    Calculate capilary tube for R410



    Heloo

    Perhaps who have program or formula to calculate lenght capilary tube for heating/cooling for air condition on R410 refregitant ?

    Power cca 5kW
    Commpressor cca 1,5kw

    Best Regards Glavca



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Calculate capilary tube for R410

    For modifications or experimenting, it is better to use TXV.
    Capillary in series production is obtained by rough calculation and fine tuning by experimenting.

    http://findarticles.com/p/articles/mi_m5PRC/is_2_112/ai_n24998225/
    Last edited by nike123; 14-09-2010 at 10:48 AM.

  3. #3
    Join Date
    Apr 2010
    Location
    Novo mesto
    Age
    46
    Posts
    7
    Rep Power
    0

    Re: Calculate capilary tube for R410

    tnx,

    But perhaps anyone know practical how long and diameter iscapilary tube for 5kw aircondition ? I not nead ideality, only approximation from other ON/OFF factory outside unit...

    I need to make modification on some LG outside unit, who have EEV and on/off comnpressor ( have digital communaction betwen outside and inside unit) to work with normal inside on/off unit. I need only for cooling unpretending room.


    Best Regards Jože

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Calculate capilary tube for R410

    Found a Trane document with some R410a capillary data in it, may be helpful.

    http://www.scribd.com/doc/27057900/T...-Piping-System

    Dancap, Danfoss, does not have R410a in it.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Calculate capilary tube for R410

    Quote Originally Posted by Brian_UK View Post
    Found a Trane document with some R410a capillary data in it, may be helpful.

    http://www.scribd.com/doc/27057900/T...-Piping-System

    Dancap, Danfoss, does not have R410a in it.
    I think that is for selecting capillary for subcooler and not for evaporator.

  6. #6
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Calculate capilary tube for R410

    Quote Originally Posted by glavca View Post
    tnx,

    But perhaps anyone know practical how long and diameter iscapilary tube for 5kw aircondition ? I not nead ideality, only approximation from other ON/OFF factory outside unit...

    I need to make modification on some LG outside unit, who have EEV and on/off comnpressor ( have digital communaction betwen outside and inside unit) to work with normal inside on/off unit. I need only for cooling unpretending room.


    Best Regards Jože
    I saw in some Mitsubishi Electric service manuals that capillary tube length and bore is noted on refrigerant diagrams. Try to search for their manuals and see what could be found.

    I found that for 18000 BTU model MSH18NV capilary is 2X 750mm of 1,6mm bore.
    Last edited by nike123; 14-09-2010 at 09:31 PM.

  7. #7
    Join Date
    Apr 2010
    Location
    Novo mesto
    Age
    46
    Posts
    7
    Rep Power
    0

    Re: Calculate capilary tube for R410

    2 x 750mm in paralell bind together ?


    Regards Jože

  8. #8
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Calculate capilary tube for R410

    Quote Originally Posted by glavca View Post
    2 x 750mm in paralell bind together ?


    Regards Jože
    Here it is outdoor unit heat exchanger divided in 2 circuits. Each circuit ends in its own capillary and at other side capillaries are bonded together. That is for balancing outdoor heat exchanger. If your is of 1 circuit only, you could bond both ends of capillaries.

Similar Threads

  1. Preliminary design of Fin tube evaporator
    By teikseng in forum Fundamentals
    Replies: 5
    Last Post: 11-06-2010, 09:59 AM
  2. Capillary Tube Characteristics
    By Chef in forum Fundamentals
    Replies: 9
    Last Post: 10-03-2009, 01:03 PM
  3. Theory of capilary tube
    By nike123 in forum Fundamentals
    Replies: 11
    Last Post: 16-09-2008, 03:56 PM
  4. Calculate cap tube
    By herefishy in forum Technical Discussions
    Replies: 55
    Last Post: 04-11-2003, 08:31 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •