and 3.2 bar suction.

    When re filling kept filling until sight glass was full. I have no real indication on how much is actually in the system as i unfortunately do not have a vacuum pump or a scale on board.

    I checked the suction superheat and it is about 13°C colder than the other compressors or about -2°C.
    What could possibly cause this?
    I just bought a new 9.8 CFM vacuum pump from "Fiery Chill" and they have them on close out. I paid UNDER $300 for an AIRSECO = Thermal vacuum pump because it cost's $250 for a rebuild kit for my 1983 1.6cfm pump from thermal. You can get a 1.8 cfm Thermal pump for only $119 here = http://fierychill.com/closeouts/vacuum-pumps

    Write Bobby = FieryChill Customer Service <info@fierychill.com> ( Bobby Bonitati - FieryChill Customer Service - 1-800-575-4180 ) there and tell him Daniel from Twin Rivers Restaurant Svs sent you over and he could PROBABLY knock that $119 down to $89 IF YOU PAY THE UPS CHARGES!

    YOU WILL NOT GET A BETTER DEAL!

    Good luck,
    Last edited by Deniver45; 17-09-2010 at 02:55 AM. Reason: forgot some info
    "NEVER assume it is only ONE problem!"

  12. #12
    Join Date
    Aug 2009
    Location
    USA
    Age
    62
    Posts
    44
    Rep Power
    0

    Re: Check valve going off

    the valve is being FORCED open due to overcharge. Go get that NEW VAC pump I wrote you about for $119 NIB from Bobby @ Fiery Chill.
    "NEVER assume it is only ONE problem!"

  13. #13
    Join Date
    Aug 2009
    Location
    USA
    Age
    62
    Posts
    44
    Rep Power
    0

    Re: Check valve going off

    anything else Kollason?
    "NEVER assume it is only ONE problem!"

  14. #14
    Kollason's Avatar
    Kollason Guest

    Re: Check valve going off

    Thanks boys, and thanks for the sarcasm as well seems i offended a lot of people.... What confuses me though is that the sight glass now is not full and the pressure is about 1 bar under normal operation on the high pressure side and about half a bar on the low. Will need to get a vacuum pump though.

  15. #15
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    712
    Rep Power
    19

    Re: Check valve going off

    sounds like it's got a leak on it or the ambients have dropped a bit whats the weather like in bermuda i need a holiday
    Last edited by james10; 18-09-2010 at 09:26 AM.

Similar Threads

  1. Bypassing a smv valve on carrier reefer
    By hzu in forum Transport
    Replies: 14
    Last Post: 04-10-2010, 06:13 AM
  2. Danfoss ICAD/ICM Valve problem
    By piewie in forum NH3
    Replies: 3
    Last Post: 11-09-2010, 09:20 AM
  3. Check valve noise - heat-pump
    By desA in forum Trouble Shooting
    Replies: 2
    Last Post: 19-03-2009, 12:52 AM
  4. Escort Compressor Check Valve Explanation
    By BlackMira in forum Supermarket Refrigeration
    Replies: 2
    Last Post: 06-02-2009, 08:00 AM
  5. Air conditioning maintenance procedure
    By Andy T in forum Air Conditioning
    Replies: 12
    Last Post: 27-05-2006, 06:57 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •