I need to communicate Carel IR33 to PLC AB ML1100, my problem is the Carel is not Modbus communication, is only Carel Protocol, I need the Carel Data Protocol, I need only actual temperature.
Thanks
-
12-09-2010, 10:17 PM #2
Re: I need Help Carel IR33
According to the Carel IR33 Manual....
ModBus®
As well as the CAREL communication protocol, IR33 can also use Modbus®. The protocol (Modbus®, CAREL) is recognised automatically,
the instrument does not need to be configured. In addition, the serial board remains the same.Brian - Newton Abbot, Devon, UK