Thread: Check valve going off
-
15-09-2010, 07:00 AM #1
Check valve going off
Hello lads,
I have a chilled water system with Copeland scroll compressors. After replacing a compressor and refilling it the compressor started up nicely. After running for a while normally i got a bit concerned with a lot of condensation on the outside of the compressor compared with the other ones. After about 5 minutes of running it started opening the built in check valve and starts releasing first about every 10 seconds then gets more frequent down to about 3 seconds. This happens with the operating pressures at normal levels.
Advice would be very much appreciated.
-
15-09-2010, 05:30 PM #2
Re: Check valve going off
Define "operating pressures at normal levels".
Have you checked the currant drawing?
-
15-09-2010, 07:44 PM #3
Re: Check valve going off
Did you Vacuum the system first and weigh the charge in?
Grizzly
-
16-09-2010, 07:04 AM #4
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Check valve going off
It look like liquid floodback.
What is suction superheat?
Describe how did you determined refrigerant charge.
Last edited by nike123; 16-09-2010 at 07:25 AM.
-
16-09-2010, 12:43 PM #5
Re: Check valve going off
Hello boys thanks for a quick reply,
I did not vacuum the system before installing the compressor no. Just closed the inlet and the outlet valves of compressor.
Logged operating pressures for this system have been 18 bar HP and 3.2 bar suction.
When re filling kept filling until sight glass was full. I have no real indication on how much is actually in the system as i unfortunately do not have a vacuum pump or a scale on board.
I checked the suction superheat and it is about 13°C colder than the other compressors or about -2°C.
What could possibly cause this?
-
16-09-2010, 12:46 PM #6
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Check valve going off
Last edited by nike123; 16-09-2010 at 05:39 PM.
-
16-09-2010, 03:14 PM #7
Re: Check valve going off
Ouch!!!
Engineering Specialist - Cuprobraze, Nocolok, CD Technology
Rarefied Technologies ( SE Asia )
-
16-09-2010, 05:36 PM #8
Re: Check valve going off
I would stick to the marine engineering
Kollason!
Because you are not doing anyone any favours ignoring the basics!
Grizzly
-
16-09-2010, 10:53 PM #9
Re: Check valve going off
Probably hasn't got a vac pump.
-
17-09-2010, 02:48 AM #10
Re: Check valve going off
I will give you this! YOU CERTAINLY ARE AN HONEST GUY, and that for sure has it's plusse's. definitelly OVERCHARGED, ( and NON-CONDENSABLES)
I knew it when you said "lot of condensation on the outside'.......... I think you may have liquid in the suction line going back into the compressor. = no superheat since your gauge temp and line temp will almost be identical in a situation like this.
It is not uncomon to have ice on a suction line in commercial refrigeration. BUT, HOW COULD YOU NOT PULL A VACUUM? Did you change the dryer?
MAN! it is SO EASY to do this right; in fact it is AS EASY to do it right, and you did this all wrong.
I would OPEN the system back up before the moisture ( non-condensables) eat away at your new scroll and PUT A NEW DRYER INTO THE SYSTEM AS WELL. Pull 500 microns on a vacuum gauge; any lower and you could boil out some of the oil in the compressors base.
WHO has a document they have new customers sign to agree to pay?
Thanks,"NEVER assume it is only ONE problem!"
-
17-09-2010, 02:52 AM #11
Re: Check valve going off
I just bought a new 9.8 CFM vacuum pump from "Fiery Chill" and they have them on close out. I paid UNDER $300 for an AIRSECO = Thermal vacuum pump because it cost's $250 for a rebuild kit for my 1983 1.6cfm pump from thermal. You can get a 1.8 cfm Thermal pump for only $119 here = http://fierychill.com/closeouts/vacuum-pumps
Write Bobby = FieryChill Customer Service <info@fierychill.com> ( Bobby Bonitati - FieryChill Customer Service - 1-800-575-4180 ) there and tell him Daniel from Twin Rivers Restaurant Svs sent you over and he could PROBABLY knock that $119 down to $89 IF YOU PAY THE UPS CHARGES!
YOU WILL NOT GET A BETTER DEAL!
Good luck,Last edited by Deniver45; 17-09-2010 at 02:55 AM. Reason: forgot some info
"NEVER assume it is only ONE problem!"
-
17-09-2010, 02:56 AM #12
Re: Check valve going off
the valve is being FORCED open due to overcharge. Go get that NEW VAC pump I wrote you about for $119 NIB from Bobby @ Fiery Chill.
"NEVER assume it is only ONE problem!"
-
17-09-2010, 02:59 AM #13
Re: Check valve going off
anything else Kollason?
"NEVER assume it is only ONE problem!"
-
17-09-2010, 12:16 PM #14
Re: Check valve going off
Thanks boys, and thanks for the sarcasm as well seems i offended a lot of people.... What confuses me though is that the sight glass now is not full and the pressure is about 1 bar under normal operation on the high pressure side and about half a bar on the low. Will need to get a vacuum pump though.
-
17-09-2010, 05:32 PM #15
Re: Check valve going off
sounds like it's got a leak on it or the ambients have dropped a bit whats the weather like in bermuda i need a holiday
Last edited by james10; 18-09-2010 at 09:26 AM.
Similar Threads
-
Bypassing a smv valve on carrier reefer
By hzu in forum TransportReplies: 14Last Post: 04-10-2010, 06:13 AM -
Danfoss ICAD/ICM Valve problem
By piewie in forum NH3Replies: 3Last Post: 11-09-2010, 09:20 AM -
Check valve noise - heat-pump
By desA in forum Trouble ShootingReplies: 2Last Post: 19-03-2009, 12:52 AM -
Escort Compressor Check Valve Explanation
By BlackMira in forum Supermarket RefrigerationReplies: 2Last Post: 06-02-2009, 08:00 AM -
Air conditioning maintenance procedure
By Andy T in forum Air ConditioningReplies: 12Last Post: 27-05-2006, 06:57 PM