    Inverting cycle without stopping the compressor



    Due a need to attain the lowest hysteresis possible , I intend to not stop the compressor and to cycle the reverse valve.

    The out unit is a Scroll 5tr , and the evaporator is it's matching unit.
    It is used in a seed germination chamber.

    I do not want to stop the compressor , as per manufacturer specs the compressor could not cycle more than 10 times by the our.

    What inconvenient shall become?

    Evaporating coil is just 1,5 meter over the Out side base plate.
    Pipe run horizontal from Evaporator by 7 meters.
    Pipes are 3/4" and 1/2"

    Thanks in advance



  2. #2
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Inverting cycle without stopping the compressor

    I don't think it is a good idea, in an instant the condenser becomes the evaporator and i believe the compressor will suffer from liquid slugging.

    A few years ago my colleague fitted a condensate pump to a 60,000btu heat pump but wired it wrong so that when the pump ran it fed the reversing valve, it really sounded nasty when it went into reverse.
    A few months later he was out there fitting a new compressor, i don't know if the two things were related but wouldn't be at all surprised.

  3. #3
    Join Date
    Oct 2006
    Location
    CORDOBA -ARGENTINA
    Age
    75
    Posts
    69
    Rep Power
    18

    Re: Inverting cycle without stopping the compressor

    The out door units have a suction accumulator , any way I will take your advice in count.

  4. #4
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Inverting cycle without stopping the compressor

    It is possible to revert the cycle without stopping the compressor, but a suction accumulator must be installed in front of the compressor, as it looks like here.

  5. #5
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Inverting cycle without stopping the compressor

    I have Fujitsu window type Ac (6kW) which, in heating mode goes in defrost and out of defrost (inverting cycle) without stopping compressor, over 12 years without any damage. It has accumulator.

Similar Threads

  1. Sanyo Semi Hermetic Compressor Problems
    By dallas in forum Technical Speculations
    Replies: 5
    Last Post: 21-04-2010, 06:51 AM
  2. [Autocascade] Only a project ATM
    By before in forum CPU Overclockers
    Replies: 1
    Last Post: 07-05-2009, 11:13 AM
  3. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM
  4. SL/SB-400 Pump Down Procedures
    By absolute-zero in forum Transport
    Replies: 1
    Last Post: 29-01-2008, 09:27 PM
  5. Efficiency of compressor assisted HRV
    By montreal in forum Heat Pumps
    Replies: 46
    Last Post: 27-08-2007, 08:51 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •