    Freezer Coil icing



    I am looking for some way to detect an excessively iced dx evaporator coil. This is in a industrial freezer walk in unit that has a hot gas type defrost with a pressure switch termination. Problem is if we have door ajar or something, the coil wont get defrosted completely and begins to ice heavily. We have already lost 2 expensive coils due to freeze damage. I want some kind of sensor to lockout the unit if if shows too much ice. Measure temperature somewhere? pressure drop across coil?
    Unit runs at -9C box temperature and uses R404
    Thanks.



  2. #2
    Join Date
    Sep 2008
    Location
    United States
    Age
    59
    Posts
    57
    Rep Power
    16

    Re: Freezer Coil icing

    Hansen makes a solid state defrost timer that has a sensor to start a defrost cycle when ice is detected on the coil. This system is very reliable and not overpriced at all.

  3. #3
    Join Date
    Aug 2009
    Location
    Manchester
    Posts
    29
    Rep Power
    0

    Re: Freezer Coil icing

    also there is a kuba controller with defrost on demand that does a smilar thing see link below (bottom 2 paragraphs of this link it explaind a bit more)
    http://www.thermofrostcryo.co.uk/new...a_warranty.htm

    But i would also recommend fixing the door or getting an automatic door that closes after 20 seconds or so

    regards sefuss

  4. #4
    Join Date
    Dec 2007
    Location
    lebanon
    Posts
    130
    Rep Power
    17

    Re: Freezer Coil icing

    hi
    what kind of controller you have modern controller has many sensors lets say two one for the set point the second for defrost termination you can set it at the desired temperature to end defrost&you activate fan motors @the desired temperature try with danfoss ekc serie

  5. #5
    Join Date
    May 2008
    Location
    Malta
    Age
    68
    Posts
    67
    Rep Power
    16

    Re: Freezer Coil icing

    As the other posters have stated throw that controller out and get a modern one with two sensors so defrost can be terminated by temperature.What I would query is your stated freezer temp of 9c,what product are you storing and for how long.

  6. #6
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: Freezer Coil icing

    Hi jgosney, welcome to the forum.
    Over here in the U.K.
    At the Cold Stores I used to work at if Door discipline was an issue.

    We installed a flashing beacon and had the door fitted with a micro switch.

    Which in turn sent a signal to our monitoring software.
    Any resultant loses proven to be relevant to the chamber door being left open.
    Was taken out of that shifts bonus.

    You would be amazed how quickly all related bad practises stopped.
    One question though, Have you ever considered fitting plastic curtain strip across the inside of the doorway?

    For the amount of iceing up you are describing, you must have a high humid atmosphere.
    Or is it very long intervals between the chamber being accessed?
    Cheers Grizzly.

Similar Threads

  1. walk-in freezer evap icing up
    By FEISTY in forum Trouble Shooting
    Replies: 8
    Last Post: 10-07-2010, 01:52 PM
  2. IQF Freezer / Dynalene Coil
    By bosse1950 in forum Commercial
    Replies: 0
    Last Post: 03-04-2009, 10:39 AM
  3. Outdoor coil icing up...
    By airflo in forum Heat Pumps
    Replies: 18
    Last Post: 28-10-2008, 07:12 PM
  4. Freezer Icing Up
    By wackiejackie88 in forum Trouble Shooting
    Replies: 5
    Last Post: 26-06-2008, 03:40 PM
  5. walk in cooler EVAPORATOR coil icing up
    By kurt854 in forum Fundamentals
    Replies: 5
    Last Post: 14-06-2007, 07:28 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •